Steam wet return
Snowmelt
Member Posts: 1,425
General statement working on 175,000 btu steam boiler the return pipping looks like 1 inch copper going roughly 30 feet along the floor , should that be a minimum of 1-1/4 or it doesn’t really matter ?
0
Comments
-
Be nice if it were bigger -- it wouldn't clog so often -- but keep in mind that the flow in a wet return is pretty small. At your boiler size, you are looking at only about a quart and a half per minute...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Only question it because the homeowner saw water spitting out of the vent0
-
I just did a 177,000 input boiler and used 1" copper for wet return.
Did the math/homework and it was all that was needed.
(Plus I had the 1" in stock )
Now if it was plugged, or you have wet steam, faulty air vent or steam main with water pocket, high steam pressure,..... then maybe the spitting problem.0 -
Lots of reasons for that other than an undersize wet return! Too much pressure, too fast a vent, wet steam... the list goes on.Snowmelt said:Only question it because the homeowner saw water spitting out of the vent
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Most likely wet steam , I’m guessing in that , the pressure trol was set at 1.5 I’m going to replace the gauge , the near boiler piping wasn’t the best , bare minimum with 2 tees instead of three take off, lots of rotted pipe that was changed out. I’m going to take a picture in a few days , it’s still working , just not the best set up
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements