Extremely loud gorton vents

2»

Comments

  • neilc
    neilc Member Posts: 2,854
    I always go back to boiler, and pressure,

    did you replace the pigtail yet?
    your gage may not be seeing the boiler pressure any better than the Ptrol is, they're both after the pigtail,
    and even then,
    the rest of the Ptrol and gage piping there needs to be checked for clear and free breathing back into the boiler also,

    second thing,
    the water line in the sightglass is up a bit, and from the pictures, looks real close to the boiler take off level, even with that properish header, you may be throwing wet steam up into the system,
    try lowering the water level closer to 1/2 a glass,

    and why is the level that high? is auto feeder doing this?
    is sightglass emptying when firing?
    high, unseen, pressure pushing water out into the returns?

    does that water line bounce much when you're firing?
    known to beat dead horses
  • Jay85
    Jay85 Member Posts: 34
    neilc said:
    I always go back to boiler, and pressure, did you replace the pigtail yet? your gage may not be seeing the boiler pressure any better than the Ptrol is, they're both after the pigtail, and even then, the rest of the Ptrol and gage piping there needs to be checked for clear and free breathing back into the boiler also, second thing, the water line in the sightglass is up a bit, and from the pictures, looks real close to the boiler take off level, even with that properish header, you may be throwing wet steam up into the system, try lowering the water level closer to 1/2 a glass, and why is the level that high? is auto feeder doing this? is sightglass emptying when firing? high, unseen, pressure pushing water out into the returns? does that water line bounce much when you're firing?
    I removed the pigtail and it it clear. I just installed the low pressure guage the other day. 

    Water line does drop and bounce when in operation, especially during a long heating cycle. I think the auto fill kicks in at certain times when this happens. Not every time. 

    Why do you say properish header? What would you suggest be changed? 

  • ChrisJ
    ChrisJ Member Posts: 16,315
    The risers from the boiler should come into the sides or top of the header.  Dropping down into the top is best but the side is fine bottom isn't.


    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • gerry gill
    gerry gill Member Posts: 3,078
    Try (just for the hell of it) switching one of the ‘bad’ Gortons to a Hoffman or a Vent-rite and see if the radiator ‘suddenly’ works as it should. Also, I suggest in the absence of good steam guys in your neighborhood, that you do a bit of mechanical research and become that guy. Everything you need to know is buried somewhere on this site.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

    Larry Weingartenethicalpaul
  • Jay85
    Jay85 Member Posts: 34
    Try (just for the hell of it) switching one of the ‘bad’ Gortons to a Hoffman or a Vent-rite and see if the radiator ‘suddenly’ works as it should. Also, I suggest in the absence of good steam guys in your neighborhood, that you do a bit of mechanical research and become that guy. Everything you need to know is buried somewhere on this site.
    Actually, trying to become that guy is how I found this site. I have learned alot in a short time. I actually have become fascinated with how steam systems work. 
  • gerry gill
    gerry gill Member Posts: 3,078
    Sometimes, it’s hard to sift through answers because people replying or saying one thing in their mind other than what you’re really talking about because they are not present at your house. This makes things very difficult and you also have to become a detective with the answers. Don’t forget you can also private message people too, and carry on a private discussion with an individual or I think maybe a couple individuals..not sure on that last part. Maybe Erin can clarify that.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,354

    Don’t forget you can also private message people too, and carry on a private discussion with an individual or I think maybe a couple individuals..not sure on that last part. Maybe Erin can clarify that.

    Yes, you can. Just click on the envelope icon and then type their usernames into the Recipients field. More tips on using the forum here: https://heatinghelp.com/forum-user-manual Thanks!

    President
    HeatingHelp.com

  • Maybe the Gorton 2 main vents are not opening, and therefore all the air is going out the radiator vents.—NBC