Is this the correct tee to install a temperature gauge on a copper manifold?
newtonkid88
Member Posts: 102
Tee: https://www.supplyhouse.com/Everflow-CCFT1112-NL-1-x-1-x-1-2-C-x-C-x-F-Cast-Brass-Tee-Lead-Free
Temp Gauge:
https://www.supplyhouse.com/Resideo-GT162-1-2-NPT-Connection-Thermometer-w-2-1-2-Dial-Size
Temp Gauge:
https://www.supplyhouse.com/Resideo-GT162-1-2-NPT-Connection-Thermometer-w-2-1-2-Dial-Size
This is for 1” hePex going into 1” copper manifold. I will have to solder a Propex fitting on one end of the tee.
For baseboard heat. Any other gauges or bells and whistles you recommend? Air bleeder?
Thanks
Thanks
0
Comments
-
That should work, but when you compare a bare copper manifold to to a pre-assembled one with flow setters, isolation valves, purge and drain valves, you’ll spend more time and money trying to make your own. And usually have less functionality.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.6 -
Ironman said:That should work, but when you compare a bare copper manifold to to a pre-assembled one with flow setters, isolation valves, purge and drain valves, you’ll spend more time and money trying to make your own. And usually have less functionality.For some reason, the cost of bare copper pipe purchased at Home Depot will cost more than a bare copper MANIFOLD. I was still planning to solder my own bare manifold because the reviews for premade bare copper manifolds were bad… leaks.Any thoughts on the inverted manifolds?0
-
With a homemade manifold you want to have isolation valves, for purging, adjusting, trouble shooting. You will need a Pex adapter on all the ports also
pre-made have these components plus flow indicators, temperature gauges and usually air vents, either auto or manual. I think once you price all that, the pre built are a better options
As for that tee, temperature gauges usually hand a probe, so a standard 1x1/2 tee with a fip adapter allows you to adjust the branch length to accept the gauge
Done prefer the gauge in a well, so you need to have that on hand also. Strap on digital gauges are not a bad option, they are as accurate and fast as well type
Azel makes a nice digital gauge that reads supply and return, also shows delta T. Eliminate the tees altogether
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:With a homemade manifold you want to have isolation valves, for purging, adjusting, trouble shooting. You will need a Pex adapter on all the ports also
pre-made have these components plus flow indicators, temperature gauges and usually air vents, either auto or manual. I think once you price all that, the pre built are a better options
As for that tee, temperature gauges usually hand a probe, so a standard 1x1/2 tee with a fip adapter allows you to adjust the branch length to accept the gauge
Done prefer the gauge in a well, so you need to have that on hand also. Strap on digital gauges are not a bad option, they are as accurate and fast as well type
Azel makes a nice digital gauge that reads supply and return, also shows delta T. Eliminate the tees altogether
I plan on getting the inverted models. Is there instructions on cleaning the flowmeters when they get debris in there?0 -
Just put a tee at the first one and run down to the next manifold. No need to actually flow thru the first to the second.
yes the flow meters can be removed, but not disassembled to clean out the plastic view part. Ideally you can clean the system well, add a conditioner and keep the flow meters from getting rust colored. They are mainly used for start up balance and as an indicator that all loops are flowingBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
hot_rod said:Just put a tee at the first one and run down to the next manifold. No need to actually flow thru the first to the second.
yes the flow meters can be removed, but not disassembled to clean out the plastic view part. Ideally you can clean the system well, add a conditioner and keep the flow meters from getting rust colored. They are mainly used for start up balance and as an indicator that all loops are flowing0 -
Yes, in parallel so they both get the same supply temperature. 1" to the first, branch off to the second with 3/4.
So a 1X 3/4 tee, 1" straight through, 3/4 on the branch to feed the second manifold.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
-
1" male X 3/4 pex adapters. Find them at the box stores even, around 6 bucks at HD.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements