Copper to pex
nordic440
Member Posts: 10
Kinda new to hydronic heating, learning more everyday. I'm planning on finishing the girlfriends basement soon and have a few questions. First off it's a new system installed 2 years ago, mix of slant fin and old cast rads, runs 154*F. They made new copper trunk but it's low, would like to replace that with 3/4" PEX, also remove the old rads and go all baseboard. Also add 3 zones not just one. I would like to use 3/4" for each zone as well, looping units off each other and back. Would also like to use circulators for each zone. Here's a couple pics. Unit is a IBC 160K BTU it is a combo unit. Works well just the heat is very uneven and unit is throttled way back cause the old rads I guess?. Any pointers would help.
0
Comments
-
Oh also why does the return tie back into the supply? Seems odd to do it that way?0
-
before you do anything you need to download the Slant Fin app and do a room X room heat loss of the whole house. otherwise how much baseboard do you need. You need to determine the heat loss first.
Then baseboards, then pipe sizing and layout, then select pumps etc
Getting rid of the cast iron may nort be the best idea ....nothing heats better
The return is hooked in "primary secondary " which is the way those boilers must be piped
Lokk for information on this in system help on this site
0 -
Yes I definitely plan on doing that. Gathering information phase right now, lol. They do heat great but are in rough shape and they are all different sizes, some tall and narrow some short and wide. One on the main floor and 4 on the second level! Hence the 3 slant fins they added to the main level, I suspect these are from the 40's and have had a good life for sure. I have installed a forced air system but this is all new to me. I don't really intend on messing with it for a few months, however I would like to atleast run the pex in the walls so I can sheet rock it. Then the baseboards can be installed near the end of the Reno.........0
-
-
It definitely does. The copper is low for the drop ceiling I wantta install. Pex will be outta sight, not a ton of head room room to start with. Ideally I wouldn't want to modify it but I feel we need the space. Again just tossing around ideas ☺️0
-
That is not an ideal mix on a one zone system, cast radiators and fin tube. They heat quite differently as you noticed. If they are in different rooms you could zone it so they are separate?
some of those joists look like oak, or just rough cut fir? It would be a tough drill to get all that piping up in the joist. Maybe you want the new piping tight to the bottom of the joists?
if you use pex I would insulate it to prevent squeaking where it touches the joists, if you intend to hang below.
Boiler piping is correct and as per the installation manual. It is a primary secondary piping arrangement.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
nordic440 said:Oh also why does the return tie back into the supply? Seems odd to do it that way?
Also in one of the photos it looks like you have already started finishing the basement or at least insulated the exterior foundation with foam board. Make sure to cover that with drywall or something approved if you back off from this project. Most foamboard cannot be installed and left exposed.0 -
I would like to put the pex below the joists. As soon as I figure out what size pex I'm going to be putting up the drywall. Lol gotta love the window shakers eh. I think where doing a mini split system in the future.
I can't figure out how to reply to individual posts so lumped it together! Made a crude drawing0 -
Before you finish the basement I recommend you do moisture testing. Tape a 3’ square of 6-mil poly (seal all edges) onto to floor and walls in few places. If you see condensing moisture you will need to plan for and manage it (And if you don’t see it. Is you probably will in the spring).You will find this is a real challenge in a house of that age.This guy does a good job summarizing the issues.0
-
Yes we have corrected the moisture issues, there was a small leak from the exterior side. New window wells and grading as well as extending down spouts have fixed the issue. Block cracks where repaired and has been hovering at around 48% humidity for months now. Definitely wouldn't be putting money into it if it wasn't dry ☺️
I appreciate everyone taking the time to respond!1 -
PC7060 said:Before you finish the basement I recommend you do moisture testing. Tape a 3’ square of 6-mil poly (seal all edges) onto to floor and walls in few places. If you see condensing moisture you will need to plan for and manage it (And if you don’t see it. Is you probably will in the spring).You will find this is a real challenge in a house of that age.This guy does a good job summarizing the issues.
And his comment about people from the old days not understanding how water works is a load of bull$hit. I'm sure some of the deadmen would have a thing or two to say about that. They were the masters of controlling water right?
Actually I bet most of these old houses weren't built to have finished basements because they DID understand water.
Yes every house older than say 25-30 years wasn't built to have a finished basement. Can they be finished anyways? It depends. But the reality? Even houses that were built to have that space finished suffer from the same issues. Foundation water proofed? Awesome. It'll fail at some point. Vapor barrier under the concrete? Awesome. Lets see what hydrostatic pressure does. Sump pump? I'd prefer a house that doesn't need one! And pumps fail, normally when you need them the most! He talks like all of these things will save your bacon down there. Sorry to bust any bubbles but do you think some plastic under concrete, tar spread on a foundation, and a sump pump is going to save you when the electric is knocked out and the sewers backs up? And most moisture in a basement comes from outside air. How much my dehumidifier runs tracks pretty darn close to what the temperature and humidity is doing outside, not how damp the ground is outside.
1 -
-
Made a crude drawing.Is that series loop one of the 3 zones you're planning (in the basement I'm guessing?). This is your chance to split and balance on a room-by-room basis. Long series loops make for uneven heating unless you have open concept.0
-
JakeCK said:PC7060 said:Before you finish the basement I recommend you do moisture testing. Tape a 3’ square of 6-mil poly (seal all edges) onto to floor and walls in few places. If you see condensing moisture you will need to plan for and manage it (And if you don’t see it. Is you probably will in the spring).You will find this is a real challenge in a house of that age.This guy does a good job summarizing the issues.
And his comment about people from the old days not understanding how water works is a load of bull$hit. I'm sure some of the deadmen would have a thing or two to say about that. They were the masters of controlling water right?
Actually I bet most of these old houses weren't built to have finished basements because they DID understand water.
Yes every house older than say 25-30 years wasn't built to have a finished basement. Can they be finished anyways? It depends. But the reality? Even houses that were built to have that space finished suffer from the same issues. Foundation water proofed? Awesome. It'll fail at some point. Vapor barrier under the concrete? Awesome. Lets see what hydrostatic pressure does. Sump pump? I'd prefer a house that doesn't need one! And pumps fail, normally when you need them the most! He talks like all of these things will save your bacon down there. Sorry to bust any bubbles but do you think some plastic under concrete, tar spread on a foundation, and a sump pump is going to save you when the electric is knocked out and the sewers backs up? And most moisture in a basement comes from outside air. How much my dehumidifier runs tracks pretty darn close to what the temperature and humidity is doing outside, not how damp the ground is outside.The point is he pretty clearly states is the same thing you say above (highlighted). Majority of pre-WWII basements are not buildable as finished area because it was never the intended purpose for the space.The central point from my original post is the key take away
Do the 6-mil poly test and if you see condensing moisture you will need to plan for and manage it”0 -
Has anyone mentioned or have you thought about using a manifold and running homeruns of 1/2" to each room / piece of heat ? All emitters will receive same temp and you'll only need 1 gpm to each type also . They were made to use 1 gpm anyway . Might even get to lower temps and increase the efficiency of that boiler a point or two .
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38331 -
PC7060 said:Wow, not sure how you got that I was advocating for him and his products. As a FYI, he especially made me cringe when he discuss thin setting tile directly to the subfloor with no decouple layer.The point is he pretty clearly states is the same thing you say above (highlighted). Majority of pre-WWII basements are not buildable as finished area because it was never the intended purpose for the space.The central point from my original post is the key take away
Do the 6-mil poly test and if you see condensing moisture you will need to plan for and manage it”
And I didn't say you were advocating for him. I was just stating I didn't like that what that guy was saying. And why.
0 -
-
Rich_49 said:Has anyone mentioned or have you thought about using a manifold and running homeruns of 1/2" to each room / piece of heat ? All emitters will receive same temp and you'll only need 1 gpm to each type also . They were made to use 1 gpm anyway . Might even get to lower temps and increase the efficiency of that boiler a point or two .
1 -
-
yesimon said:Made a crude drawing.Is that series loop one of the 3 zones you're planning (in the basement I'm guessing?). This is your chance to split and balance on a room-by-room basis. Long series loops make for uneven heating unless you have open concept.0
-
-
Ah yes. Basements. Just for laughs, may I point out that all two of the three houses which I maintain have unfinished basements. In both, the basements are used, quite successfully, for a variety of projects -- not just utilities, but food storage, carpentry workshops, etc. The bigger, in Cedric's home, dates to 1780 or thereabouts. It is not waterproof, nor was it ever intended to be. It has, in fact, neat gutters running around the perimeter to accept the inevitable water which comes in and take it neatly away to daylight. Works a treat. The basement is never damp -- higher humidity, yes (usually around 70%) and not heated by anything except Cedric and the surrounding ground, but very pleasant.
The other was carefully worked on to be finishable (it isn't, but that's another story). Careful waterproofing (right...) and, of necessity, two sump pumps. It isn't quite as old -- 1820, we think -- and would have been better had no waterproofing been attempted.
If you don't want water in your basement, however, don't try to keep it out with waterproofing. That will fail. Rather you need to work outside, to make sure groundwater does not and cannot come up to the foundation. That means drains at footing level, with fabric and gravel and the lot, open to daylight somewhere. Done well, that will be a good long term solution. Anything else -- particularly applied on the inside -- is doomed.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements