Capitol Steam Boiler

Alan (California Radiant) Forbes
Member Posts: 4,317
Every now and then I get a call to service a steam heating problem. This one was a flooded boiler that probably over filled because someone was messing around with the manual fill valve.
I drained the boiler completely and checked the LWCO for continuity before and after it was drained just to make sure it was working properly and it was. Dropped the operating Pressuretrol from 2.5 psi to .5 psi.
I believe that this is the original boiler from when the house was built in 1919. I love the old stuff!








I drained the boiler completely and checked the LWCO for continuity before and after it was drained just to make sure it was working properly and it was. Dropped the operating Pressuretrol from 2.5 psi to .5 psi.
I believe that this is the original boiler from when the house was built in 1919. I love the old stuff!








8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
2
Comments
-
According to some of my Dead Men's Books, that boiler is about 40% efficient...........All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Now that I'm back in the office looking at the pictures, I see that the pressuretrol has a subtractive differential. When I adjusted the setting down to .5 psi, shouldn't the boiler have turned off with the differential set to 1?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Better check the wiring on those two pressure controls. The pressuretrol is subtractive, as you note -- and while the boiler may have turned on, once it turned off on that pressuretrol, it shouldn't restart.
Of considerably more concern to me, however, is the mercury switch pressuretrol appears to be in the off position in the picture -- and the boiler shouldn't be able to run at all. That one is, I think, manual reset.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thanks, Jamie. Good eye on that high limit. That picture was taken before I drained the boiler and before I reset the high limit.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements