Radiator vents not closing
I tried several new ones so I don't think it's defective and I used a laser thermometer and I am getting around 180 - 190 f. If the system is producing wet steam can that cause a Gorton vent not to shut? Are there any other things besides for dirt that can cause it not to shut if it reaches temperature?
I have had this issue with Gorton #2 on a steam main also and it only shot after like 5-10 minutes of releasing steam.
Thank you in advance.
Comments
-
What you describe isn't normal. I have seen a couple folks report some bad luck with recent Gorton vents. Try a Maid O Mist, at least for experimentation's sake. They are very inexpensive and actually quite good.
https://www.supplyhouse.com/Jacobus-Maid-O-Mist-J4-4-1-8-Angle-Air-Valve-3564000-pNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
When you're boiling is firing and the vents are releasing steam, what pressure is your gauge showing? If you're running at a high enough pressure you could be pushing right past the vents and ruining them.0
-
I have this same problem with the new Gorton 5, 6 and C vents I installed on my larger rads. My smaller rads have Hoffman 40s and they seem to close. I don’t know what pressure I’m operating at because of my useless 0-30psi gauge (another issue I need to deal with). Do you know your system pressure when your rads are fully heated and the vents should be closing?0
-
In a one pipe system no manufacturer vent valves will work properly if the steam temperature is below 212 degrees. Assuming you are at sea level your boiler should be set at no less than 1 1/2 psi where the steam temperature is 216 degrees. At 212 and above the vent valves should shut down unless they are defective.
Resetting the pressure control to 1 1/2 psi off and 1 psi on. An issue like none insulated steam mains can affect the temperature of the steam before it gets to the radiators ( the vent valve takes a long time to shut down).
jakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron1 -
Jake tnx that's exactly what I wanted to understand. So if a boiler is not piped properly so water is entering with the steam (causing it to cool down faster) and there is not a lot of latent heat in the steam the vents will have a hard time shutting if it's under 212? Because when I read from the manufacturer they claim that it will shut at much lower temps.
TnxLevi0 -
@dopey27177
I have the opposite problem. Rads are quiet till around 5-8 oz then they let steam though. After 8oz to my 16oz cutoff they quiet down. Rads are completely hot with less than an oz of pressure. It’s not until 5-8 oz that they hiss steam. Mostly on the top floor. Main is fully insulated.dopey27177 said:In a one pipe system no manufacturer vent valves will work properly if the steam temperature is below 212 degrees. Assuming you are at sea level your boiler should be set at no less than 1 1/2 psi where the steam temperature is 216 degrees. At 212 and above the vent valves should shut down unless they are defective.
Resetting the pressure control to 1 1/2 psi off and 1 psi on. An issue like none insulated steam mains can affect the temperature of the steam before it gets to the radiators ( the vent valve takes a long time to shut down).
jake
0 -
Your 5-8 oz at the boiler is not 5-8 oz at the radiator. it takes some time for the air leaving the rads to heat up enough to close the vent valves.
Just a shot in the dark.
try a smaller vent valve on the rads, maybe the air is leaving to fast and that may be why the vent valves are noisy.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
dopey27177 said:Your 5-8 oz at the boiler is not 5-8 oz at the radiator. it takes some time for the air leaving the rads to heat up enough to close the vent valves. Just a shot in the dark. try a smaller vent valve on the rads, maybe the air is leaving to fast and that may be why the vent valves are noisy. Jake
0 -
@StevenNYC After your main vents close the steam will look for its next path of least resistance. If well balanced and radiators venting relatively slowly then this should be pretty unnoticeable. However, if you are trying to bias steam to a large radiator or cold room by heavily venting this particular radiator then after the mains close steam flow will tend to concentrate to that riser leading to that radiator and you will hear a hissing associated with air rapidly being driven out by the advancing steam. My experience that I cannot totally explain has been that once the steam reaches and starts filling the radiator the amount of hissing and thus probably rate of steam delivery to that radiator decreases. If you have purposely unbalanced your system in order to get steam to certain rooms faster you will likely just have to live with those rads hissing when evacuating air and likely hissing again or whistling when the boiler shuts down and vacuum sucks air back into the system through those large radiator vents (they will often open before the mains reopen). Your best bet to reduce the issue while maintaining the balance that you like would be to slow everything down at the radiators.0
-
My issue is not so much with the hissing but with vents that are already 190 degrees but don't want to shut so I get quite a bit of steam out of them until they finally shut after 5-10 minutes was wondering if that is an issue only with Gorton's0
-
May I humbly enquire... if all your radiators are nice and hot at a fraction of an ounce, why are you letting the pressure build beyond that? Why not stop at 6 ounces or so, or even less?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Just a shot in the dark,
Are the radiators on the top floors the same size as the radiators on the lower floor?
When I was a helper 65 years ago my job was to carry the rads up and install them in certain rooms.
Not all the rooms had the same size radiators, the top floors had smaller rads than the lower floors.
I asked my boss how come. He then said to me the reason for smaller rads on the top floor is heat rises.
You know we do this work for high end customers so I have a shop engineer that does heat calcs for all the buildings we work in and as a result we never get come back.
Unfortunately for me I went away in the navy at that tie and did not learn about heat loss in a building and heating element design an placement till 20 years later.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
So just an update on my Gorton #1 that was not closing I replaced it with a Hoffman 75 and it closes perfectly this is after trying several Gorton's straight out of the box not sure why that is but I'm not sure I can trust Gorton for the mains anymore0
-
-
STEAM DOCTOR said:Recently, I have had numerous Gorton vents fail to close. As in, they are letting out steam. Something is up with Gorton. Not happy0
-
Probably more cost effective to change the vents. Running at low pressure is ideal.0
-
STEAM DOCTOR said:Probably more cost effective to change the vents. Running at low pressure is ideal.0
-
Me too….I used to use Gorton vents exclusively. But I have been having nothing but headaches with new vents not working as of the past year. They won’t close. I switched to Barnes and Jones, Hoffman, and Ventrite…now no problems closing but had to acquire new venting strategy etc.STEAM DOCTOR said:Recently, I have had numerous Gorton vents fail to close. As in, they are letting out steam. Something is up with Gorton. Not happy
gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.1 -
Had issues with the BJ Big mouth. Lots of them. I was a huge and loud proponent of the Big Mouth. Not any more. Had way to many that leaked steam. Heavy leaks. Some leaked from day one. That's half a headache. Had a bunch that worked fine when installed and started to leak weeks or months later. Some with property damage.1
-
Where does one buy ventrites?0
-
Last month I replaced two Ds and two #5 vents, all MOMs, with one Gorton D, one C and two number 5s, and much to my chagrin not one of the 4 vents closed on steam. I sent them back and replaced the #5s with Hoffman 40s, the Ds with MOMs and the C with a Ventrite #1 open all the way.
The Ventrite hisses loudly but closes with a reassuring thump as do the two Hoffman 40s. The Two MOM Ds keep venting air for the most part but when the outside temp drops and the boiler runs more frequently they then close. All rads heat evenly across.
I have replaced two defective Big Mouths with BJ-2VV Vari-vents from Barnes and they have never once leaked steam in three seasons. My boiler operates at 1.2psi and shuts down at 1.8psi. All my rad vents open before the main vents and suck in air. My steam is pretty wet but my mains and returns are fully insulated.
Any suggestions with respect two MOM Ds that are on the 2 largest rads that seem reluctant to vent air completely? Thanks in advance.0 -
@PhilKulkarni
Do those radiation’s gurgle by any chance when they’re nice and hot?PhilKulkarni said:Last month I replaced two Ds and two #5 vents, all MOMs, with one Gorton D, one C and two number 5s, and much to my chagrin not one of the 4 vents closed on steam. I sent them back and replaced the #5s with Hoffman 40s, the Ds with MOMs and the C with a Ventrite #1 open all the way.
The Ventrite hisses loudly but closes with a reassuring thump as do the two Hoffman 40s. The Two MOM Ds keep venting air for the most part but when the outside temp drops and the boiler runs more frequently they then close. All rads heat evenly across.
I have replaced two defective Big Mouths with BJ-2VV Vari-vents from Barnes and they have never once leaked steam in three seasons. My boiler operates at 1.2psi and shuts down at 1.8psi. All my rad vents open before the main vents and suck in air. My steam is pretty wet but my mains and returns are fully insulated.
Any suggestions with respect two MOM Ds that are on the 2 largest rads that seem reluctant to vent air completely? Thanks in advance.
1 -
Yeah, how wet I was wondering
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Out of a total of 10 radiators spread over 3 floors there are 2 on the 2nd floor that gurgle quite loudly but heat up normally. I increased their pitch but see no difference.
While this is a minor concern, my greatest headache is a leak in the system that I have not been able to fix which is consuming approx 1.5gallons/day when temp in NYC drops to 20F and below. I have checked the usual suspects-boiler leak, radiator valve joints, leaking main and radiator vents in my previous post, horizontal run outs, wet returns, tel tale signs of leaks through the insulation on the mains, billowing steam through the chimney. Had two different plumbers including an HVAC company who felt 1.5-4 gallons of water draw/day by a steam boiler was quite normal. I have plaster walls everywhere and there are no water stains on any.
This leak has persisted for 3 seasons but my boiler miraculously seems to have 9 lives, though it is 12 years old.
Thanks in advance for any expert suggestions on how I might address this pesky leak.0 -
Had two different plumbers including an HVAC company who felt 1.5-4 gallons of water draw/day by a steam boiler was quite normal.
HilariousNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Yes, but also very sad.0
-
Amazing how two people look at the same problem. I called in the two professionals asking them whether they were familiar with steam heating and when they said yes I asked whether they could find and fix a leak in my one pipe system. I was careful not to seek their opinion on my system- just find the leak please. Yet one found none, asked if I had skimmed the boiler, and I told him the boiler water level did not surge. He said there was no leak got paid and left. The other said the water consumption was normal, made little effort to find the leak, but got paid as well. Wallet just got lighter, Ouch!0
-
PhilKulkarni said:Amazing how two people look at the same problem. I called in the two professionals asking them whether they were familiar with steam heating and when they said yes I asked whether they could find and fix a leak in my one pipe system. I was careful not to seek their opinion on my system- just find the leak please. Yet one found none, asked if I had skimmed the boiler, and I told him the boiler water level did not surge. He said there was no leak got paid and left. The other said the water consumption was normal, made little effort to find the leak, but got paid as well. Wallet just got lighter, Ouch!0
-
but a jumpy pressure gage, or a bouncing sight glass isn't a gallon a day leak, it may be a wet steam, low water in the glass type problem, but not a gallon a day problem,
but since you said sight glass,
it itself could be leaking, and the one I had I never saw, until , , ,
close the top valve and see if the water rises in the glass, that would be steam/air leaving the top of the glass,
and you'll never see it unless the steam is VERY wet,
might be worth a look.known to beat dead horses1 -
-
In early November, I filled the boiler until the water came out of the Big Mouth at the end of the main which is approx 31" from the center of the sight glass. Let it sit there for 48 hrs and then checked the firebox to for any drips or wet spots. Then last month when the temp in the NYC area was in the teens and the boiler was operating more frequently, I stepped out a couple of times to look at the chimney but saw no steam which if it was going up the chimney would have been visible against the ambient air. Finally, I don't see any steam coming out of the piping around the boiler including the top of the sight glass as suggested by a member on this thread. My returns are above ground in the basement.0
-
read what I wrote again,PhilKulkarni said:, , , Finally, I don't see any steam coming out of the piping around the boiler including the top of the sight glass as suggested by a member on this thread.
I didn't see steam from the top of the glass either,
but while exercising the glass valves, the level rose in the glass, quickly, when the top valve was closed,
air or steam was escaping out that upper gasket, until it was snugged up a bit more.known to beat dead horses0 -
and it could be the lower gasket also,
that steamin hot water could dry off before it makes a mess
just another place to check , , ,known to beat dead horses0 -
Checking the sight glass gaskets. I took off the two copper rods on the sides of the glass and shut off the top valve while the boiler was running. The water level went up by about 1/8”. I opened it and closed it again but this time the water level stayed the same(put a mark on the glass with a pen). I wrapped a paper towel around the lower gasket and checked for signs of moisture but came up dry. Checked the upper gasket for moisture the same way and also came up dry.
I am thinking of inspecting the 4 riser joints at the mains one more time. I will have to take off the fiberglass insulation and the plastic wrap around the tees which is a pain because of limited space between them and the floor boards above. Unless there are multiple leaks in the system that occurred at the same time 3 yrs ago-none of which I have been able to find, I am back to speculating that the boiler is the culprit and believing that looking at the chimney for escaping steam is not the easiest diagnostic.
Is it possible that the boiler has a leak which reveals when the boiler expands, i.e. producing steam but stays closed when the boiler is cold and thus passes the flooded boiler test?0 -
Did you check all the radiator valves are fully open and no leaks at the radiator valve stems. Similar to the sight glass they can leak almost invisibly. Use a tissue when the boiler is running and the rads are hot.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements