Line Voltage Thermostat

I was testing the wiring on a boiler replacement and got a tic tracer beep with the thermostat both on and off and couldn't understand until I realized that they split the neutral at the thermostat instead of the hot.

My meter reading with the thermostat on was 110 volts and 56 volts with the thermostat off. Why am I not getting zero volts with a disconnected neutral?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

Two btu per sq ft for degree difference for a slab

Comments

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378
    edited February 2022
    I can't be 100% sure without looking at the job, but the windings on the motor or resistance coils on the heating unit that thermostat is operating is allowing the voltage to back feed to the thermostat junction box. That resistance is the reason for the voltage drop on your meter. An old Simpson analog meter will be more forgiving and realistic with that kind of voltage reading. (never did like them con-found digital meter contraptions)

    OR

    You have a DIY Homeowner wiring something off that circuit because it was the closest electric he could find to make the impromptu wiring hack.

    Disconnect the wire at the source and see if there is still power at the thermostat. If there is, then it's the DIY Hack

    Stay safe. You may want to know that many of my old customers were SHOCKED to find out that I wasn't the best electrician

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Alan (California Radiant) ForbesLarry Weingartenwmgeorge
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,474
    Are you sure they split the neutral? Assuming a two wire line voltage stat they would usually just run 1 cable with a black and a white wired like a switch loop.

    Whatever they did I agree with @EdTheHeaterMan digital meters can and do give false readings sometimes.

    An analog meter puts some load on a circuit, a digital does not so the digital picks up transient voltages sometimes


    I had a flourecent light fixture once that the installer did not ground the fixture, it was mounted on a block wall, the power supply came in the back of the fixture with no ground wire and no metal connection to a conduit or flex.

    Emt came out of the light fixture down to a metal switch box. Checking with a digital meter showed the EMT was "Hot".

    An analog meter showed nothing. You could touch the EMT nothing there.

    Picking up some transient off the ballast. We ran a scrap piece of wire to a conduit that was grounded to check against
    HVACNUT
  • wmgeorge
    wmgeorge Member Posts: 222
    My newer digital Fluke has a setting that puts a little load on the circuit, its optional of course.
    Old retired Commercial HVAC/R guy in Iowa. Master electrician.
  • HVACNUT
    HVACNUT Member Posts: 6,331
    edited February 2022
    Why is there a neutral at the thermostat? Is it wired from the panel to the emergency switch to the thermostat to the system? Probably not. 
    Zman
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378
    HVACNUT said:

    Why is there a neutral at the thermostat? Is it wired from the panel to the emergency switch to the thermostat to the system? Probably not. 



    Why not? It would work.

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Yes, that would work, but as I said, the hot wire is always energized at the boiler; thermostat on or thermostat off.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • HomerJSmith
    HomerJSmith Member Posts: 2,635
    I'm kinda dumb. I don't quite know what you did or what was the situation in how you were measuring. Was it a 110 V or a 220 V thermostat? I suspect a 110 V thermostat.

    AC is a two way traveler on a conductor. Measuring a hot lead to ground will give you a 110 V reading, measuring a "grounded conductor", erroneously more commonly referred to as a "neutral", will give you a reduced voltage in line with what you saw.

    That's my take on the issue without further understanding.
  • hot_rod
    hot_rod Member Posts: 23,387
    Bad t-stat? Is it a mechanical or digital stat?
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • wmgeorge
    wmgeorge Member Posts: 222
    edited February 2022
    If you read across an open switch, you will (might) get a reading because the device is in the circuit. My guess its not on a grounded box nor is the neutral available, that is what he is seeing.
    Old retired Commercial HVAC/R guy in Iowa. Master electrician.
  • Jamie Hall
    Jamie Hall Member Posts: 24,852
    If the hot wire is always energized at the boiler, but the thermostat will turn things on and off... there may be a serious wiring error: the neutral should NEVER be switched. It sounds as though it might be. Another possibility is that someone wired an extension leg -- like the lower arrangement in @EdTheHeaterMan 's diagram -- and neglected to mark the white wire of the two wire cable they were using with black (or red). That's another no-no. You can use a two wire cable -- white and black -- that way, but only if the white is marked.

    I'd be mightily inclined to trace back all the wiring -- not just the cable -- and find out who did what. Or at least what had been done.

    Phantom voltages are a first class bore. I have a nice little test light (made it myself) consisting of a wire with an alligator clip, a 5 amp fuse, a 4 watt night light bulb in a socket, and another wire with an alligator clip. Made it because I got tired of scratching my head over phantom voltages on ungrounded BX cable (don't ask and I won't tell). Clip one end to the perplexing wire and the other end to ground. If the wire is genuinely hot the light will glow cheerfully. If it doesn't glow, now measure the voltage -- it it's a phantom, the rig will ground it out to zero.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    Solid_Fuel_ManEdTheHeaterMan
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    High impedance digital meters can do that....

    I have a Klien clamp on meter with a separate "LOW Z" position on the dial. It mimics what @Jamie Hallis talking about. The meter was $120,  no need for Fluke expensive meter for that. 


    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
    EdTheHeaterMan
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,378

    Yes, that would work, but as I said, the hot wire is always energized at the boiler; thermostat on or thermostat off.

    This diagram would explain your statement Alan


    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

  • Yes, that does. Thank you, Ed and everyone else!