Cut radiator pipe while removing old fittings
branimal
Member Posts: 228
I nicked a radiator pipe (1") while removing some old fittings. In the past I've used Blue Block to seal nicks. Not sure if this cut is too severe for Blue block. I know people use some type of plumbers rope in the threads. Forgot what that was called.
The next fitting is a 3 way tee which would be way too much work to replace.
Here are some pics.
The next fitting is a 3 way tee which would be way too much work to replace.
Here are some pics.
0
Comments
-
That's pretty deep. Yes, you can use plumbers wicking if you can find it. Basically, waxed string.
I would probably just use Teflon tape and dope. I like the regular tape, but some insist on blue monster which I don't like. My favorite dope is Rector seal True Blue.
But asking a question of will it work you will get 1000 different answers on what people would use. Everyone has their favorites.
get ready for the onslaught0 -
You're not the first one... I can think of at least two ways out of that -- but both depend on having a threader. First, try filling the cut -- completely -- with an epoxy, such as JB Weld, which will take the temperature and hardens hard. Then rethread. Second, cut the pipe a bit shorter, thread the new end, and use a coupling and a short nipple.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Is it steam or hot water? Supplyhouse.com has ball wicking. I'm guessing this is steam since the pipe is in such good condition.
Can you get to the next fitting with wrenches to unscrew the pipe out of it? That pipe looks to be in very good condition and should unscrew with the proper tools used properly.0 -
mattmia2 said:Is it steam or hot water? Supplyhouse.com has ball wicking. I'm guessing this is steam since the pipe is in such good condition. Can you get to the next fitting with wrenches to unscrew the pipe out of it? That pipe looks to be in very good condition and should unscrew with the proper tools used properly.
the system is steam.0 -
Are you going to extend this pipe....cap it or what is the plan....??0
-
You can disassemble steam pipes and fittings. If I can, anyone can.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
-
EBEBRATT-Ed said:That's pretty deep. Yes, you can use plumbers wicking if you can find it. Basically, waxed string. I would probably just use Teflon tape and dope. I like the regular tape, but some insist on blue monster which I don't like. My favorite dope is Rector seal True Blue. But asking a question of will it work you will get 1000 different answers on what people would use. Everyone has their favorites. get ready for the onslaught0
-
Agree with @pedmec; I’d remove and replace the section of pipe. Looks accessible and you can get a pipe cut to size at Home Depot or Lowes.I’ve used Ridgid MegaPress to fix errant cuts in radiant heat lines (by others ). Those were typically mid span cuts for lines that could not be easily replaced. Really saves the day for the customer.0
-
-
-
An advantage of a steam system is that you could pipe everything below the floor with a cap on your rad riser, then fire up the system to a fair bit of pressure.
Look for leaks with a mirror or cold spoon looking for condensation to show.
Unlike water systems you can shut it down for repairs without draining the entire system.
I am sure you are aware of maintaining slope on that runout and using swing 90 ells.1 -
JUGHNE said:An advantage of a steam system is that you could pipe everything below the floor with a cap on your rad riser, then fire up the system to a fair bit of pressure. Look for leaks with a mirror or cold spoon looking for condensation to show. Unlike water systems you can shut it down for repairs without draining the entire system. I am sure you are aware of maintaining slope on that runout and using swing 90 ells.
what is a swing 90 ell?
0 -
Assuming the pipe you are replacing is a horizontal run out to a rad, it should be sloped to drain back to the tee.
At the end of your new pipe, a 90 with a close nipple pointing horizontally, then another 90 to point up to the rad valve.
This would be a swing 90 set up. It gives you something to swing as the pipe expands with the steam temp.
It also allows you to have your rad valve riser adjusted to be plumb straight up for better alignment.
Usually standard practice in steam piping. You might see them in your basement for other runouts.1 -
When I nick the threads I use permatex gasket maker as pipe dope. Works excellent.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
-
The great contradiction: we must make a swing to allow for the joint to turn due to expansion and yet every joint gets frozen almost immediately and is very difficult to free, even with a cheater.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements