Venting the risers too fast can cause system balancing issues, thus uneven heating. Maybe vent the main faster if possible.National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
How high are your risers? Riser venting is usually needed only on risers at least three stories high, and often not even then.—
Bburd0 -
Two stories. But it's a duplex and we're on the second floor, so there are no first floor radiators for our steam system. The radiator vents have to deal with air both the rad and the risers.bburd said:How high are your risers? Riser venting is usually needed only on risers at least three stories high, and often not even then.
0 -
I have two 1-1/4" risers going to my second floor that are at the END of my main, about a foot before the end where the main vent is. Since I have plans to change the old steam radiator valves anyways I have thought of going to an inline valve rather than a 90 degree angle valve.
I was thinking of installing a 90 degree elbow and then install a Gorton #2 right before the radiator valve. I already have a Barnes and Jones Big Mouth at the end of my two mains. My thinking was to vent the risers so that the steam hits the downstairs and upstairs radiators at relatively the same time.
Since my risers are at the END of my main, I think this may be mildly beneficial. Probably more fun than anything. If my risers were not at the end of the main and say, half way down the main I would re-think this approach.
If the riser vent is the closest vent to the boiler the steam may rush there first and heat that radiator up first before the steam moves on to the main vent and the rest of the heating system, causing balance issues.
I'm not a pro though, so I'll wait for the real professionals to weigh in.0 -
Your idea is a good one, and it is commonly used on taller risers. Do you need it on a riser (probably about 10 feet of inch and a quarter or inch and a half?) maybe. It certainly won't hurt anything. I've been know to say that it is almost impossible to over vent a supply line, whether it is horizontal or vertical doesn't matter -- but after a certain point you aren't gaining anything for your money, as the steam front velocity becomes limited by how fast it can heat the pipe, not how fast it can push air out.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Depends.Jamie Hall said:Your idea is a good one, and it is commonly used on taller risers. Do you need it on a riser (probably about 10 feet of inch and a quarter or inch and a half?) maybe. It certainly won't hurt anything. I've been know to say that it is almost impossible to over vent a supply line, whether it is horizontal or vertical doesn't matter -- but after a certain point you aren't gaining anything for your money, as the steam front velocity becomes limited by how fast it can heat the pipe, not how fast it can push air out.
I have a 13' main and a 32' main and I needed to get them balanced. If I vent them the same, it's a bad time.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Just remove the packing from the supply valve of the top floor radiators so that air can move freely out of the riser and through the valve stem. When you hear steam entering the valve, run out of the room quickly.
(A little plumber's humor. Do not do this.)Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Did they ever use manual steam vents before automatic ones were created?JohnNY said:Just remove the packing from the supply valve of the top floor radiators so that air can move freely out of the riser and through the valve stem. When you hear steam entering the valve, run out of the room quickly.
(A little plumber's humor. Do not do this.)Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Yes. On the first coal fired steam systems.ChrisJ said:
Did they ever use manual steam vents before automatic ones were created?JohnNY said:Just remove the packing from the supply valve of the top floor radiators so that air can move freely out of the riser and through the valve stem. When you hear steam entering the valve, run out of the room quickly.
(A little plumber's humor. Do not do this.)
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
I put riser vents on my 3rd floor and I think they did improve my system. However, I wonder if they will do much on a 2nd floor with no 1st floor radiators. There might be other fun stuff to do to improve your system. How is the insulation of the mains and near boiler piping? Do you have a 0-3 or 0-5psi gauge? Can you flush your wet return? Do you have adequate combustion air? LOL just foolin'0
-
Boiler header is properly sized and piped, mains are vented, and everything else is insulated. No wet return -- we're one pipe counterflow.
Looking at other posts, tapping the supply valve for a vent seems like an option, just was wondering if there exists a pre-built solution.0 -
What the late-great Frank Gerety often did was to remove the angle supply valve at the top of the riser and replace it with a tee. The riser vent goes in the top of that tee. You'll have to shift the radiator a bit away from the riser now because you're going to use a straight supply valve off a nipple that connects to the new tee. Lining things up may not be simple, so weigh the costs (in time, money, and aggravation) against the quicker heat-up time.Retired and loving it.0
-
Are you sure you've got no returns? In decades of maintaining steam heating systems I've come across exactly one counterflow system.jfleming said:we're one pipe counterflow.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
2nd floor I wouldn't bother. I put on one my new riser I ran to the second floor just for fun and I have never noticed any difference in comfort/heating
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Wow... I live in MA and also have a single pipe counterflow system. Are they relatively rare or is it maybe just different trends in different geographic areas?JohnNY said:
Are you sure you've got no returns? In decades of maintaining steam heating systems I've come across exactly one counterflow system.jfleming said:we're one pipe counterflow.
0 -
We see them once in a while in the Baltimore area too.
@jfleming , in your situation you could just use slightly larger radiator vents.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
100% positive, New England SteamWorks came out and said so.JohnNY said:
Are you sure you've got no returns? In decades of maintaining steam heating systems I've come across exactly one counterflow system.jfleming said:we're one pipe counterflow.
We switched to the largest oriifce on the Maid O-Mist vent, which helps a lot, but it still takes a while.Steamhead said:We see them once in a while in the Baltimore area too.
@jfleming , in your situation you could just use slightly larger radiator vents.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements