Spark test
Isacc
Member Posts: 5
in Gas Heating
What is a safe and reliable way to test different kind of spark ignitors? Specially the ones used on Gordon Piatt burners where only the rod comes out.
0
Comments
-
Hello @Isacc,
Maybe this will help.
https://heatinghelp.com/assets/documents/Troubleshooting-Intermittent-Ignition-Systems-for-Gas-Furnaces-and-Boilers2.pdfNational - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
Start with the single tap ignition transformer, do you get at least a 1/2" spark jumping to your grounded well insulated screwdriver? If so, and still not seeing a spark through the burner window or boiler rear sight glass, I suggest pulling the pilot assembly. Examine the porcelain real well for cracks and check to see if the steel rod (electrode) is loose or moves. Make sure the electrode gap is correct and make sure distance from the gas pilot jets and/or ground is correct.1
-
In addition to what @ScottSecor said check the 120 volt supply to the transformer. If the 120 is low the output will be low1
-
So, you are all saying the hold on to the wire test is not Best Practice?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
The procedure that 109A_5 recommended is taken from one of my manuals I created and still sell it should help you find the problem.0
-
This looks like a G & P commercial burner, not residential. Probably has a 6000-8000 volt single pole ignition transformer0
-
If power burner, could the air flow be too high that it is lifting the pilot gas and spark away?0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 98 Geothermal
- 155 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 909 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements