Are mini split ceiling cassettes an option without access from above the cassettes?
Sounds like you may need a new installer. There are also ducted min splits that can be concealed somewhere where they are serviceable.0
What type of ceiling are you mounting them in?
If there is no ceiling access, how do you expect they can be installed?
Most of the cassettes I have looked at have limited condensate head pumping ability.
Is this an existing ceiling/house or new construction?0 -
If you had an access panel in the right spot it might be ok.0
Check out the Mitsubishi MLZ series. Designed to fit between 16" joists. All components can be accessed from the ceiling opening by taking off the grille, including the flare nuts and pump. Just roughed in my first one last week, so don't have any operational feedback yet, but overall was impressed with the unit0
Ceiling cassettes use a condensate pump that many people complain about the noise. Mostly from bedroom installations.0
This is the upstairs, which until our renovations had a ceiling consisting of the sloped roof rafters, with OSB nailed to the rafters. Now, I have finished the ceiling in pine tongue and groove boards, and created a flat, dropped ceiling about 4 1/2 feet wide, dropped about 20 inches from the ridge rafter. That flat ceiling will also be clad with pine boards, and the flat ceiling will contain several 6 inch wafer LED lights, two ceiling fans, and serves as a chase through which some Romex runs from end to end. The cassettes would go into this small dropped ceiling. The only way to gain access from the top for future service would be to create access hatches by cutting open the roof -- so obviously not an option there.EBEBRATT-Ed said:What type of ceiling are you mounting them in?
If I'm reading the specs correctly, this proposed Mitsubishi cassette installation would make for less convenient access for future repairs, but would not make future repairs impossible, right? It appears that all the guts of the cassette can be cleaned, serviced, repaired or swapped out from below. If that is correct, for the sake of aesthetics, it's worth the trade-off to me to create inconvenient future service access for the benefit of not having to install what I consider to be ugly wall-hung condenser/blower heads. I just want to make sure I'm not creating an impossible-to-service scenario.0 -
I would stick with the wall mounts0
I despise the wall tumors, there's nothing uglier than them.
If the paperworks say it can be serviced 100% from below, you should be ok—I'd complete the lineset pressure test prior to closing it up.
Alternately, you should be able to fabricate a removable panel for that ceiling with nothing more obvious than the edge cuts of the panel itself.
From a service standpoint I'm not a fan. It's not always possible or desired to go with a wall mount. Here is a job we are in the process of installing a ceiling mounted unit at. It's in a third floor attic build out so space was limited.
Owner of Grunaire Climate Solutions. Check us out under the locate a contractor section. Located in Detroit area.
1
