Steam Boiler Replacement Water
Comments
-
It could be, but it seems unlikely. But before you become concerned, make sure that you are checking the water level with the system in more or less the same condition -- that is, when the boiler has been off for at least 15 minutes. Somewhat slow returns can make the water level appear low when the boiler has just been running.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie, thank you very much for the advice. I refilled the boiler gauge glass to halfway and made a mark where I filled it to. I’ll try checking it in the next few days after the heat has been off for at least 15 minutes. I’m not sure it was off for 15 minutes when I looked at it today with the cold weather we’re having in the northeast.New Jersey0
-
Jamie Hall said:It could be, but it seems unlikely. But before you become concerned, make sure that you are checking the water level with the system in more or less the same condition -- that is, when the boiler has been off for at least 15 minutes. Somewhat slow returns can make the water level appear low when the boiler has just been running.
I took your advice and checked the water level today after the boiler was off for a bit. I filled the boiler yesterday halfway up the sight glass to the black line and then checked it today when I got home from work. I turned the boiler off and waited 30 minutes and there was some water loss. The first photo is from yesterday after I filled it and the second is today. Do you think I should be concerned about the water loss or could this just be normal?
New Jersey1 -
Honestly that is more water loss than I would expect from a day of running -- even in cold weather. Time to go looking for anywhere and everywhere there might be a leak. Keep in mind while you do this that there is no such thing as a trivial leak: even one drip every 10 seconds will add up to a gallon in a day!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Jamie Hall said:Honestly that is more water loss than I would expect from a day of running -- even in cold weather. Time to go looking for anywhere and everywhere there might be a leak. Keep in mind while you do this that there is no such thing as a trivial leak: even one drip every 10 seconds will add up to a gallon in a day!New Jersey0
-
-
Just checking, but you are looking for leaks during long calls for heat, as opposed to when the boiler isn't firing, correct?
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
ethicalpaul said:Just checking, but you are looking for leaks during long calls for heat, as opposed to when the boiler isn't firing, correct?Any suggestions on where else to look to find the possible leak?New Jersey0
-
@kub1080
You can use a small mirror to check for steam leaks. Steam can leakand you can't see it. Hold the mirror near the air vents and around the radiator supply valves . If there is a leak the water vapor will usually condense on the mirror2 -
About the best I can do. Chasing small leaks, particularly in older systems, is one of the most frustrating tasks I can think of!sophia123 said:
Really helpful advise.Jamie Hall said:Honestly that is more water loss than I would expect from a day of running -- even in cold weather. Time to go looking for anywhere and everywhere there might be a leak. Keep in mind while you do this that there is no such thing as a trivial leak: even one drip every 10 seconds will add up to a gallon in a day!
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
I suppose you could remove all of the air vents and plug the holes and then pressure test the system with air at 10 PSI or so and go around listening and using soapy water.Jamie Hall said:
About the best I can do. Chasing small leaks, particularly in older systems, is one of the most frustrating tasks I can think of!sophia123 said:
Really helpful advise.Jamie Hall said:Honestly that is more water loss than I would expect from a day of running -- even in cold weather. Time to go looking for anywhere and everywhere there might be a leak. Keep in mind while you do this that there is no such thing as a trivial leak: even one drip every 10 seconds will add up to a gallon in a day!
That's probably the fastest and most sure way if you have the time and know how.
On my system I had a union leaking but it was only noticeable when steam first got to it as it would make a slight sizzling noise, but then it'd stop and anything wet dried up immediately.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
2 -
One of the most annoying leaks I have found was a very minor drip way out in the wilderness on the threaded connection between a riser and a horizontal run on a dry return. About a drip every 20 seconds. Accounted for a solid gallon per day...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Jamie Hall said:One of the most annoying leaks I have found was a very minor drip way out in the wilderness on the threaded connection between a riser and a horizontal run on a dry return. About a drip every 20 seconds. Accounted for a solid gallon per day...New Jersey0
-
I think I have found the leak. It’s a small drip. My plumber is coming tomorrow morning so hopefully this is an easy fix. I better check all the valves again since I missed this the first time I checked.https://youtu.be/RFsihfcVnc4Do you think this small drop could account for all the water loss I’m seeing?Thanks for the help,
DanNew Jersey0 -
-
Let's run the numbers... 1 drop, say 0.5 ml, every 3 seconds or so. 10 ml per minute. 0.6 litres per hour. 14 litres per day... almost 4 gallons... yeah. Although I may have overestimated drop size and underestimated frequency... but even so, and even if it only does it when the boiler is running...
Yeah.
See what I mean by even a small drip can account for a lot of water?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Jamie Hall said:Let's run the numbers... 1 drop, say 0.5 ml, every 3 seconds or so. 10 ml per minute. 0.6 litres per hour. 14 litres per day... almost 4 gallons... yeah. Although I may have overestimated drop size and underestimated frequency... but even so, and even if it only does it when the boiler is running... Yeah. See what I mean by even a small drip can account for a lot of water?New Jersey0
-
nice job on the find, so satisfying!!
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
The leak is fixed! Turned out the nut was loose. It is a very tight space where the connection is made, but my plumber was able to tighten the nut a half turn and the leak stopped.
One other question. This morning I heard what I thought was the usual sound of air coming through a few of the air vents. However, the heat was on a long run after being lowered at night. They weren’t spitting water but when I held a mirror it instantly fogged right up. Is that a definite sign it is leaking steam? I had tried this test earlier in the week and saw nothing on the mirror from any of my radiators, but that was in the evening after heat was on maybe 15 minutes.I don’t see any steam coming out of the vent but the entire radiator was warm from the boiler running for a while. Just wondering if I should replace the 3 air vents? I’ve been using the Varivalve Ventrite #1 which I liked due to their adjustable setting.New Jersey0 -
Now that I had the leak repaired on Friday morning 1/14, I lost maybe an 8th of an inch or less of water as of this afternoon 1/8. I am assuming that this is what would be within the limits of normal water loss for four days. Would you agree?
New Jersey0 -
I had the same boiler installed in May of 2006 and it worked fine for years, but in January 2022 I notice the automatic water feeder kept going off frequently. When I checked steam was coming out of the top. I immediately called my utility company and they shut it down, because of the risk of carbon dioxide poisoning. Long story short the top of boiler (heat exchanger) was totally rusted out, so I had to replace the boiler. I did contact the company Weil-Maclain and they said their warranty is only for 10 years (the woman was very rude). I would think that a boiler that's only used a few months a year would last longer. I know people with boilers 20 + years old. This boiler is definitely a safety hazard!!
0 -
OOps! I meant carbon monoxide in the previous post.
0 -
Couple things here. The boiler rotting out on the steam side has no impact on the combustion gases leaking into your house, so the person that told you that was either not properly educated or flat out lied.Pissed123 said:I had the same boiler installed in May of 2006 and it worked fine for years, but in January 2022 I notice the automatic water feeder kept going off frequently. When I checked steam was coming out of the top. I immediately called my utility company and they shut it down, because of the risk of carbon dioxide poisoning. Long story short the top of boiler (heat exchanger) was totally rusted out, so I had to replace the boiler. I did contact the company Weil-Maclain and they said their warranty is only for 10 years (the woman was very rude). I would think that a boiler that's only used a few months a year would last longer. I know people with boilers 20 + years old. This boiler is definitely a safety hazard!!
Second, the boiler having a short life most likely is due to improper installation, or improper maintenance. That boiler is a rebranded Weil Mclain, and I can tell you first hand those boilers will last if properly installed an maintained. I had one go 32 years, and I put another one in and I plan on it lasting longer with water treatment.
People want to go after manufacturers in these situations, and most of the time that isn't justified. Based on what is posted on this website regularly, most of the time its the contractors fault.
The boiler isn't a safety hazard, the people you have been listening to are.1 -
I'll ad to @KC_Jones comment there -- water quality isn't what causes problems at the top of a boiler, although it can cause corrosion below the water line -- if, and only if, too much water is being added because of leaks elsewhere. Such as might be caused by sloppy installation of the boiler.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 93 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements