Converting one pipe steam radiators to hot water
TheGerman
Member Posts: 3
I'm putting a boiler in a small ranch style house. I have the urge to put in radiators in a couple of rooms. I found some really ornate radiators but they are one pipe steam with steam vents about 1/3 the way down from the top and it appears the top connections between the sections are very small. Can I drill a vent at the top and tap it to 1/8" FPT? I think I can get the plug out of the opposite end of the existing connection.
0
Comments
-
-
@Jamie Hall is right. You can drill all the bleeder openings you want, and they still won't work on hot-water.
But you could always install a steam system in that rancher...................All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Post a picture of the rads you are looking at. We can tell you if they will work on water.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
The steam radiators will work on a hot water heating system. You wont need vents on the radiators if you install the system with the pumping away method of locating the circ pump.
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
We haven't seen the radiators yet.0
-
I agree post a picture so we can see0
-
Radiators (both hot water and steam, but mostly hot water) are available on Facebook marketplace (Zuckerberg and I aren't pals) at giveaway prices. If you want a hot water system just go source a few there, the sellers will be so happy they found some fool willing to take away that giant, heavy door stop. Find the right radiator that suits your needs, there are even lots with fancy filigree on them.
BTW, if it were me dreaming up interesting places to install old hot water radiators I would specify wide and low (ie; not steam radiators) so I can sit on top of the warm ribs and watch the snow fall through my ranch house picture windows.
1 -
If you're going to covert what cannot be converted, best to go all the way, install a blower and duct system. If you want to retain the boiler install a hot water or steam coil in a cooling blower.
There was an error rendering this rich post.
0 -
veteransteamhvac said:<Snip> available on Facebook </Snip>One way to get familiar something you know nothing about is to ask a really smart person a really stupid question1
-
I have found this to be true too. It may take a bit of time, but the circulating water will gradually absorb the air in the tops of the radiators and bring it back to the air separator near the boiler. I would use at least a B&G IAS ( not a plain air scoop) or a microbubbler air separator for this application.dopey27177 said:The steam radiators will work on a hot water heating system. You wont need vents on the radiators if you install the system with the pumping away method of locating the circ pump.
Jake
There are several old Reed type radiators at the Florence Hotel, in historic Pullman (Train car manufacturer company town) that were reused when they pulled out the steam and hacked in a hot water system ( destroying trimwork, tin ceilings and the like). Now they have to inspect 100 some radiators in cold weather to make sure nothing is getting frozen since most of the structure has not been renovated and is not in regular use.To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
That's just sad.The Steam Whisperer said:dopey27177 said:The steam radiators will work on a hot water heating system. You wont need vents on the radiators if you install the system with the pumping away method of locating the circ pump.
Jake
There are several old Reed type radiators at the Florence Hotel, in historic Pullman (Train car manufacturer company town) that were reused when they pulled out the steam and hacked in a hot water system ( destroying trimwork, tin ceilings and the like). Now they have to inspect 100 some radiators in cold weather to make sure nothing is getting frozen since most of the structure has not been renovated and is not in regular use.Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements