What am I missing?
brett288
Member Posts: 8
A friend of mine had some guy pipe his in for hydronic system. It ran as piped for two months. I repiped it and now for some reason I can't get flow out the return manifold. I can't get the GPM gauges to hardly jump. I am wondering if the pumps have lost their ability to produce the amount of head originally intended. I will be putting a new pump in on one zone to try that. With no flow promotion I am racking my brain thinking I'm missing something. The first set of pictures are what I tore out and the second set with watts manifolds is what I put in. (the shark bite cap is for when we bring in permanent water.
0
Comments
-
Looks to me that you have the expansion tank & air sep on the return should be on the supply & The pumps should be pumping away. Are you pumping hot ut of the boiler through the pumps into the zones?
Does that boiler require primary secondary piping?0 -
How much flow are you expecting vs what those can measure?0
-
Is there a circulator in the boiler?
No LLH?
What does the manual say?0 -
EBEBRATT-Ed said:Looks to me that you have the expansion tank & air sep on the return should be on the supply & The pumps should be pumping away. Are you pumping hot ut of the boiler through the pumps into the zones? Does that boiler require primary secondary piping?0
-
Here's the manual to that water heater. Like I said this is a buddy I'm just trying to help out. All this stuff was here and I'm just trying to make it work after just having him but the manifolds.
Manual: https://images.homedepot-static.com/catalog/pdfImages/94/94d875b5-44c8-4f5b-91a4-598f8aebf610.pdf
Picture from the manual. It is only trying to be used for heating in floor heat.0 -
Its a tankless water heater...not a boiler. You are asking it to do something that it is really not supposed to do. The pressure drop through the WH AND the loops lengths are so high you are not getting flow.
For it have any chance you need to pipe in a boiler/ primary loop and then a system/secondary loop. Then you will need to wire it to work as such.
1 -
In addition to what @kcopp said -- which I would have said more forcefully -- that tankless has far more power than those loops can ever absorb, but since it is controlled by flow not temperature, you are going to have some serious temperature control problems in that floor.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If you think about this as a domestic water heater, which is all it is, it was designed to work with 40-60 PSI water pressure pushing the water thru small tubing inside it's heat exchanger.
The pumps you have will not develop anywhere near that pressure.
And as Jamie said, 199,000 is a lot of heat for that system to never get rid of.0 -
Don't walk away from this one. Run!
Or get the proper appliance for the job.
And install it according to the manual.
By the way, what does the Richmond manual say about "radiant floor heating"?0 -
Page 47:brett288 said:Here's the manual to that water heater. Like I said this is a buddy I'm just trying to help out. All this stuff was here and I'm just trying to make it work after just having him but the manifolds.
Manual: https://images.homedepot-static.com/catalog/pdfImages/94/94d875b5-44c8-4f5b-91a4-598f8aebf610.pdf
Picture from the manual. It is only trying to be used for heating in floor heat.
• Inlet water temperatures above 32°F (0°C), but
not exceeding 120°F (49°C).
• DO NOT reverse the HOT and COLD water
connections.
• DO NOT connect this water heater to water lines
previously used for space heating. All water
piping and components shall be suitable for
potable water0 -
@brett288 As others have said, the tankless is the wrong appliance for the job, but it can be made to work (more than likely). 1) It will have to be piped with Primary/Secondary piping. 2) the circulator on the primary will need to be a high head circulator—a Taco 0015 will probably handle it. 3) if I’m looking at the before and after pictures correctly, the three Hydrosmart circulators that you moved cannot have the shaft of the motor in the vertical position as you have them. I currently am temporarily using a tankless for my radiant, until my house addition is done and a proper boiler is installed.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements