Reflectix/bubble wrap for staple up joist insulation
baltik
Member Posts: 21
My radiant installer swears by reflectix for insulation. We are in a very mild climate but temps do fall into upper 30s in the winter and I'd love to be as efficient as possible. A vented and unfinished crawl space is below the joists
So I've done my reading here and am fully aware that Reflectix is only rated to R1 but I have also read that if you do factor in the air pocket in a joist sealing scenario that the performance can be much better
Their literature claims r19 as a single layer and r21 as a double layer for radiant floor joist heating
https://www.reflectixinc.com/wp-content/uploads/Click-Here-to-Download-DIY-Rad-Fl-Wood-Joists-Installation-Instructions-Rev-0417.pdf
would love to hear some real-world feedback here. My inclination is to force him to stuff r19 fiber insulation but and eat the extra cost, but again would love some real world feedback
0
Comments
-
Hi, Here's a link: https://www.greenbuildingadvisor.com/article/stay-away-from-foil-faced-bubble-wrap You get the idea...
Yours, Larry0 -
Thanks Larry, I read the article before and it accurately concludes that it is terrible slab and duct insulation material and needs air space to work, which in the specific case of joists, it theoretically would?Larry Weingarten said:Hi, Here's a link: https://www.greenbuildingadvisor.com/article/stay-away-from-foil-faced-bubble-wrap You get the idea...
Yours, Larry
0 -
-
-
-
-
Please define "works well". How do you know it works better than no insulation at all?BlueGreen said:Two layers with an air gap between them works well from my own experience in my home. It's easy enough to DIY without the mess of fiberglass bats, foam, fitting rigid foam, or spray in fiberglass/cellulose.
Real insulation is rated using scientific testing procedures. These reflective product salespeople are just making up numbers.
If I called in an insulation inspection in my area and the inspector saw reflective insulation, he would fail me and make me tear it all out. If I showed him the brochure from the manufacturer stating "effective R-values" he would laugh and ask which ASTM tests they used? A real insulation report looks like this http://www.spf.basf.com/DOCS/TDS_Walltite_US.pdf, what are they using?
People use reflective insulations for 2 reasons: it is easier to install and it costs less."If you can't explain it simply, you don't understand it well enough"
Albert Einstein4 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements