Piping steam radiator to perfect height without shimming
My setup is as follows:
1. old 1" pipe coming up thru the floor
2. new bushing 1 1/4" --> 1"
3. 1 1/4" extension
4. 90 elbow
I bought the 1 1/4" extension vs a close nipple and coupling b/c that's all my hardware store had in stock. Can a close nipple and coupling provide a lower height profile than an extension?
Comments
-
You could also put a reducing bushing on the radiator (looks like there might be a 1.5 -> 1.25 on there now, it could be replaced) and then have just 1" stuff which would let you get away from that reducer on the vertical
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Yup paul. That’s what I’m thinking. Local hw didn’t have 1” couplings either. I’ll pick one up at Hd next time I’m there.0
-
Unless the bushing is eccentric, a reducing bushing on the radiator will allow water to pool in the bottom. Reducing the vertical is always better for drainage. Also, if you could use a 45° elbow, water won't stay in the valve body.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-242 -
@branimal no a coupling and a nipple will raise the radiator
I think you have it as close as your going to get it.
Your supply pipe is 1" if you changed to a 1" valve with 1" fittings being smaller you might be able to get it closer
Your piping between two fixed points that don't change, the pipe through the floor and the height of the radiator. With only a couple of threads in between it can be tough to get it exact
Why not stain some wood to match the floor and cut it up and use it for shims?1 -
You're not wrong theoretically but all my radiators have them without issueHap_Hazzard said:Unless the bushing is eccentric, a reducing bushing on the radiator will allow water to pool in the bottom. Reducing the vertical is always better for drainage. Also, if you could use a 45° elbow, water won't stay in the valve body.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
-
What is below the floor in that photo? Is it the basement with easy access to install a shorter nipple thru the floor? Or is it on the second (or third) floor with a finished ceiling below it?
Sometimes you want to fix a future floor settling problem today and not when you are much older and have a hard time getting into the tight spaces you could when you were a kid.
A street 45° with a new floor opening, an eccentric bushing 1-1/2" to 1", and a shorter nipple thru the floor is ideal. But we all can't always get what we wish for and may just have to go with what is available.
Nice floor
Mr.Ed
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
-
ScottSecor said:
I do not recall ever doing it, but I've seen many radiators that had the legs shortened. In other words the legs were say three inches long and now there two and a half inches long. I suspect a portable band saw would make it pretty easy to do.
"No matter how many times I cut the legs on this radiator, they are still too short!"
I think you might be going in the wrong direction Scott. I believe he wants to eliminate the shim. It will look better without them on that new floor.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
@EdTheHeaterMan , you are correct and I am mistaken.
@branimal if you got rid of the reducing bushing on from the vertical one inch riser and convert everything to one inch it would be significantly lower (shorter). However, I suspect you don't want to do the entire job over again. Along those same lines (most will disagree with me) I see almost no need for a radiator angle stop, a regular black malleable union would do the job.1 -
Wait a few years. One of my radiators has started heating very slowly and making bubbling noises. I increased the pitch as far as I could, which seemed to help a little, but the steam still doesn't get far enough to close the vent before the end of the cycle. I haven't disconnected it to look at it yet, but I'm almost positive the problem is inside the radiator.ethicalpaul said:You're not wrong theoretically but all my radiators have them without issue
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
Maybe mark the shims at each leg then use a 1" hole saw on each shim.0
-
If you have enough room, you might consider getting a marble threshhold to put under the radiator. I've done this with a couple of my radiators, and it really looks nice. It also lets the legs slide when the radiator expands without making any noise.
Another possibility is to use radiator pedestals. These are like little cast iron foot extesions that almost look like they're part of the radiator. They'd need to be shortened to fit.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
Take the reducing bushing and extension off the riser, replace it with a reducing ell with the outlet perpendicular to the wall, screw a street ell in to that at whatever angle you need to screw it in to the radiator valve, you will need a nipple on the other end of the street ell, wither at the reducing ell or between the valve and the street ell. The length of that nipple could give you some flexibility.0
-
Initially I had it piped with a 45 elbow. This would have required large shim blocks.Hap_Hazzard said:Unless the bushing is eccentric, a reducing bushing on the radiator will allow water to pool in the bottom. Reducing the vertical is always better for drainage. Also, if you could use a 45° elbow, water won't stay in the valve body.
0 -
Thanks Ed. Is there a chart the lists heights of black pipe fittings? I always do a dry run to see how things fit. With cast iron plumbing pipes there are charts where you can get a good idea on how things will measure out.EBEBRATT-Ed said:@branimal no a coupling and a nipple will raise the radiator
I think you have it as close as your going to get it.
Your supply pipe is 1" if you changed to a 1" valve with 1" fittings being smaller you might be able to get it closer
Your piping between two fixed points that don't change, the pipe through the floor and the height of the radiator. With only a couple of threads in between it can be tough to get it exact
Why not stain some wood to match the floor and cut it up and use it for shims?
Regarding the shims, yeah I might end up doing just that. I did that for another radiator. Cut some matching hardwood flooring scraps to size and rounded over the edges. Stain and poly. Hopefully they won't even be noticed.
Here are the shims I made (1 1/16" thick) for another radiator. I still have to stain and poly the routed edges.
0 -
Below this is the 2nd floor apartment. I will be renovating that next. So maybe I'll repipe it then. A 45* would be ideal. I thought laying my valve on its side would cause water pooling in the valve body and hence hammering. But no problems yet. Today should be a cold day in NYC so I'll see how she holds up.EdTheHeaterMan said:What is below the floor in that photo? Is it the basement with easy access to install a shorter nipple thru the floor? Or is it on the second (or third) floor with a finished ceiling below it?
Sometimes you want to fix a future floor settling problem today and not when you are much older and have a hard time getting into the tight spaces you could when you were a kid.
A street 45° with a new floor opening, an eccentric bushing 1-1/2" to 1", and a shorter nipple thru the floor is ideal. But we all can't always get what we wish for and may just have to go with what is available.
Nice floor
Mr.Ed0 -
Interesting idea. I do have a reducing elbow in my parts box. Just need to get a street elbow.mattmia2 said:Take the reducing bushing and extension off the riser, replace it with a reducing ell with the outlet perpendicular to the wall, screw a street ell in to that at whatever angle you need to screw it in to the radiator valve, you will need a nipple on the other end of the street ell, wither at the reducing ell or between the valve and the street ell. The length of that nipple could give you some flexibility.
0 -
Pipe fittings vary a lot from one manufacturer to the next. You need to use trial and error.
I think the radiator with the two blocks under the feet would look great on a piece of marble threshhold. You definitely want something under those feet or else they'll ruin that flooring.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
-
Is the flooring you posted laminate or LVP? Would that sort damage occur to 3/4" thick white oak floors? I was under the impression that the hardness of oak floors would resist depressions from radiators.Hap_Hazzard said:Pipe fittings vary a lot from one manufacturer to the next. You need to use trial and error.
I think the radiator with the two blocks under the feet would look great on a piece of marble threshhold. You definitely want something under those feet or else they'll ruin that flooring.
This is the largest radiator I have and it's been sitting on the floor for 3 days with no damage so far. Maybe that changes over time. I got lucky on the pipe height for this rad - it was a perfect fit.
0 -
@branimal pipe fitting measurements
http://www.pipe-valve-fitting.com/wp-content/uploads/2013/02/Pipe_Fittings.pdf1 -
It must be vinyl, but it wasn't supposed to do that. I'm sure the damage to solid hardwood flooring would look different, but I wouldn't trust it not to do any damage. Eventually I plan to put marble slabs under all of my radiators.branimal said:Is the flooring you posted laminate or LVP? Would that sort damage occur to 3/4" thick white oak floors? I was under the impression that the hardness of oak floors would resist depressions from radiators.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
mattmia2 said:Take the reducing bushing and extension off the riser, replace it with a reducing ell with the outlet perpendicular to the wall, screw a street ell in to that at whatever angle you need to screw it in to the radiator valve, you will need a nipple on the other end of the street ell, wither at the reducing ell or between the valve and the street ell. The length of that nipple could give you some flexibility.1
-
-
You chose a great wood and I wouldn't worry and go overboard as the
White Oak Hardwood is strong with a tight grain
It gets a Janka rating of 1360, it comes harder than the Red Oak.
I'd even let it be and see what it looks like in a season...If you cover the floor no one will see it now or later anyway.. you might as well get the benefits of the wood and the premium price you paid and show it off..
Just my 2¢ ✌️One way to get familiar something you know nothing about is to ask a really smart person a really stupid question0 -
What's the Janka rating of cast iron?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el3 -
ethicalpaul said:What's the Janka rating of cast iron?
but you already knew this. 😶Brinell hardness will scale the hardness of materials by the penetration depth of an indenter, which means we need to punch a small pit on the surface of the metal castings.
The Rockwell hardness determines the hardness by measuring the depth of penetration of an indenter under a large load compared to the penetration made by a preload.
The Vickers hardness has the same basic principle as with all common measures of hardness, is to observe the questioned material's ability to resist plastic deformation from a standard source.
One way to get familiar something you know nothing about is to ask a really smart person a really stupid question1 -
If the issue is that is slides around and cuts in to the floor as it slides you could put pieces of moderately thick synthetic rubber of plastic sheet under the feet.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements