Radiator not Heating
mgambuzza
Member Posts: 29
I've been troubleshooting the 22 radiators at my home one (sometimes a few) at a time to get them all working well again. I've gotten down to my last few and was hitting homeruns until the one in a large bedroom. The USR CORP radiator had a vintage Hoffman air valve that seemed a little loose. I went to screw it out and it fell out - not from shear, but because it was stripped so badly they could wedge it back into the radiator. Obviously a new valve won't go in, and during the period it was out for me to take these pictures and wedge it back in, it was heating.
How and what size tap do I need to use to either re-thread, so I can screw a valve back in. Also - at the top offset of the radiator, there is a screw that looks like the valve could either be top mounted or mounted in the middle. Should I try tap and insert the valve in the middle opening, or seal it and place the valve in the upper opening?
How and what size tap do I need to use to either re-thread, so I can screw a valve back in. Also - at the top offset of the radiator, there is a screw that looks like the valve could either be top mounted or mounted in the middle. Should I try tap and insert the valve in the middle opening, or seal it and place the valve in the upper opening?
0
Comments
-
Tough to see without a reference like a dime or a ruler next to the hole, but the standard pipe size for radiator vents is 1/8" NTP. That pipe size tap is usually a part of the standard SAE Tap and Die set, or you can purchase it separately at ACE or True Value hardware stores, or Auto parts stores that sell tools. The problem is, there may not be enough metal to take the new threads.
You may need to tap and thread a 1/4" NTP pipe opening and install a 1/4" x 1/8" bushingEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
First, try the 1/8" pipe thread tap. It may just need to have the threads cleaned out.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Do not use the upper vent tapping on that radiator. That is for hot water systems. If you use it for steam, the radiator is likely to heat only partially.
The only time it should be used for steam is if two vents are needed to get the radiator to heat quickly enough. That way the top vent will close first once the air is out of the riser, and leave the lower vent to fill the radiator more slowly so that steam and condensate don’t clash violently in the piping and cause trouble.—
Bburd0 -
It looks like the threads may have corroded/sheared off that valve, so you might get lucky and might be able to thread a new valve if you clean it up with a tap. It is hard to tell from that picture. Otherwise you will have to drill and tap to 1/4" and use a bushing as @EdTheHeaterMan said.0
-
I want to thank all for their input on this. After a VERY frustrating search for a 1/8 tap, I easily found a 1/4. Drilled, tapped, screwed, and inserted a leftover Leader air valve, and voila - heat!! Grateful for the advice, and confidence to do this. This was the last radiator to repair and just in time for the sub 20 degree weather.
2 -
nice workBr. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Nice job. I was gonna say Ed was being a little optimistic thinking a 1/8" NPT tap is available at all those places. But it's easily available at Amazon.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements