Oil in sight glass, but no surging. Is this a problem?
There's an obvious amount of oil sitting inside the sight glass. When the boiler is running it's not really surging - I don't see a lot of violent/turbulent movement in there, it just sort of gently bounces up and down. Is the existence of oil in there a problem or not, regardless of whether there is surging or not? I received contradicting information from two different plumbers and I don't know who is right.
I have been having this issue where brand-new Gorton #1 main vents installed on a menorah-like pipe fitting arrangement on both of my mains eventually start to leak wet steam and refuse to close until _very_ late in the call for heat. The boiler itself is also mostly brand-new, having been installed July 2022.
One plumber I hired to diagnose the issue said that he believed oil was increasing the pressure in a way that my pressuretrol couldn't read (pressuretrol stays at 1.5-2.0 psi throughout the call for heat). So I called the plumber that installed the boiler back to my house and when he looked at it, he said there was no surging so it doesn't need to be skimmed.
Can anyone give me any indication one way or another who is right? My system just keeps leaking. If the main vents don't leak, one of the smaller rad vents starts to leak. When I replace the smaller rad vents, one of the main vents start to leak.
Comments
-
-
The plumber that installed the boiler should have skimmed all of the oil out of it, period. The boiler installation isn't "complete" until all the oil is gone or you will wind up with various problems in perpetuity because that oil isn't going away on its own.0
-
how how hard is it?0
-
Does the water when steaming flow over the top of the gauge glass , if so ,boiler needs to be skimmed ...
There was an error rendering this rich post.
0 -
No @Big Ed_4, the boiler was never skimmed, so it needs to be skimmed.0
-
@Waher . get the installer or another plumber to come back and skim the boiler, fix the leaks and adjust the pressure control to cut out at 1.5 psi and cut in at 1/2 psi and clean the gauge glass.
In addition it looks like the the bottom gauge glass fitting has a small leak.
The skimming and gauge glass leak and adjusting the pressure control are for sure the original installers problem0 -
-
The fact that you have enough water in the area of the vent to prevent them from closing tells me you are either producing wet steam due to poor piping, or surging causing water to go up into the mains.
After confirming the piping is proper, then skimming would be the next step. Are you sure the boiler has been properly piped?0 -
I think you meant @ccorderoEBEBRATT-Ed said:
Not my boiler, but my recommendation that @ccordero ask the original installer to come back and skim the oils out of the boiler.
0 -
Are the mains insulated ?
There was an error rendering this rich post.
0 -
Big Ed_4 said:Are the mains insulated ?
Okay thanks everyone! It seems everyone is in full agreement that the boiler needs to be skimmed, regardless of whether there is surging in the sight glass. I called the plumbers to come back and do that, and they said that instead of a skim, they have something that they can pour into the boiler to force the oil to settle at the bottom of the tank where it can be drained.
First, is this a thing? If so, what is this thing that you can pour into your boiler to do this?
Second, is this an appropriate alternative to skimming the boiler? I was tempted to tell them to not bother and go with a different plumber altogether, but I don’t know enough to argue against the alternative they suggested.0 -
There is no substitute to properly skimming the oil off the boiler water. Any chemicals added to avoid that work will only further your problem.
You should also be sure that the plumber who doesn't know how to skim a boiler knew how to pipe it correctly. Might want to check this out while he's still responsive. Your problem is probably more than some oil.0 -
-
Easyer to keep it out then spend the hours skimming it out ..
There was an error rendering this rich post.
0 -
EBEBRATT-Ed said:
@ccordero They are taking the easy way out. 15 min to add chemicals versus a maybe 4 hr skim job.
Big Ed_4 said:Easyer to keep it out then spend the hours skimming it out ..
It's easier, but is it a worse way to do it? Or should I insist on a skim job?0 -
Thanks for this!Long Beach Ed said:There is no substitute to properly skimming the oil off the boiler water. Any chemicals added to avoid that work will only further your problem.
You should also be sure that the plumber who doesn't know how to skim a boiler knew how to pipe it correctly. Might want to check this out while he's still responsive. Your problem is probably more than some oil.0 -
It's a thing. See my video below. But I wouldn't use that stuff if I had the option of skimming. There's no point.
I suggest go to the video on youtube, not the embedded viewer below because it's rather long and I put the times of different parts in the description. Although I do see in the embedded player you can hover your mouse over the timeline and it will give you the sections and names.
https://youtu.be/Q0CkJUr0JRYNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
One quart of of oil can pollute one square mile of ocean . They don't mix . The iron added, first needs to be degreased before installing to a steam system ..
There was an error rendering this rich post.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements