Private house, family of four.

Comments

  • ChrisJ
    ChrisJ Posts: 17,763
    You can keep all of this in one thread.

    In fact, it would probably be highly beneficial to you because everyone could see the history of the discussion to help see what you're trying to accomplish.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • taylorgeo
    taylorgeo Posts: 74
    edited September 2022
    @ChrisJ

    Yeah, good point. My bad.

    So my supply house only has an American Standard Cadet PRO in a 1.28. I currently have a 25-year-old Kohler 1.6.

    I'm surprised I can't get the 1.6 AS from the supply house. Should I just go with the 1.28?

    Thanks!
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,330
    you can do what i do and flush 2x if you have to
    GGross
  • We have a 10 yr old Kohler 1.6, Toto 1.28, and a Delta 1.28 in our house.  I would not buy another 1.6 toilet.

    although the Toto is my favorite I would give the Delta my “Best Buy” rating.  It was inexpensive and works great.
  • @Robert_25

    Cool, thanks for the info.

    The 1.28 is also WaterSense Certified. Not sure how big of a deal that is.
  • ChrisJ
    ChrisJ Posts: 17,763
    edited September 2022
    taylorgeo said:
    @Robert_25 Cool, thanks for the info. The 1.28 is also WaterSense Certified. Not sure how big of a deal that is.
    Personally i don't care what it's certified.  I just want sh......poo to go down everytime. I don't care if it's 1.25 gallons or 5 gallons.

    But that's me.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Lyle {pheloa} Carter
  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,330
    I have 2 1.6gph Kohler's. The round one would pull your arm to the sewage plant. The one upstairs with the elongated bowel is just ok
  • ChrisJ
    ChrisJ Posts: 17,763
    I have 2 1.6gph Kohler's. The round one would pull your arm to the sewage plant. The one upstairs with the elongated bowel is just ok
    Are they both the same age and model other than elongated vs round?

    I have a 1.6 Kohler that's one of the worst I've ever used.   I also have a 1.6 Gerber that's amazing.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • EBEBRATT-Ed
    EBEBRATT-Ed Posts: 21,330
    @ChrisJ yes within a couple months of each other
  • mattmia2
    mattmia2 Posts: 18,399
    I think this comes more down to design than amount. There are terrible 1.6 toilets and great 1.2 toilets.
  • ChrisJ
    ChrisJ Posts: 17,763
    mattmia2 said:
    I think this comes more down to design than amount. There are terrible 1.6 toilets and great 1.2 toilets.
    That's why I said I don't care how much water it uses as long as it does the job well.

    1.2,1.6,3,5. Don't care.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • HomerJSmith
    HomerJSmith Posts: 2,837
    edited September 2022
    The problem is and always has been "solids transport". The lower the flush quantity, the more the chance of waste being left behind. The dia of the soil piping has a lot to do with moving solids down the line. Too big a pipe and too little water makes Roto Rooter a happy camper.

    Yes, a low flush toilet saves water, but not if you have to flush twice and certainly doesn't pay off if you have to call a rooting service. Bureaucrats are poor planners. As for me 1.6 is my choice. If that choice doesn't exist than 1.28 rated at a 5. Dual flush is the way to go. One for liquid wastes and one for solid wastes.
  • pedmec
    pedmec Posts: 1,488
    The problem is you wont know until you buy it and have it installed. That's when you find out whether you bought a good one or not.
  • @HomerJSmith

    "1.28 rated at a 5"

    How would I find that out?

  • taylorgeo said:

    @HomerJSmith

    "1.28 rated at a 5"

    How would I find that out?

    You can read a lot of toilet reviews online. I found Terry Love's summary very helpful: https://www.terrylove.com/crtoilet.htm

    Yesterday I noticed that our last old toilet (1980's American Standard, 3.5 GPF I think) is leaking past the flapper. I know it is a cheap fix, but I decided it is a good time to upgrade. I ended up ordering a Toto Drake 1.28 GPF.
    MikeL_2
  • TAG
    TAG Posts: 807
    ChrisJ said:


    mattmia2 said:

    I think this comes more down to design than amount. There are terrible 1.6 toilets and great 1.2 toilets.

    That's why I said I don't care how much water it uses as long as it does the job well.

    1.2,1.6,3,5. Don't care.

    My old suburban house has a very long main drain -- it's a big long extended cape on a rise with a walk out lower level. I remodeled the second floor bath when I bought it years ago and in went a low flow toilet ... we would have a problem almost every summer when the house was mostly empty. The toilet did not give enough water to flow all the way out to the street and clogs would occur at the main trap/ back flow. The other toilets in the house were water hog lowboy Kohler. The fix was to switch it out. Same with an old farm house I had w/ septic -- I mentioned in another thread I needed to get a pressure assist for that one. It must have had some wacky fittings to the main and needed the push ....
  • Jamie Hall
    Jamie Hall Posts: 27,975

    @HomerJSmith and @TAG made a very good point up there. If you have older, large, often rather flat plumbing or a long often rather flat drain to the street or your septic system, the low flush toilets WILL give you trouble, even if they manage to clear the bowl (some do, some don't). And the insidious part is that that won't show up right away — it may be months before solids build up in the drain to the point that you have a problem. If you're stuck with replacing a good old 5 gallon unit on one of those systems (rather than fixing what's leaking or not working), with a low flow unit plan on giving any solids at least two or better three flushes. It's not the new toilet's fault — just the way the water does or doesn't flow.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ethicalpaul
    ethicalpaul Posts: 9,076

    Bureaucrats are poor planners. As for me 1.6 is my choice.

    Didn't bureaucrats mandate 1.6?

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    CLamb
  • ChrisJ
    ChrisJ Posts: 17,763

    And 3 gallon.

    Personally I find the most recent 1.6's outperform the 3's I've used.

    But all of my 114 year old cast iron has a proper amount of pitch.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • JUGHNE
    JUGHNE Posts: 11,653

    Having 2 teenage boys at one time, the decision was to flush before and then after the paperwork.

    This solved most problems and the solution has been passed down to the next generation after 30 years or so.

    So double flushing in the middle of the process is the answer here.

  • ChrisJ
    ChrisJ Posts: 17,763

    Never found the need with a modern 1.6G.

    Not unless it's a rare really bad situation.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • JUGHNE
    JUGHNE Posts: 11,653

    It is a habit I have and the wife does not.

    Also we are about 300' of 4" pipe from the 6" main. Then there are only 2 more houses before a manhole about 500' from that.

    I have always wondered how long it takes for our donations to get to that manhole.

  • ethicalpaul
    ethicalpaul Posts: 9,076

    See also "Mercy Flush" or "Courtesy Flush"

    Which are totally mythological…the smell has already escaped

    NJ Steam Homeowner.
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • leonz
    leonz Posts: 1,994

    A bidet or toilet with a three inch trap will allow a better flush speed and less clogging.

  • HomerJSmith
    HomerJSmith Posts: 2,837
    edited August 2024

    @ethicalpaul—Yes, the bureaucrats did mandate 1.6 flush, but what choice do you have. You can't buy a 3 gal flush except out of a bone yard. There are 'no flush urinals', but that's liquid waste. Solid waste is a different matter. Most waste sys are old and were designed for a 3 gal flush. There was some talk about going to a 2 1/2" soil line to facilitate solid transport with the low flush toilets.

    Added note: What would life be like with out toilet paper. Hmmm Dealing with human waste in an adequate manner is a sign of a high civilization. It is probably the main reason for the elimination of diseases that have plagued mankind for eons. Doctors think they have done it, but is was the sanitary engineers that should be credited.

    PC7060old_diy_guy
  • hot_rod
    hot_rod Posts: 28,708
    edited August 2024

    Probably a combination of the actual toilet and the operator on any given day

    I worked as a hotel maintenance plumber once. Its amazing the wide variety of loads found in toilet bowls 😯

    If you expect a potential problem get a toilet dual flush, a flushometer, or one of the pressure assisted with the Sloan pressure tank system type

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    CLamb
  • ChrisJ
    ChrisJ Posts: 17,763

    That's a big part of why I decided I'm downsizing my 4" to a 3" when I finally replace all of the cast iron with pvc. I believe the claims that a 3" pipe works better with modern toilets.

    Keep in mind, when 4" became the standard 3.5 gallon wasn't a set standard. I think that became a thing in the 1980s? Allegedly, there's many 4-5 gallon flush toilets out there, or at least was.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Jamie Hall
    Jamie Hall Posts: 27,975

    Fun detail… Rome had water carriage sewers. So did the Minoans, a thousand years earlier…

    And yes. There is a truism in the sanitary engineering trade — both design and operation. If it can be fit down a toilet bowl, it will be…

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    CLamb
  • HomerJSmith
    HomerJSmith Posts: 2,837

    The size of the soil pipe is determined by the number of fixture units, as I recollect. I hated working on soil pipes, every germ in the Universe has a home there.

  • ChrisJ
    ChrisJ Posts: 17,763

    Correct.

    And that number varies from code to code some. In my area I can use 3" for quite a bit more than I have, but I can also just go with a 4" like I currently have. I'm choosing to go down a size because I feel 3" works better with modern toilets.

    In some areas you must have a 4" and that's that, luckily my area isn't one of them.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.