Weil Mclain Easy Up manifold question
jakethomas
Member Posts: 9
Hello all!
Im currently replacing my munchkin boiler. Im putting in an AquaBalance heat only boiler to replace it. The question I have is with the new plumbing. The old plumbing was simple, but this easy up manifold makes me think I need a check valve in the system. Please let me know if Im wrong.
Here is how the current plumbing sits. Exit boiler-plumbing goes up to T fill valve. After that the circulation pump, then expansion tank, after that all the zone valves. Pump would only come on when the zone valve was triggered. In this scenario all the flow makes sense. Water has only one way to go based on the pump setup. Now with the easy up manifold the return and supply are connected within 12" of a T. I have attached pictures. Can someone help fill me in on how to set this new system up. Not sure if I need a check valve installed..
Thanks
Jake
Im currently replacing my munchkin boiler. Im putting in an AquaBalance heat only boiler to replace it. The question I have is with the new plumbing. The old plumbing was simple, but this easy up manifold makes me think I need a check valve in the system. Please let me know if Im wrong.
Here is how the current plumbing sits. Exit boiler-plumbing goes up to T fill valve. After that the circulation pump, then expansion tank, after that all the zone valves. Pump would only come on when the zone valve was triggered. In this scenario all the flow makes sense. Water has only one way to go based on the pump setup. Now with the easy up manifold the return and supply are connected within 12" of a T. I have attached pictures. Can someone help fill me in on how to set this new system up. Not sure if I need a check valve installed..
Thanks
Jake
0
Comments
-
That’s a primary/secondary manifold that allows hydraulic separation between the boiler and the system.
You need to supply the pump for the manifold and also a correctly sized one in the system loop.
Forget the check valve, you don’t use those with zone valves.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The installation manual shows some piping options
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Weil-Mclain-383-100-050-User-Guide.pdfBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
My old system didn't have this. I did see the manual on different ways to route everything. Is it wise to stick with this? Or should I ditch this manifold and just have the pump mounted outside the boiler supply and route it back through with a return?Ironman said:That’s a primary/secondary manifold that allows hydraulic separation between the boiler and the system.
You need to supply the pump for the manifold and also a correctly sized one in the system loop.
Forget the check valve, you don’t use those with zone valves.
I might down the road install an indirect water heater.
Thanks for the replies0 -
While the manual doesn’t prohibit direct piping, they don’t show any piping that way?
With a zoned system like yours you may not get adequate flow when only one zone operates. Do you know the flow rate of the smallest zone?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:While the manual doesn’t prohibit direct piping, they don’t show any piping that way? With a zoned system like yours you may not get adequate flow when only one zone operates. Do you know the flow rate of the smallest zone?0
-
-
Why do you say that?EBEBRATT-Ed said:I would strongly stick with the primary secondary manifold
Hot_rod they didnt have any diagrams showing direct in the manual.0 -
In some cases you can buy a hydraulic separator for the same $$ as that manifold.
Then you get air, dirt, magnetic, separation plus the primary secondary feature.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
That Munchkin was very likely supposed to be piped primary/secondary like the new one, that is likely why you had the overheating scenario with low flow conditions. Primary/secondary is there to separate the boiler flow from system flow, in other words to guarantee flow through the heat exchanger. There was less education around water tube condensing boilers back then and a whole lot were direct piped when they shouldn't have been. Looks like you got your moneys worth out of the first one though.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements