safe air pressure to test baseboard heating pipes?
bk9
Member Posts: 22
I've got a gas fired boiler baseboard heating system with 3/4" copper piping. I've got a leak in a pipe in the slab. I want to test the other pipes in the same zone that are also in slab before I bother to reroute around the leaking pipe. What is a safe air pressure to test these pipes? Pipes are 60yrs old. The zone/loop in question is isolated from the boiler on both supply and return sides.
0
Comments
-
-
-
-
-
To supplement my earlier comment -- all of the above. Plus a comment adding to @Gilmorrie 's remark: testing with water is much much safer, as he suggests. It is also a good bit easier in one major regard: Assuming there is no expansion tank involved, even a small leak will cause a significant and moderately rapid pressure drop, and variations in temperature (within normal comfort ranges) won't obscure the results.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Thanks.
Before I cut open the loop on either side of the leaking pipe buried in the slab, so I could pressure test both sides, I figured I'd see how quickly the entire loop with leaking pipe lost pressure. Using an air compressor, I charged the isolated zone (isolated from boiler and other piping) to 42 psi (42, and not 40 because 42 lined up with one of the marks on the pressure gauge), then sealed off the zone from the air compressor. Much to my surprise, it held 42 psi for 2 hours, then very slowly started dropping. After 24 hours, it's ~28 psi. I assume that large a drop for a zone that covers basement and ground floor of a split level single family is too much for it to be just copper pipe expansion?
For sure, it's 60yr old pipe. I don't want to test the limits of all those old joints and the very thin walled spots that must exist.kcopp said:Where 60 would be for sure and prob to the letter of the law... I would hate to see test and 60 and create a leak that wasnt an issue before...
0 -
I had a fire inspector once insist on a 300# on an older PVC system being remodeled. They did a double-take when I refused to be in the mechanical room when it came up to pressure.
In your case 30# will give you the info you need, Only go to 60# if required."If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements