End of Main Venting

Does anyone have some advice, Pro or Con, regarding an end of Main Vent Antler I dry fit together adjacent to the last Radiator stub up. There is minimal distance to install this pair of Gorton #1s due to the foundation wall. I sized up the vents and it is a good match for the 2 inch main.

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 2,973
    We can not understand the problem

    There was an error rendering this rich post.

  • Steamhead
    Steamhead Member Posts: 17,312
    @PoponPachaug , post some pics if you can. I think I know what you're getting at, but pics always help.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,281
    edited November 2022
    Elbows and Street Elbows are your friends. Sounds like quite an investment. How long is that main?
  • PoponPachaug
    PoponPachaug Member Posts: 16
    Gentlemen, please forgive me for not posting pictures and answering your questions.
    My phone is not forwarding pics so please be patient with new me awaiting to upload pictures as soon as I can.

    The 1 1/2" main is 14 ft and previous to that, there is a 2" main of 23 ft
  • ethicalpaul
    ethicalpaul Member Posts: 6,367
    That is very short main, which is good, but you only need a single Gorton #1 or Maid O Mist #1 for that 2" main and your short 1-1/2" main is barely more than a 2nd floor radiator runout but of course a #1 won't hurt it.

    I don't think you need an antler but it won't hurt.

    I also can't tell exactly what you are asking though.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Long Beach Ed
    Long Beach Ed Member Posts: 1,281
    Don't go nuts with this. Unless the boiler's way oversized a Gorton #1 on each main would be fine.
  • PoponPachaug
    PoponPachaug Member Posts: 16
    The 23 ft of 2" main and the 14 ft of 1 1/2" main is the sole main to that point of end of main vent antler.
    I finally got to upload a picture, take a look and please advise of any issues you may see.
  • Long Beach Ed
    Long Beach Ed Member Posts: 1,281
    Way more venting than you need but looks fine to me.
    ethicalpaul
  • Steamhead
    Steamhead Member Posts: 17,312

    The 23 ft of 2" main and the 14 ft of 1 1/2" main is the sole main to that point of end of main vent antler.
    I finally got to upload a picture, take a look and please advise of any issues you may see.

    Is that main with the two Gorton #1 vents the only main in the system?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • PoponPachaug
    PoponPachaug Member Posts: 16
    No, there is another similar 2" main and I installed a pair of Gorton #1 vents near the end of the dry return.
  • Steamhead
    Steamhead Member Posts: 17,312
    If the steam reaches the ends of both mains at about the same time, and the trip down the mains takes a minute or two, you're good.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • ethicalpaul
    ethicalpaul Member Posts: 6,367
    A minute or two if the mains are hot already, right?

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Steamhead
    Steamhead Member Posts: 17,312

    A minute or two if the mains are hot already, right?

    Depends. With enough venting some will only take that long when cold.