Venting Risers...Because Why Not??

This has come up multiple times but I am going to put a twist on it. Often the problem is with 3rd story radiators on the cold side of the main. But.....

I'll be replacing the radiator valve and spud on my 2nd floor radiators. It dawned on me that it would be a good time to vent the risers going to these radiators. Between the runout and risers there is probably 15-20ft of 1-1/4 pipe going to these radiators.

My back-of-the-napkin math says that's about 1.5-2.0 cubic feet in the riser/runout to vent.

I have Big Mouth main vents and these radiators heat well....but I want the air out of my mains as quick as possible which made me think maybe getting the air out of the risers would help accomplish this.

I'd use a reducing Tee and a straight radiator valve with its matching spud. The fittings are cheap and I already have some good Gorton #1's lying around so this really wouldn't cost me anything. The Reducing Tee I am referring too looks like this:


Comments

  • ChrisJ
    ChrisJ Member Posts: 16,225
    I might have missed it, what's the question?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • AdmiralYoda
    AdmiralYoda Member Posts: 665
    @ChrisJ
    Hahaha....sorry, I tend to elaborate (ramble) TOO much sometimes. While I'm at it replacing the radiator valves I'd like to vent the risers. Do I need to? No. Do I want to? Yes.

    The risers/runouts are 15-20ft long.

    I'm wondering if this is a good idea or a completely unnecessary idea. I tend to be Captain Overkill most of the time.
  • Jamie Hall
    Jamie Hall Member Posts: 24,467
    In my view it's an excellent idea. After all, when you really look at it from the viewpoint of the air or steam, a riser is no different from any other steam main.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ChrisJ
    ChrisJ Member Posts: 16,225

    @ChrisJ
    Hahaha....sorry, I tend to elaborate (ramble) TOO much sometimes. While I'm at it replacing the radiator valves I'd like to vent the risers. Do I need to? No. Do I want to? Yes.

    The risers/runouts are 15-20ft long.

    I'm wondering if this is a good idea or a completely unnecessary idea. I tend to be Captain Overkill most of the time.

    I like it.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • AdmiralYoda
    AdmiralYoda Member Posts: 665
    edited January 2022
    @Jamie Hall @ChrisJ
    I have seen people vent visors after the fact to correct the lack of steam getting to the 3rd+ floors and it usually involves drilling and tapping to get a vent installed somewhere.

    I want to use a reducing Tee and a straight radiator valve to accomplish the same thing. It is good to know this is an option. Thanks!
    delcrossv
  • KC_Jones
    KC_Jones Member Posts: 5,788
    I'd agree with doing this, it would be a fascinating experiment honestly. The radiator vent would truly be only for the radiator. The idea of getting steam to every rad simultaneously would be much easier.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    stormbytes
  • cross_skier
    cross_skier Member Posts: 201
    I vented my risers 20 years ago and I'm happy with my decision.  Large vents on radiators caused random issues during my first two years.  Double vents worked a little better.  Venting the risers fast and the radiators relatively slow solved everything.

    I used Gorton D's 1/4" straight vents

    stormbytes
  • AdmiralYoda
    AdmiralYoda Member Posts: 665
    @KC_Jones That was my thought exactly. There is even one radiator on the 1st floor with a rather long runout as well. It is a relatively inexpensive experiment with the only extra cost being a Gorton #1. And if for some reason it turns out to be a bad idea (unlikely) I can just plug the vent hole.

    @cross_skier If I'm not mistaken the Gorton D and #1 has the same venting capacity, with the difference being the thread size. Sounds like a great choice either way.
  • ethicalpaul
    ethicalpaul Member Posts: 6,339
    I did mine on a second floor riser that I re-ran just for fun. I think it's not necessary for 2nd floor. I'm sure it's faster to get steam, but it's not really noticeable at least for me.

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

  • Jells
    Jells Member Posts: 576
    I did one at the furthest spot on my system, but I put the tee between the spud and the rad. Seems to have improved things, I mean, how could it not?
  • cross_skier
    cross_skier Member Posts: 201
    I also started with the furthest bathroom out.  A hot bathroom radiator in the morning was a "must have" every winter morning.  2" main to 33' of 1-1/2" main with 12' of 1"riser to the tiny bathroom radiator.
  • PhilKulkarni
    PhilKulkarni Member Posts: 70
    I would like to vent two of my 1 1/4" risers feeding the third floor radiators, but these recessed Cast Ray rads don't have the space for a tee with a vent on it since the valves are located below the rads, not on the side. The risers come through the floor with a 6-8" run outs from the valve to the radiator.

    The risers are in the walls and only a small section of them- 20-24" where they connect to the main are accessible from my crawl basement crawl space. I have 22' risers feeding the 3rd floor rads which are currently vented with the largest orifice MOM vents but still take a couple of boiler cycles to heat up.

    Thanks in advance for any suggestions.


    rad.docx 148.8K
  • jhewings
    jhewings Member Posts: 139
    edited January 2022
    @PhilKulkarni You can consider drilling the 6-8" runout and tapping for 1/8" angle vent such as a Gorton D.
  • cross_skier
    cross_skier Member Posts: 201
    I also used a tap, 1/4" npt
  • cross_skier
    cross_skier Member Posts: 201

  • Jells
    Jells Member Posts: 576
    jhewings said:

    @PhilKulkarni You can consider drilling the 6-8" runout and tapping for 1/8" angle vent such as a Gorton D.

    That's an interesting idea. Is there a reason tapping the rad instead just above the spud wouldn't accomplish the same thing? Seems to me EVERY rad could benefit from 2 vents, a riser vent and a rad vent on opposite sides. Or am I, steam novice, missing something?
  • jhewings
    jhewings Member Posts: 139
    I did 3 like the one above and 1 on a radiator (on the steam valve side about 6 inches above the steam valve because the above was not convenient). They are all "riser" vents though. I have 4 risers. I don't think my system needs 2 vents on every radiator. These are on the 3rd floor of a 3flat (Chicago). I am happy with these riser vents although an unexpected result was one of them erupts with loud hissing of air going back in after the boiler shuts down (every time). I don't mind it although I have read here a vacuum breaker on the main vent tree will solve this.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,240
    @AdmiralYoda

    1st floor not necessary
    2d floor may or may not help
    3rd floor ..do it

    If your riser and radiator are both 1 1/4" you can use a 1 1/4 X 1/2 x 1 1/4 tee bush the 1/2" as needed for the vent