Old cast iron radiators
joseph annon
Member Posts: 54
I am currently working on a remodel of a home that has Crane cast iron radiators. The inspector is requesting and air test on the radiators at 60PSI.
To clarify where I am (Santa Fe New Mexico) cast iron radiators are rare and steam even rarer especially in residences. So I do have a lot of experience with cast iron radiators other that servicing boilers on water radiators.
What are your experiences in these cases? Am I going to see air leaks in the system due the pressure being 5X what the system has seen?
We are also shortening a coupling of radiator runs. What should I look for in the radiator push nipple connectors while doing this alteration.
To clarify where I am (Santa Fe New Mexico) cast iron radiators are rare and steam even rarer especially in residences. So I do have a lot of experience with cast iron radiators other that servicing boilers on water radiators.
What are your experiences in these cases? Am I going to see air leaks in the system due the pressure being 5X what the system has seen?
We are also shortening a coupling of radiator runs. What should I look for in the radiator push nipple connectors while doing this alteration.
There was an error rendering this rich post.
0
Comments
-
I can't guarantee you will see leaks at 60 psi -- but I'd be real surprised if you didn't. The real question, though, is were these steam or hot water? And if hot water, what is the pressure relief valve setting? if it's the standard 30 psi, you do need a pressure test at twice the relief valve setting.
However, if at all possible, persuade him to let you test with water, not air. Please. Air is easier, I'll grant you. However, if there is a crack or defect, and it lets go, you are in a world of hurt if you are anywhere in the vicinity -- whereas with water all you are is wet.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
That’s way too much pressure on the rads.
The inspector needs to use a little common sense and realize that those rads were never meant to take that kind of pressure anymore than the boiler could. If the rads are presently connected, why is a pressure test required? You can’t apply today’s code to something that’s been there for 100 years.
If you’re running new piping to them, only the new piping should be required to be tested.
If you’re shortening radiator lengths, you could have push or threaded nipples. If there are no draw rods, the rad will have threaded nipples and you’ll probably need a machine shop to deal with them. If they have push nipples, you may still need a machine shop to make new ones if the old ones are pitted.
I’ve had to deal with a local inspector who could be a little too aggressive, and who would invent requirements not in the code about pressurizing old rads, and he finally came to agree that 30 psi was all that was needed.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
They are cast iron hot water baseboards. Made by Crane and are type R baseboards. There are signs that the coin vents leaked (corrosion). I did ask if I could use a water test instead of air. Inspector said they would be OK with 60PSi air. Relief valve will be 30 PSI. I will mention to him the possibility of catastrophic failure under air and see if he will let me do a water test. The areas where we have new piping to them is all in Pex home runs.
The baseboards that have been removed have push nipples. The push nipples look clean. They are 3/4" connectors. The end radiators have threaded connectors.There was an error rendering this rich post.
0 -
60 psi air is NOT equal to 60 psi water: it’s 2.31 times greater.
In a dry sprinkler system, 45 psi is used to hold back 100 psi street water pressure. Like Jamie said, see if you can use water.
Do you have the draw tool to re-assemble the BB sections?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I'll look into water pressure vs air pressure and present it to the inspector. I do not have a draw tool for the sections. What are the options for draw clamps? I will more than likely not need the tool again.
There was an error rendering this rich post.
0 -
some supply houses or online suppliers will rent or loan the tool0
-
-
Where can find something to support the need to use a water test instead of an air test. I have found a local contractor who will loan me his draw tool.
There was an error rendering this rich post.
0 -
I believe you can find it in the plumbing code where it says it requires a hydrostatic pressure test0
-
I think this publication should have your answer if you can find someone who has access to it.
https://webstore.ansi.org/preview-pages/IAPMO/preview_IAPMO+IGC+332-2017a.pdf
We used to test our hydronic installations on some jobs with air where water was not readily available. Often, the inspector demanded a hydrostatic test.
On plumbing work, the UPC allowed a 4 psi air test which equals a 10 foot column of water above the highest fitting which is the normal test.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I’ll be honest, you shouldn’t need a code or a rule. It’s called common sense.joseph annon said:Where can find something to support the need to use a water test instead of an air test. I have found a local contractor who will loan me his draw tool.
If there is some kind of catastrophic failure at 60 PSI, the shrapnel can and will send someone to the emergency room, or the morgue. This isn’t a joke.
Your inspector is dumb as a box of rocks. I feel no need to be polite in this situation considering the stupidity that is being expressed by that person.
If one uses water that changes the entire discussion.
The mention of 4 PSI is much more sensible.
In all seriousness I can’t believe this conversation is happening.1 -
I think psi is a unit of pressure, not density. 30 psi air = 30 psi of anythingIronman said:60 psi air is NOT equal to 60 psi water: it’s 2.31 times greater.
In a dry sprinkler system, 45 psi is used to hold back 100 psi street water pressure. Like Jamie said, see if you can use water.
Do you have the draw tool to re-assemble the BB sections?
Now a column of water is where the 2.31 comes into it, maybe? .433 psi per foot of water column
In a dry sprinkler system valve it's the surface area difference between the air and water side that allows a lower air side pressure.
A lower psi air test is sometimes used as explained here.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2 -
it's that the air is compressible,
so there's more of it to "let go" if bad things happen,
you'll pump more air in the system than water to hit that 60 psi,
air will go PUUSSHHH,
water will just go pu_opknown to beat dead horses0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements