Oil Usage calculation

pecmsg
pecmsg Member Posts: 5,251
1100 Gals of oil used yearly. Indirect HW heater. What's the calculation to convert to BTU's?

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited December 2021
    152,761,574 btu's
    1100 x 139,000

    If you're trying to do a heat loss off it I would need your zip code.

    There was an error rendering this rich post.

    pecmsg
  • pecmsg
    pecmsg Member Posts: 5,251

    152,761,574 btu's
    1100 x 139,000

    If you're trying to do a heat loss off it I would need your zip code.

    11971

  • R Mannino
    R Mannino Member Posts: 441
    On Long Island if you multiply gallons by 55 it gets you a WAG. It sounds crude but it works. My house uses 600 gallons a year, give or take. My house has has 80 feet of S/F baseboard, so the numbers jive. Radiation 40,000. WAG heat loss 33,000. Still waiting for someone to make a small enough boiler.
    Robert O'Brienpecmsg
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,559
    To learn more about this professional, click here to visit their ad in Find A Contractor.
    pecmsg
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    edited December 2021
    Making some assumptions...I didn't have DDay entered in for the tip of the Island, I figured New Haven was close enough.




    P.S Hey @Robert O'Brien did you get the files I sent you?

    There was an error rendering this rich post.

  • Jamie Hall
    Jamie Hall Member Posts: 24,576
    You guys cheat. As a way to get a building's heat loss, that works just fine! But you do need a reasonably accurate fuel usage...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    STEVEusaPA
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505

    You guys cheat. As a way to get a building's heat loss, that works just fine! But you do need a reasonably accurate fuel usage...

    He said 1100 gallons...

    There was an error rendering this rich post.

  • pecmsg
    pecmsg Member Posts: 5,251
    this young man helped on the beach house project so I’ll return the favor. 
    I told him I’d sizing and help with the piping design. 
    The HW is supplied by a zone valve. During the summer they run the 1st floor circ to get HW. 
    I get to play with the pro press again  
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Well even if I'm off the smallest boiler will be a little too big. Maybe it's time to pop in an EK.

    There was an error rendering this rich post.

  • pecmsg
    pecmsg Member Posts: 5,251
    Moneys a bit tight but that’s my next post. Manufactures. My rough estimates were 80K input. 
  • Robert_25
    Robert_25 Member Posts: 549
    What is the story with the thimble for the flue pipe? Looks strange in the picture. Masonry chimney?
  • pecmsg
    pecmsg Member Posts: 5,251
    Robert_25 said:
    What is the story with the thimble for the flue pipe? Looks strange in the picture. Masonry chimney?
    I’m afraid to open it and find out. There is a clean out next to it that was for the fireplace that’s sealed with fiberglass. 
  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 9,157
    R Mannino said:

    On Long Island if you multiply gallons by 55 it gets you a WAG. It sounds crude but it works. My house uses 600 gallons a year, give or take. My house has has 80 feet of S/F baseboard, so the numbers jive. Radiation 40,000. WAG heat loss 33,000. Still waiting for someone to make a small enough boiler.

    You need to put on an addition, or sell some capacity to a neighbor.

    Just trying to think outside the box

    Mr.Ed


    LOL :'(

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    pecmsg
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    R Mannino said:

    On Long Island if you multiply gallons by 55 it gets you a WAG. It sounds crude but it works. My house uses 600 gallons a year, give or take. My house has has 80 feet of S/F baseboard, so the numbers jive. Radiation 40,000. WAG heat loss 33,000. Still waiting for someone to make a small enough boiler.

    They make small boilers that fire with a .17 nozzle.
    Just not in America.

    There was an error rendering this rich post.

    R ManninoEdTheHeaterMan
  • R Mannino
    R Mannino Member Posts: 441


    They make small boilers that fire with a .17 nozzle.
    Just not in America.

    I'm just going to have to get by with my .5 nozzle in my G115 and biofuel has a little less BTU's, so I'm sneaking up on it!