Rotting from the top
Comments
-
Any answer is going to be speculation in large part. My guess would be the turbulence of the boil was causing those areas to be affected more than the others, given they are end sections where the steam is exiting.
There are many factors, but the primary one is generally the amount of make up water bringing in oxygen.
Hopefully they fix the boiler piping and figure out the reason for the excess make up water. Was sizing verified with the replacement?0 -
Your near boiler piping is not to standard but probably not the issue. I am curious how much water you add per season and the pH of the water.
I saw a This Old House episode where the top of a newer Weil McLain. boiler rotted out so I guess it's not unheard of.
My 23 year old Pearless series 61 is still going strong. I have not installed the VXT water feed but have spent a few hours tracking down small leaks over the years. Its "double header" is similar to yours but each header services a different main.1 -
Speculation: At the water line, the temperature of the iron is moderated by the sloshing boiling water. But up high it can get much hotter. That higher temperature combined with the oxygen that is getting released by the fresh makeup water might increase oxidation rate there.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el2 -
@KC_Jones
This is a boiler that was not closely monitored. It has an automatic water feeder so I don't have an answer. What you say makes a lot of sense. Regarding sizing of the new boiler, yes it was sized to the connected load. But so was the old one. Regarding the near boiler piping, Although it's definitely overkill having two three inch headers, I think that would only contribute to slowing the steam velocity out of the boiler and making drier steam.0 -
0
-
@cross_skier
Yes. I thought that 16 years was a poor run. But in fairness, I'm sure that diligence was lacking regarding detecting leaks throughout the system over the years1 -
@john walsh_2
Sadely in this day and age 16 years is not a bad run if the boiler is not maintained. It's not uncommon to see 6 or 8 year old boiler rotted out1 -
So all the radiators were measured and the EDR properly calculated?john walsh_2 said:@KC_Jones
This is a boiler that was not closely monitored. It has an automatic water feeder so I don't have an answer. What you say makes a lot of sense. Regarding sizing of the new boiler, yes it was sized to the connected load. But so was the old one. Regarding the near boiler piping, Although it's definitely overkill having two three inch headers, I think that would only contribute to slowing the steam velocity out of the boiler and making drier steam.
0 -
I'm pretty sure 3 pass steam boilers where the flue gasses stay under the waterline will last at least twice as long. I am told almost all boilers rot at waterline or above.
Intense heat against dry iron may be the problem.
Anyhow my next boiler will be the Megasteam with gas burner conversion. I'm hoping that by then it will be manufacture option or at least well documented.0 -
Looks like Slantfin Intrepid may be the only smaller 3 pass wet jacket steam boiler that is currently approved for use with a gas burner.
https://forum.heatinghelp.com/discussion/153026/new-slant-fin-intrepid-with-ez-gas-burner
If you are trying to avoid steam boiler rot this may be worth investigating
0 -
You should be aware that the noise from the gas burner will take some getting used to if you're used to an atmospheric boiler. The efficiency is very attractive, but I'm not sure I'd want that much noise in my basement. I'll probably get a Peerless 63-04 when my 40year old 561 gives up the ghost, but I might consider a SteamMax, unless they show the same tendency to rot as the Independence series. The jury's still out.cross_skier said:Anyhow my next boiler will be the Megasteam with gas burner conversion. I'm hoping that by then it will be manufacture option or at least well documented.
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
-
-
-
Yes. That is correct.pecmsg said:
So all the radiators were measured and the EDR properly calculated?john walsh_2 said:@KC_Jones
This is a boiler that was not closely monitored. It has an automatic water feeder so I don't have an answer. What you say makes a lot of sense. Regarding sizing of the new boiler, yes it was sized to the connected load. But so was the old one. Regarding the near boiler piping, Although it's definitely overkill having two three inch headers, I think that would only contribute to slowing the steam velocity out of the boiler and making drier steam.0 -
I wonder if there was a lot of surging. So the water line at the outlet would drop, metal gets hot, then the water surges up and cools it…. Rinse and repeat with oxygenated water if there a lot of makeup.
Or, 2nd theory, water boils at the point of lowest pressure. the outlets would be the point of lowest pressure. So there’s a lot of steam flashing at that point combined with oxygenated water and high dissolved solid acting also an an abrasive. Added to surging.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements