One Pipe System Losing Water
AVInstalls
Member Posts: 1
Hi
My house was built in 1927. The Boiler probably about 10 years old.
So two questions
- is it possible that being how much water I’m losing it could be because of steam being released by the boiler or by any of the radiators? (Typing this out i realized I can shut off all the valves to test the radiators- is that safe? )
- if I do rip up the area of my floor around that area that’s hot in my basement, can I just rip up that one area and fix the pipe?
My house was built in 1927. The Boiler probably about 10 years old.
The heat works great. The issue is though that the auto-filler is going off every few minutes. Does that mean a leak or can that mean too much steam is coming out of the boiler.
In my basement underneath the floor in one area feels very hot, I’m assuming that’s where my return pipe is.
So two questions
- is it possible that being how much water I’m losing it could be because of steam being released by the boiler or by any of the radiators? (Typing this out i realized I can shut off all the valves to test the radiators- is that safe? )
- if I do rip up the area of my floor around that area that’s hot in my basement, can I just rip up that one area and fix the pipe?
- any other possibilities I’m missing?
Thanks in advance
Thanks in advance
1
Comments
-
Flood your boiler and check for leaks dripping if no leaks but the water level drops down to your Hartford loop height then you have a buried wet return leaking . Usually a repair while leaving the rest of the buried pipe in place is just a band aid . The 3 paths are cut the floor install a trough and install new pipe or re route the new wet returns above the floor and the final depending upon your piping height is to install a dry return w that being said you will need pitch and a mim distance above the boilers water line from the dry return to operate properly and not spit water from your new main vents optimum mim distance I stick to 34 inch above water line for dry returns and usually have no issues . Peace and good luck clammy
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating1 -
clammy said:Flood your boiler and check for leaks dripping if no leaks but the water level drops down to your Hartford loop height then you have a buried wet return leaking . Usually a repair while leaving the rest of the buried pipe in place is just a band aid . The 3 paths are cut the floor install a trough and install new pipe or re route the new wet returns above the floor and the final depending upon your piping height is to install a dry return w that being said you will need pitch and a mim distance above the boilers water line from the dry return to operate properly and not spit water from your new main vents optimum mim distance I stick to 34 inch above water line for dry returns and usually have no issues . Peace and good luck clammy0
-
If it's a lot of water, a buried return is the most likely culprit, if it's not a leak in the boiler.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie Hall said:If it's a lot of water, a buried return is the most likely culprit, if it's not a leak in the boiler.0
-
You can notice it coming out the chimney if you look up there, and if you have some historical knowledge of the previous amount of combustion condensation that emitted from it. But overfilling to the header as Clammy said is the better test
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Also, check your radiators themselves. I have a leak in one radiator's input valve and it is a steady drip when the heat's running only realized it very recently after plaster starting sagging and peeling in the ceiling and wall below.0
-
-
Hopefully not too much of a hijack on this thread, but I recently noticed my new-to-me 2 pipe system triggered its LWCO. My water feeder is an older model that doesn't recorded the amount added over time, so I don't know how often this is occurring, though any LWCO troubles me a bit. Would the same procedure of overfilling and looking for boiler leaks be appropriate?
I'm running a 2020 Weil-McLain. No buried pipes. I have one radiator with an occasional spit at a trap joint, but all the other radiators appear to be in good working order.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements