Honeywell zone valve

simba
simba Member Posts: 18
Is there a harm to unhook the out spring of Honeywell zone valve in order to eliminate water hammer in one zone.
Thankyou

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Derheatmeister
    Derheatmeister Member Posts: 1,633
    It would most likely result in a uncontrollable zone associated with it..
    Most of the times a waterhammer is due to:
    1. Pumping against the Zone valves intended Flow direction.
    2. A loose pipe.
    3. Overpumping.
    Some Zonevalves such as the Taco 571 or Caleffi 676 series are slow opening valves which may help with this situation..


  • HVACNUT
    HVACNUT Member Posts: 6,685
    It's the spring that makes it close. It only gets power to open. 
    There are other valves out there that close slower.
  • simba
    simba Member Posts: 18
    Thanks for the quick reply. So i unhooked one of the outer spring and now i can see the valve closes a bid slower and the noise went sway. Can i leave it like this for now and take care of it in the spring. Does this harm my boiler. Thank you
  • HomerJSmith
    HomerJSmith Member Posts: 2,640
    Yes & no.
  • Derheatmeister
    Derheatmeister Member Posts: 1,633
    simba said:

    Thanks for the quick reply. So i unhooked one of the outer spring and now i can see the valve closes a bid slower and the noise went sway. Can i leave it like this for now and take care of it in the spring. Does this harm my boiler. Thank you

    It is probably piped in reverse direction..
  • hot_rod
    hot_rod Member Posts: 24,849
    The springs determine the close off pressure of the zone valve. If it is an 8 Cv valve, the most common, it has a 20 paid shutoff. Disconnecting one spring reduces that close off, so depending on the circulator delta P, the valve may not close tightly. Swapping one problem for another. Check the temperature a few feet away from that zv, if its hot, the valve is leaking past

    over pumping is the most common cause of hammer. A delta P circulator is ideal for multi zoned systems, as it adjusts flow according to the valves open.  And saves 50% or more on electricity 
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    HVACNUT
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,631
    Removing one of the springs is a widely used trick in the field. It usually gets rid of the hammer on closing. 
    Retired and loving it.
  • Tim McElwain
    Tim McElwain Member Posts: 4,653
    Dan is correct I have been doing it for years and no harm done. I have been directly or indirectly involved with this industry since I was sixteen and now I am 82. If there had been a problem with me doing it I would have heard about it by now.
  • hot_rod
    hot_rod Member Posts: 24,849
    Wonder why they still put two springs on? To bad the HW engineers don’t hang here😗
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    SuperTech
  • nathandclements
    nathandclements Member Posts: 12
    What exactly IS water hammer, and what is happening to cause it when the valve closes? I have a terrible banging sounds I'm trying to solve. If happens almost every time the system cycles. I thought it happened on valve open, but now I'm wondering if it's actually happening on valve close. I have noticed that if I leave the thermostat cranked all the time, it doesn't do it as bad or as much.

    Here's a link to my post about it: https://forum.heatinghelp.com/discussion/187411/obnoxious-banging-constant-bleeding-info-overload#latest
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,631
    Retired and loving it.