Ultra Boiler efficiency
icy78
Member Posts: 404
Hey all, havent been around in a while, and hope everyone's well.
Got a question on rating conditions on Weil McClain ultra boilers. I thought I'd read a couple years ago that the efficiency rating was, in part, based on an EWT of 60 degrees F.
Well I can't find that spec anywhere.
Anyone know what the rating points are?
I see the ratings in the manual but not specifics.
Thanks!
Got a question on rating conditions on Weil McClain ultra boilers. I thought I'd read a couple years ago that the efficiency rating was, in part, based on an EWT of 60 degrees F.
Well I can't find that spec anywhere.
Anyone know what the rating points are?
I see the ratings in the manual but not specifics.
Thanks!
0
Comments
-
-
Ironman said:The EPA requires that all hot water boiler AFUE ratings be done with 120* return water and 140* supply water. The brand makes no difference. Like MPG ratings for a car.
Hmm. So that's true for condensing and non-condensing then.
I ment to type 80F RWT not 60 but still that's far below 120.
Wondering if the 120 is from back before condensing boilers were a thing?
Maybe the 80F was European. Dont they size for 130-140 SWT and 40-50 emitter delta ?
0 -
I think the point to remember is sort of a twist on @Ironman 's comment: the AFUE rating is a means of comparing various designs. In order to make the comparison valid, it is done under a tightly prescribed set of conditions. One can say that under those specific conditions with the specified installation and perfectly tuned a new boiler will have such and such an efficiency. Beyond that, no. Changing the conditions will change the efficiency -- obviously -- but it won't change them in the same way for different designs. Even relatively minor changes in installation have an effect. And, as we know, setting the combustion off -- even by a relatively small amount -- can have major changes on efficiency.
What is it for,then? As I say, mostly to provide a comparison point -- and also to demonstrate compliance with various legislative or regulatory diktats. No more, and no less.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
While waiting in the Chiropractors office today, I was reading the Ultra manual and I found the testing is based on AHRI BTS-2000.
It states that for condensing boilers, EWT is to be 80° F plus or min 5°F and LWT to be 180.
Interesting that's a 100 degree delta and the Ultra allows 58 delta max. ( before faulting)0 -
icy78 said:While waiting in the Chiropractors office today, I was reading the Ultra manual and I found the testing is based on AHRI BTS-2000.
It states that for condensing boilers, EWT is to be 80° F plus or min 5°F and LWT to be 180.
Interesting that's a 100 degree delta and the Ultra allows 58 delta max. ( before faulting)
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements