EDR Question for Trane #75 Unit ventilators ?Dangers of Not Changing All traps in One Day??
JUGHNE
Member Posts: 11,276
There is a job with steam pouring out of cond pump vents.
I hope to have all materials arrive before starting the change out of all trap elements.
There are 5 EOM F&T's that need minor repiping.
These include 2 bucket traps that may be the main source of the steam in the return.
I feel confident to get these changed/repiped before having to have heat again overnight.
What is the thinking that failed smaller radiator traps could pass enough steam back to harm the new F&T's for one overnight operation of boiler??
The remaining 31 Hoffman 17C and 8C could be dealt with the next day.
I could adjust the pressure as low as possible....below 2 PSI.
I hope to have all materials arrive before starting the change out of all trap elements.
There are 5 EOM F&T's that need minor repiping.
These include 2 bucket traps that may be the main source of the steam in the return.
I feel confident to get these changed/repiped before having to have heat again overnight.
What is the thinking that failed smaller radiator traps could pass enough steam back to harm the new F&T's for one overnight operation of boiler??
The remaining 31 Hoffman 17C and 8C could be dealt with the next day.
I could adjust the pressure as low as possible....below 2 PSI.
0
Comments
-
-
I agree with @Jamie Hall if you can identify any bad traps do those first0
-
For my own understanding whats in an F&T that steam can harm?JUGHNE said:There is a job with steam pouring out of cond pump vents.
I hope to have all materials arrive before starting the change out of all trap elements.
There are 5 EOM F&T's that need minor repiping.
These include 2 bucket traps that may be the main source of the steam in the return.
I feel confident to get these changed/repiped before having to have heat again overnight.
What is the thinking that failed smaller radiator traps could pass enough steam back to harm the new F&T's for one overnight operation of boiler??
The remaining 31 Hoffman 17C and 8C could be dealt with the next day.
I could adjust the pressure as low as possible....below 2 PSI.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
From reading and conversation with others, bad trap elements can pass steam to wreck newly installed elements.
F&T's have the thermostatic element and the float. Worst case scenarios are steam in the return entering the discharge line, meeting the water around the float and creating water hammer to beat up the float.
Also have read of the element being crushed by steam on the back side and vacuum on the front side.
This system has been running at 8 PSI for years. Plenty of steam out of pump vent pipe. Down to 4 PSI now. Would lower pressure for the overnight heating.
We could see single digits for that night.
I may be over cautious but this is a long distance job 150 miles away.0 -
-
There was one trap cage back ordered for this project.
The trap is 3/4" Hoffman 8C.
The emitters are: (1950) Trane unit ventilators #75, coil #2 Cabinet is 15 x 32 x 60.
Print EDR is 298.2.
Is that EDR with the fan running or just convection?
There are 6 of these; one will be missing a trap element another has a broken TRV remote cap tube tstat.
For these problem children I was going to install an orifice in the inlet valve unions.
I have plenty of sizing info for orifices at various pressures.
I just need a good guess on the EDR as a coil.
They do not use the fan function.
I would size for 80% of the EDR.0 -
You can always start smaller and see how much of the coil heats.0
-
The 298 EDR has to be with the fan running.
In another old school there are 99 EDR CI single pipe rads, these are huge as far as CI goes. They only heat 1/3 across with air vent TRV's.
So as a convector these must be 120 to 150.
Yes it is easy to up size, however I am only there this weekend. 150 mile/3hours away.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements