Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Stuck Rehau gauge
Rayh7777777
Member Posts: 2
Several of my 17 main floor Rehau gauges are stuck and not reacting to a change in flow rate all showing zero. Any suggestions on methods to unstick them?
0
Comments
-
You have to isolate the manifold and take them out and clean them. Sometimes they'll free up as you're unscrewing them from the manifold.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The bottom of the gauge where it contacts the inside of the manifold creates a sort of screen. I have had issues with those screens clogging. They are pretty easy to take apart and clean."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Thanks for your answers.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements