Looking for motorized angle radiator valves.
The Steam Whisperer
The Steam Whisperer Member Posts: 1,323
edited July 2022 in Strictly Steam
I have a project with recessed radiator/ convectors and valves that are all motorized for zoning. They don't want TRV's. Since the motors are in the enclosures, they have to deal with high ambient temperatures, so the wax motors used by Danfoss and Tunstall are out. I am shooting for simple 24 v on/off motors.
The old valves have the big square Honeywell motors.
    Alan (California Radiant) Forbes Member Posts: 4,771
    edited July 2022
    Why not just a 24 volt zone valve? Taco, Caleffi...............
    Edit: Sorry, I just saw where you said "angle valve".
    mattmia2 Member Posts: 17,211
    Are those rated for steam? It looks like Macon makes some actuators that are motorized but it looked like they were 0-10v modulating. Maybe honeywell still makes the valves that are on there.
    EBEBRATT-Ed Member Posts: 20,394
    edited July 2022
    Honeywell VP512 is a straight or angle valve rated for water or steam. Don't know what pipe size you need or how many lbs of steam.
    The VP512 has a pneumatic actuator but you can get it with an electric actuator.
    Or you can use steam rated ball valves with an actuator but that won't be an angle valve. If it has to be an angle valve it will have to be a globe
    Probably not an off the shelf item will have to be ordered.
    Best bet is to call someone like Dodge Engineering and controls or Kele Associates
  • The Steam Whisperer
    I keep on running into a maximum ambient temp of 122F on the actuators. Just how hot is the air from convectors or the enclosure? Erie steam zone valves are rated to 169F ambient. I'll have to give Kele a call?
    The mva series actuators here are rated for over 200 degrees but lok like they are 0-10v:
    https://s3.amazonaws.com/s3.supplyhouse.com/product_files/MaconControls-MAC-N10857-Brochure.pdf
    Electronic or electric steam actuators are supposed to be mounted at a 45-degree angle with the horizontal pipe they are mounted on. This keeps (supposedly) heat from rising straight up and affecting the actuator. I don't know if this applies to Pneumatic actuators.
    Don't know how you could do this with an angle valve if the vertical pipe drops straight down.
    I looked at those, but to controlled medium is up to 203F, Max ambient is 122F.
    pecmsg Member Posts: 7,193
    Absolutely no place else it can be installed, Basement, below the rad with access door?
    If we replace the angle valve with angle valve, it has to be at the radiator. I have zone valves that are rated to 169F ambient I could use if I repipe it all.
    What about a straight valve at the bottom of the riser where the cabinet is cool?
    I think I am just going to put in an insulated divider (duct board) to keep the valve cool. Seems to be the simplest solution since high ambient valve operators don't seem to be available for angle valves.
  • Lyle {pheloa} Carter
    Lyle {pheloa} Carter Member Posts: 77
    A three-way Honeywell zone valve may work for your purposes. It is fed in through the bottom, and then exits through the sides A and B ports. By plugging off one of the ports you turn it into either a normally open or a normally closed 24 volt angle type zone valve. According to honeywell's ambient temperature chart it can handle an ambient temperature up to 200° based on the incoming heating medium.