Paralleling two transformers
What about a 12Va with a 40Va, in parallel?
trainer for Caleffi NA
Living the hydronic dream
Comments
-
Why?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Looking for a simple way to add more Va to switching relay boxes.
Caleffi zone relay boxes allow you to plug in two 40Va transformers for 80VA.
But the switching relays have a 12Va populated on the board. Since we use the same enclosure, extra transformers could snap in, but would need to be wired properly.
A bit of trial and error and it seems to be working.
Mainly to add enough Va to power smart/ wi fi stats.
I've heard multiple reasons why some brands of those stats pull high current. One thought is when they go into battery recharge a year or so down the road they overload the transformers. Another thought is the wi fi function pulls the current? Do you know?
Here are a couple of my trainer boards I'm experiment with. Luckily they have circuit protection on the transformersBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I'm not an electrical engineer, but I play one on TV. I have never read anything about transformers in parallel having to be the same except for voltages on the primary and secondary, but whata I know.
I've talked about the spark test on this site before and receiving a lot of derision. Using a volt meter works, too, and I posted that procedure as well.
The spark test consists of tying the primaries of the two transformers together and tying one secondary from each transformer together, and then striking the other two secondaries, quickly, against each other and observing the resulting spark and then reversing the secondary of one transformer and then striking the two untied secondaries against each other, again, and observing the spark. The spark that is the smallest is the connection that is phased correctly.
I don't see a reason why the transformers have to be matched as to VA or brand. Maybe, inductive reactance?1 -
I've watched a handful of You Tube, from HVAC guys to engineers, they all claim the Va need to match. One even suggested un-wraping some of the secondary windings to match same Va transformers exactly!HomerJSmith said:I'm not an electrical engineer, but I play one on TV. I have never read anything about transformers in parallel having to be the same except for voltages on the primary and secondary, but whata I know.
I've talked about the spark test on this site before and receiving a lot of derision. Using a volt meter works, too, and I posted that procedure as well.
The spark test consists of tying the primaries of the two transformers together and tying one secondary from each transformer together, and then striking the other two secondaries, quickly, against each other and observing the resulting spark and then reversing the secondary of one transformer and then striking the two untied secondaries against each other, again, and observing the spark. The spark that is the smallest is the connection that is phased correctly.
I don't see a reason why the transformers have to be match as to VA or brand. Maybe, inductive reactance?
I did the spark test, got them wired properly after one fuse pop. It seems to be working, transformers are not heating up. So, essentially I should have 52Va available?
Any thoughts on why some stats draw high current?
Not a factory approved hack, by the way.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Hot Rod, used to use this method when adding additional VA to Carriers early heat pumps.
1. Connect 115 volt primary leads from additional transformer to same points as primary leads of existing
transformer/
2. Attach one 24 volt secondary lead from new transformer to terminal "C" of existing transformer.
3. Apply power & measure voltage between unconnected 24 volt lead on new transformer and terminal "R"
on existing transformer.
If voltage is "0" transformers are in phase.
If 50 volts (approx) is measured reverse primary leads of one transfer & recheck for " 0" volts.
Perhaps this will help.
John Pughe
4 -
"why some stats draw high current?" The design of the circuit, I would think. I don't know whether the stat has a charging capacitor or a battery. They don't publish their designs. I would think a charging capacitor as batteries wear out (limited charging cycles) and are larger. My supposition.
As far as matching transformers parameters, I'm not as much interested in the consensus as I am interested in knowing why.0 -
Two transformers of different VA rating can be paralleled if three things are observed.
https://pressbooks.bccampus.ca/singlephasetransformers/chapter/paralleling-transformers/
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.3 -
Yes, thanks that method seem a bit more professional. Although R&C are not always labeled.Pughie1 said:Hot Rod, used to use this method when adding additional VA to Carriers early heat pumps.
1. Connect 115 volt primary
transformer/
2. Attach one 24 volt secondary lead from new transformer to terminal "C" of existing transformer.
3. Apply power & measure voltage between unconnected 24 volt lead on new transformer and terminal "R"
on existing transformer.
If voltage is "0" transformers are in phase.
If 50 volts (approx) is measured reverse primary leads of one transfer & recheck for " 0" volts.
Perhaps this will help.
John PugheBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
the resulting power source may no longer be class 2. technically the low energy section of the code says you can't tie 2 class 2 power supplies together.0
-
The article @Ironman provided covers it quite nicely. Itis quite reasonable to assume that two transformers of the same rating from the same manufacturer will match well. It is quite unreasonable to assume that two transformers of different ratings will match, and if they even if do, they they won't share the load in accordance to their rating. The best case will be that they will share the output equally -- so that in your case, 40 VA and 12 VA -- you will almost certainly overload the 12 VA transformer if you draw more than 24 VA from the circuit. It may not fry immediately, but it will fry. In most cases, the phase angle will be slightly off, resulting in those circulating currents mentioned, which will overheat both transformers until the smaller one goes poof.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
@hot_rod , I have never liked or recommended paralleling transformers. On a late-night no-heat call, it's way too easy to get the wires reversed and blow them.
With that said, in the second pic you posted, the existing transformer plugs into a jack on the board. There is second, identical jack right above. If that jack is configured to accommodate a second factory-supplied transformer, it would overcome this problem.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
Jamie Hall said:The article @Ironman provided covers it quite nicely. Itis quite reasonable to assume that two transformers of the same rating from the same manufacturer will match well. It is quite unreasonable to assume that two transformers of different ratings will match, and if they even if do, they they won't share the load in accordance to their rating. The best case will be that they will share the output equally -- so that in your case, 40 VA and 12 VA -- you will almost certainly overload the 12 VA transformer if you draw more than 24 VA from the circuit. It may not fry immediately, but it will fry. In most cases, the phase angle will be slightly off, resulting in those circulating currents mentioned, which will overheat both transformers until the smaller one goes poof.
My reasoning is this.
Let's say you have a 40va and a 12va xformer and they both run around 27v unloaded. As you load them down the 12va is going to drop faster than the 40 so the 40 will pick up the slack.
Just because the output of the smaller one drops more than the bigger doesn't necessarily mean it's overloaded.
@hot_rod unfortunately people say a lot of things and they often aren't true. I'm talking about the YouTube people not Jamie.
Unwrapping a winding seems like it would drop voltage not current carrying capacity. That would go by wire size not the turns.
I don't know though, I've always matched them and never really put thought into it. A simple bench test would prove it though, just make sure you go extreme. Meaning a small and a much bigger one and load the circuit down and see what happens. If the smaller one gets too hot you know it'll have an issue.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Steamhead said:@hot_rod , I have never liked or recommended paralleling transformers. On a late-night no-heat call, it's way too easy to get the wires reversed and blow them. With that said, in the second pic you posted, the existing transformer plugs into a jack on the board. There is second, identical jack right above. If that jack is configured to accommodate a second factory-supplied transformer, it would overcome this problem.
So the 3,4,5 or 6 zone can all have 80Va
The 5 and 6 version include both transformers in the box, or add a replacement transformer to the 3 &4, that we have with molex connectors on them. So a safe UL listed option for the zone valve box.
The common installer question that comes in is how to use 4 nest thermostats on a pump relay box that has a 12Va transformer built on the board? Or any brand of power sterling stat.
My though was to find a way to do this within the relay boxes that have only 12 Va in them.
Although any modification does negate the UL listing, even if done safely and correctly, I’m told.
My prototype shown is working, but I need to load it up as Jamie mentioned
The post that @Ironman attached claims different Va transformers can be matched successfully.I think the are talking large power line transformers.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Measuring the current in the various branches unloaded and under load will quickly answer that question. I think it has a little to do with the exact design of the transformer and how the terminal voltage relates to the current of both transformers.hot_rod said:The post that @Ironman attached claims different Va transformers can be matched successfully.I think the are talking large power line transformers.
0 -
So @hot_rod Bob is now in the R&D Department... NICE!
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Truth to tell with the little guys we play with -- so long as they are approximately in phase (see the tips above) it probably doesn't make much difference. Where it starts to get fun is with bigger transformers. Never mind paralleling bigger generators.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Used to used to be a fellow from Honeywell that hung here on the wall, 2003-2008 years. He had good answers to all control questions and Honeywell specific questions. BillW I think was his handle?
savy hydronic and HVAC troubleshooters always kept a 75va transformer on the truck. As @Steamhead mentioned, sometimes you had to parallel a couple 40’s to get the heat back on. I think it was Bill that was one of the first to confirm it could be done and how to do to properly, here at HH.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Now you made me go digging! I printed off the post from May 2000👍🏻Found some post even older from Paul with an interesting email address. S8610U@aol.com. He knew a lot about controls also, maybe a HW guy?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I remember billw. I hadn't been here for a while and he was gone when I came back. I've wondered what happened to him a few times.hot_rod said:Used to used to be a fellow from Honeywell that hung here on the wall, 2003-2008 years. He had good answers to all control questions and Honeywell specific questions. BillW I think was his handle?
0 -
Just a side note, those automotive fuses are only good for 32 volts I think....not 120V. Use a glass fues with the little plastic twist lock fues holder.
I think the real answer for Caleffi and Taco is that they should be making relay boxes with a 80va transformer and the "C" terminal at every zone.
For what it's worth, I always just take out the small transformer and put in a 75 when I have more than 1 smart stat.
Serving Northern Maine HVAC & Controls. I burn wood, it smells good!2 -
Solid_Fuel_Man said:Just a side note, those automotive fuses are only good for 32 volts I think....not 120V. Use a glass fues with the little plastic twist lock fues holder.
I think the real answer for Caleffi and Taco is that they should be making relay boxes with a 80va transformer and the "C" terminal at every zone.
For what it's worth, I always just take out the small transformer and put in a 75 when I have more than 1 smart stat.
Plastic blade fuses are ok on 24vac but they have no business being used on 120vac stuff.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Good catch on the fuse, thanks.Solid_Fuel_Man said:Just a side note, those automotive fuses are only good for 32 volts I think....not 120V. Use a glass fues with the little plastic twist lock fues holder.
I think the real answer for Caleffi and Taco is that they should be making relay boxes with a 80va transformer and the "C" terminal at every zone.
For what it's worth, I always just take out the small transformer and put in a 75 when I have more than 1 smart stat.
The Caleffi ZVR relay boxes for zone valves come with two 40Va in the 5 and 6 zone version, the extra transformer can be added to the 3&4. The 120V side has a self resetting fuse. All our relays have R,W and C connections for stats, FYI.
Trying to decide if adding a 40Va or more to the pump relay box is worth the cost and having it run through UL again. We see more and more smart stats being used and the 12Va currently on the board doesn't provide adequate Va.
I was just looking at work around options, with the board we have now that has the 12Va included.
Requests like the one attached:Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
How sensitive are those Smart stats to voltage drop ? Voltage drop (loss) on a wire is related to the current flow and the resistance (gauge) of the wire. Probably not applicable for a regular home, but a mansion or commercial building maybe ?
30+ yrs in telecom outside plant.
Currently in building maintenance.0 -
It probably gets regulated or converted to 3.3 v or 5v so it will never be an issue.Dave Carpentier said:How sensitive are those Smart stats to voltage drop ? Voltage drop (loss) on a wire is related to the current flow and the resistance (gauge) of the wire. Probably not applicable for a regular home, but a mansion or commercial building maybe ?
0 -
@hot_rod a single 280 watt source would not be class 2. there would be too much energy available to a fault that it could start a fire. It would have to be divided in to multiple smaller sources or at least each circuit would have to have individual overcurrent protection that was smaller than the output of the source(i don't know the exact rules, i only know the intent). Cascadable zone controllers would make the most sense here where they have inputs and outputs to connect things like the end switches/heat call together and some way to make a priority call global over all the controllers. It is also of note that each individual connection to a t-stat only carries 1a so using #16 control wiring would not be necessary.0
-
I agree, just daisy chain the relay boxes with 40 or 80 Va onboard each box, would cover large zoned options. And you get a factory built, UL listed solution.mattmia2 said:@hot_rod a single 280 watt source would not be class 2. there would be too much energy available to a fault that it could start a fire. It would have to be divided in to multiple smaller sources or at least each circuit would have to have individual overcurrent protection that was smaller than the output of the source(i don't know the exact rules, i only know the intent). Cascadable zone controllers would make the most sense here where they have inputs and outputs to connect things like the end switches/heat call together and some way to make a priority call global over all the controllers. It is also of note that each individual connection to a t-stat only carries 1a so using #16 control wiring would not be necessary.
That was a typical call or question tech support gets often that I attached above.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements