Is this Expansion Tank in Attic Draining Water?
Comments
-
Where does that overflow line go? You wouldn't fill that system to a pressure, you would just fill it until that expansion tank is more or less full. In many systems that overflow line runs in to the basement so you can tell when water starts running out of the tank but it could go somewhere else too. That is why old pressure gauges were called altitude gauges and marked in feet of water so you could fill it until the pressure reached the height of the tank.2
-
-
Hello @Dairon421, If your system stays at 5 PSI.
5.0 (PSI) / 0.4335 (PSI, 1 Foot of Head) = 11.53 Feet.
I would start looking for the leak (or overflow pipe) at 11.53 Feet above the gauge, assuming the gauge is working correctly. And if that is the height of that horizontal pipe connected to the top of the tank in the picture I would find out where it goes (or drains to), just so you know.
What did the old Boiler gauge read or was it defective ?
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
The elevation from the top of that tank down to your boiler gauge will determine the most pressure you will get from that system.
If the tank is full then that is usually all you need....once all the air is out of the piping/rads.
10' will give you about 5 PSI. 30' will give you about 14 PSI.
If you keep adding water the overflow water will go somewhere.
Perhaps out onto the roof or rain gutter.
Maybe connected in the attic to the sewer vent or dropping down a wall to the basement drain lines or laundry sink.
You have 2 pipes connected into the bottom....my best guess is that one is a connection to the supply piping and the other to the return piping.
This induces water circulation into the tank, just like a radiator, to keep it from freezing in the attic.
Is there a pump on the new boiler?0 -
Assuming that tank is still active -- and it sounds like it is -- 5 psi is all you'll get unless the house is very tall. But -- that's not a problem! That's all you need, so not to worry.
I would find out where that overflow line goes, though...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
I've seen many attic tank overflows in Cleveland punched into the main sanitary stack vent. Not kosher today but Ohio didn't even have a Plumbing code until 1922 so the guys just did whatever worked prior to that.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.1 -
Those were the good old days when stuff worked forever. Some suction on overflow got air out.mattmia2 said:Where does that overflow line go? You wouldn't fill that system to a pressure, you would just fill it until that expansion tank is more or less full. In many systems that overflow line runs in to the basement so you can tell when water starts running out of the tank but it could go somewhere else too. That is why old pressure gauges were called altitude gauges and marked in feet of water so you could fill it until the pressure reached the height of the tank.
0 -
gerry gill said:
I've seen many attic tank overflows in Cleveland punched into the main sanitary stack vent. Not kosher today but Ohio didn't even have a Plumbing code until 1922 so the guys just did whatever worked prior to that.
Can you imagine that?
Guys thinking and doing what works instead of just following rules and having no idea why.
I'm not saying we shouldn't have codes. It would just be nice if more people would use their brain more.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements