Opinion requested on this photo
SlamDunk
Member Posts: 1,664
This hole would be perfectly round if not for tool mark. It served as a condensate line from a base board. I Bought it from Lowes and installed it seven years ago. It was fine until a year ago when I noticed I was loosing water then this past Wednesday it opened up and triggered a leak alarm I had in crawl space. It is 1/16" hole. It was not in an area where it could have been accidentaly drilled.
I know this sounds like a conspiracy theory but do you think someone pre drilled this but not all the way thru to fail at a later date?
I know this sounds like a conspiracy theory but do you think someone pre drilled this but not all the way thru to fail at a later date?
0
Comments
-
Chinese pipe?0
-
-
Water hammer?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Looks like you got a hernia when you bore down with the pipe wrench on cheap pipe.0
-
Looks like an electric arc hole. A live wire touch it?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Looks like there was a defect in the steel, some slag layered in to it and the piece of steel surrounded by a thin layer of slag broke free.0
-
This is a 3/32” drill hole. Look at these photos. Thank God it wasnt used on a gas line. Do you agree? Or am I coo coo ?0
-
-
Is it possible this was a return to the store with a hole drilled in it and you just got enough condensate now to reach the level of the hole? Or it clogged enough that it slowed enough to reach that level?
If it was a defect it would look more blown out than that on the inside, it wouldn't be that clean0 -
mattmia2 said:
Is it possible this was a return to the store with a hole drilled in it and you just got enough condensate now to reach the level of the hole? Or it clogged enough that it slowed enough to reach that level?
If it was a defect it would look more blown out than that on the inside, it wouldn't be that clean
I think the hole was in the seven to nine oclock position and as crud built up the condensate level rose and spilled out. The pipe needs better pitch so that gets added to my list.
None the less, there is a nut job out there vandalising pipe.
0 -
On commercial and industrial work, Schedule 80 black pipe is normally specified for condensate lines because condensate contains small amounts of carbonic acid from CO2 in the air. Schedule 40 is normally specified for steam lines.
This is why condensate lines rot out well before steam lines that are pitched for proper drainage.—
Bburd0 -
But this is residential. Most of of the system is 90 years and looks great.0
-
The worst part of this is last year I thought I had a horizontal steel drain pipe in my wall rotted thru. It always drained slow and over the years I have hit it with a lot of draino. I thought it finally rotted and caused the puddle in crawlspace so I opened the wall and replaced it. Now, I believe it was this hole all along. All in the same vicinity.
Whoever drilled that hole cost me a few hundred bucks, a couple vacation days, a sore body and a bottle of Alleve.
0 -
Just another reason to hate the big box stores. I agree with schedule 80 on commercial/industrial where there is a lot of make up water.
I have never seen #80 installed in a house0 -
I dont hate them. Someone vandalized a pipe and returned it. It could have happened to any pipe supplier that accepts returns. I hate the vandal. I hope he had a very miserable seven years. That hole was so small that I almost reinstalled the pipe.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements