seized pump--steam boiler hot water loop
Recently added a hot water loop to a steam installation to heat a basement space--about 100 feet of 3/4" copper and 25 ft of baseboard radiation. Adjusted to operate at or below 180 degrees, and used a TACO 006-B4 brass pump.
After a couple of hours of operation pump seized. I was able to free it manually by dis-assembling it, but a couple of days later it happened again. Not an issue of dirty water, it
was just internally stuck.
Photo attached--boiler is located immediately to right of photo. This is my first installation of this type--I'm scratching my head.
dave
    ethicalpaul Member Posts: 8,933
    edited February 2022
    That's up pretty high. How does it compare to the water line? For a steam boiler water loop you have to rely on the static pressure of the water to supply water to the pump, so it's a good idea to have the pump like right on the floor.
    Also you'd want a nice short path with minimal bends and a reasonably large supply pipe IMO
  • dopey27177
    dopey27177 Member Posts: 916
    All the installations I did the pump was put below the boiler.
    As was said by EthicalPaul the pump needs some static pressure to keep its prime.
    I can see this happening, the boiler water is at based on the steam pressure 212 degrees to 232 degrees on average. Although the the pump is all brass there are different coefficient of expansion of the pump parts. The impeller will expand faster than the body of the pump, as each part expands they will eventually touch and the pump will seize.
    All of the piping should be installed at or below the boiler water lines. That area has the cooler water. All the steam in the system is spent and comes back as much cooler condensate. The condensate is mixed with the hot boiler water which lowers the water temperature passing through the pump. The cooler the water the less expansion will occur to the impeller and the body of the pump.
    Jake
    P.S. mount the pump vertically as is shown in Dan's sketches.
    EBEBRATT-Ed Member Posts: 20,486
    You can't mount a wet rotor pump vertically
  • dopey27177
    The wet rotor pump can be mounted in any position except for having the motor upside down.
    jake
    pecmsg Member Posts: 7,285
    The wet rotor pump can be mounted in any position except for having the motor upside down. jake
    I believe Lon systems twitch 20 PSI standing pressure!
  • dhelmkamp
    dhelmkamp Member Posts: 6
    Thanks all--some follow-up:
    1) pump height, and tap into boiler, and condensate return, are about 12" below water line. I can increase that to about 24" if I move pump to floor level. Worth doing?
    2) regarding pump orientation, Taco instructions read "circulator must be mounted with the motor in
    the horizontal position. It may be mounted vertically with motor up if system pressure is at least 20 psi"
    So I think I am OK on this one.
    3) should I be replacing the pump cartridge at this point, or can I assume it will be reliable if I can get it
    operating again?
    Where should I look for Dan's sketches referenced above?
    thanks,
    dave
    I would lower it yes. I would also have it closer to the boiler with as few bends as possible in the pipe.
    Also, are you feeding the boiler water directly to the pump (at possibly up to 212 degrees) or are you mixing it with a bypass from the loop in order to temper the water down to something more reasonable like 180?
    If you try to pump 212 degree water, and there is not very much static pressure on the supply side of the pump, the pump will lower the pressure enough there that the water will become steam and your pump won't like that.
  • dhelmkamp
    i will lower the pump and see how it does. it's about 3 feet from boiler, which is as close as I can get. the water temp has not exceeded 180 at any time I was watching it; that's with the mixing valve partially open (see photo).
    thanks for the advice
    -dave
    mattmia2 Member Posts: 17,483
    Side note, gate valves shouldn't be used for throttling, they should be fully open or closed. Use a globe or a ball valve. The threads on the stem and gate don't like the gate fluttering in the flow.
  • Greybeard
    Greybeard Member Posts: 17
    I'm not sure why your pump is seizing, but you should be using a 3 piece bronze pump, not the Taco impeller. I believe Dan discusses this in his article on hot water loops.
    That said, more than 20 years ago our oil company replaced a three piece cast iron pump with a cast iron Taco impeller. When the Taco seized I just replaced the impeller, and it has been working fine on our hot water loop for more than 10 years. By the way, a complete pump cost no more than just the impeller.
  • dhelmkamp
    Where can I find that article?
    -dave
  • dhelmkamp
    So Dan's article recommends a 1700 rpm 3 piece circulator. Is the Taco 110 stainless steel a good match?
    https://www.supplyhouse.com/Taco-110-24S-110-Stainless-Steel-Three-Piece-Circulator-Pump-1-12-HP
    I have not seen any bronze models in this series.
    -dave
  • Greybeard
    Stainless steel should be at least as good as bronze, but you should check with the manufacturer or supplier to see if that pump is good for condensate.
    Bell and Gossett has a bronze three piece circulator that is crazy expensive. You should check to see if the flanges are compatible with your Taco flanges. Here is the link: https://www.supplyhouse.com/Bell-Gossett-106192LF-1-12-HP-Series-100-AB-Bronze-Circulator-Pump .
    I suppose there is some point of crazy expensive that it makes more sense to make it a closed system with a tankless coil.
    I’m using a cast iron grundfos, I know I’m not supposed to but it was too cheap to resist trying. I have treated clean water and a screen in front of it. One year, so far so good
  • EzzyT
    EzzyT Member Posts: 1,380
    I’m my opinion you have the wrong pump installed, it needs to be a 3 piece oil lubricated bronze pump like B&G 100.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • dhelmkamp
    Happy to report success after upgrade to a three section pump and lowering of piping. One week of operation with no issues.
    Thanks all!
    To my eyes, that's a nice layout! Congratulations on the successful change!
    You might consider a screen at the hot water output from the boiler (prior to the bypass)