Furthest radiators slow to heat
To get heat to these rads I set the thermostat to 1.5’ differential so I have a longer burn.
Comments
-
Are the rooms getting warm? In early winter, with moderate cold, the system may not need to fill all the radiator.
For comfort.
Are there any crossover traps in this system? They are critical to proper function of some two-pipe systems. You need 1005 of the traps working to get the air out.—NBC
0 -
Thats a lot of pipe that has to get up to steam temperature - is that main insulated? The radiator feeds off that main sb insulated as far as you can reach as well.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
How much main venting? For 100' main you will need, at least, 3-4 Gorton #2 vents, maybe as many as 5. Vent location also depends on system design. If the main ends with a wet return you will also need vents on the dry return for the radiators. If you have the crossover trap then the vents will be on the dry return only. Also, the above recommendation is for the main only, if you have vents on the dry return, you may need at least 1 more Gorton. Others more well versed in 2 pipe may be able to comment further on that.
I don't believe the boiler is undersized by the amount suggested. That's only a 6% difference and can't be enough change to create the issue you have IMHO. The boiler piping could be causing issues, we need to see pictures of that to comment. That would help a lot.1 -
Are the rooms getting warm? In early winter, with moderate cold, the system may not need to fill all the radiator.
For comfort.
Are there any crossover traps in this system? They are critical to proper function of some two-pipe systems. You need 1005 of the traps working to get the air out
No the room is not heating well. Last night after a burn the thermostat was at 72 and that room was at 66. There are some insulation and draft issues, but those radiators are not helping much. The rest of the house heats really well other than some light banging.
There are no crossover traps.
How much main venting? For 100' main you will need, at least, 3-4 Gorton #2 vents, maybe as many as 5. Vent location also depends on system design. If the main ends with a wet return you will also need vents on the dry return for the radiators. If you have the crossover trap then the vents will be on the dry return only. Also, the above recommendation is for the main only, if you have vents on the dry return, you may need at least 1 more Gorton. Others more well versed in 2 pipe may be able to comment further on that.
I count 9 big mouth BJ vents in different places. They were put in at the same time our wet returns were replaced. Someone I found on this site did the work, same person who suggested boiler is undersized. No offense if he reads this, just looking for other possibilities than a new boiler
This was a Haines vacuum system -- we took it out of vacuum when installing the vents.
Here are some photos, let me know if anything else would help.
0 -
Steam piping in vacuum systems generally is a bit smaller than steam piping in a just plain steam systems.
so if there is a problem with heating it is to the entire structure.
If this was a two pipe vacuum system there is or was no need to put vent valves on the system.
Because you no longer heat at a vacuum the operating steam pressure needs to increased to at least 1 psi off and 12 psi on. You may have to increase the pressure settings.
Because you are a 2 pipe system you may and I say may have to install a small condensate pump and remove those vent valves.
Jake
Steam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
So here's the thing about pressure -- I've never seen any on the vaporstat, even after running it for an hour coming home from vacation.dopey27177 said:Steam piping in vacuum systems generally is a bit smaller than steam piping in a just plain steam systems.
so if there is a problem with heating it is to the entire structure.
If this was a two pipe vacuum system there is or was no need to put vent valves on the system.
Because you no longer heat at a vacuum the operating steam pressure needs to increased to at least 1 psi off and 12 psi on. You may have to increase the pressure settings.
Because you are a 2 pipe system you may and I say may have to install a small condensate pump and remove those vent valves.
Jake
All the rads heat up fully except for this one room. The bedroom next to it heats slow also, but at least the rads will get going. I was told we could always return it to vacuum by replacing the big mouths with vacuum vents.
You can see how this system was set up here: https://books.google.com/books/content?id=O9JBAQAAMAAJ&pg=RA1-PA925&img=1&zoom=3&hl=en&bul=1&sig=ACfU3U16U8ssAycU74I2SCHSsUcyxnToUQ&ci=109,86,774,1050&edge=00 -
There are a number of things about this system which I really don't like much, looking at it, but they are mostly minor, and if it is working satisfactorily I'd leave it alone.
Howeve.
Have you really gone back to the beginning on those two radiators? We know the rest of the system is heating well and the pressure never rises, so we know it's adequately vented (in fact, that's one of my problems with it -- it's wildly overvented). We know the boiler makes enough steam. I presume the mains are adequately vented, considering the shotgun approach to vents everywhere. But... those two radiators don't heat. OK, for a radiator to heat the steam has to be able to get to it and the air and condensate have to be able to get out. So -- Find the nearest steam main which gets steam. Trace the runout to each radiator in question. Does it get hot for its full length? If not, where does it stop? Find out why the steam stops there and fix the problem. Now you have steam to the radiator valve. Is that radiator valve open? It wouldn't be the first time. Now go to the outlet. Is there a trap there? Is it known to be working? Trace the return line. Does it drain freely to the nearest return which drains a known good radiator? Is the return line or the one it drains into steam hot? It shouldn't be.
All this takes longer to write than to do. But stop chasing phantoms in the basement, or undersized boilers, or extra vents in the corners, or questions about Haines vacuum systems, or whatever, and find out why the steam doesn't get to those radiators.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
Made a TYPE O
Where it says 12 psi on it should be 1/2 psi on
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron1 -
I had 2 second floor radiators that did not heat consistently and of course had cold risers. I added vents to the top of the risers with little street elbows and the problem was solved.
I have never heard of too much venting on mains but I'm no expert in 2 pipe. My longest main is 55', I added a main vent in the middle of it on a pipe tapped into the main. I also have antlers at the ends of all 3 mains.0 -
Thanks for the reply. I don't see anything obvious. But I'm just a homeowner who's read Dan's book. I think both of the radiators are fed by the same riser, which knocks when the system starts up. There seems to be proper slope for the return. They are going to be really f'n hard to access so I hope that's not the issue.Jamie Hall said:There are a number of things about this system which I really don't like much, looking at it, but they are mostly minor, and if it is working satisfactorily I'd leave it alone.
Howeve.
Have you really gone back to the beginning on those two radiators? We know the rest of the system is heating well and the pressure never rises, so we know it's adequately vented (in fact, that's one of my problems with it -- it's wildly overvented). We know the boiler makes enough steam. I presume the mains are adequately vented, considering the shotgun approach to vents everywhere. But... those two radiators don't heat. OK, for a radiator to heat the steam has to be able to get to it and the air and condensate have to be able to get out. So -- Find the nearest steam main which gets steam. Trace the runout to each radiator in question. Does it get hot for its full length? If not, where does it stop? Find out why the steam stops there and fix the problem. Now you have steam to the radiator valve. Is that radiator valve open? It wouldn't be the first time. Now go to the outlet. Is there a trap there? Is it known to be working? Trace the return line. Does it drain freely to the nearest return which drains a known good radiator? Is the return line or the one it drains into steam hot? It shouldn't be.
All this takes longer to write than to do. But stop chasing phantoms in the basement, or undersized boilers, or extra vents in the corners, or questions about Haines vacuum systems, or whatever, and find out why the steam doesn't get to those radiators.
The traps are new on the radiators. The valve is a TRV but I removed the thermostat dial because I was told they would cause trouble, so it's just the little metal pin for now. The pin moves up and down so it's not stuck. The radiator pitch is wrong, but pretty much none of my radiators are sloped correct and the others heat OK. I'm wondering if the valves could be clogged.
Also I checked the vents again, it is 3 big mouths on ends of each of two mains, and 2 big mouths on each of 2 dry returns.
1/2 or 12, still will never see any pressuredopey27177 said:Made a TYPE O
Where it says 12 psi on it should be 1/2 psi on
Jake
thanks I am getting close to trying this...cross_skier said:I had 2 second floor radiators that did not heat consistently and of course had cold risers. I added vents to the top of the risers with little street elbows and the problem was solved.
I have never heard of too much venting on mains but I'm no expert in 2 pipe. My longest main is 55', I added a main vent in the middle of it on a pipe tapped into the main. I also have antlers at the ends of all 3 mains.0 -
If the riser knocks when the system starts up, is it a water hammer or expansion? if it's a water hammer, somewhere in that riser there may be a bit of pipe -- needn't be long -- which is horizontal or nearly so, and it may not have enough pitch. That can be a real ause of slow or even no heat.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
How about some pictures of these problem radiators? Also some of the working ones.0
-
try setting the t stat at 85 degrees for a boiler longer run time'
If the pressure increases to 1psi off the problem is T stat in wrong place in the house.
jakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
I came back from vacation which gave me the chance to run the boiler for a couple hours. Both of these radiators did eventually heat up all the way across, but the supply pipe on each gurgles pretty loud. So it makes me think there's water trapped somewhere. I'm going to try raising the radiators and see if that gives me enough pitch. Is there anything else I can try short of opening the floor/walls?Jamie Hall said:If the riser knocks when the system starts up, is it a water hammer or expansion? if it's a water hammer, somewhere in that riser there may be a bit of pipe -- needn't be long -- which is horizontal or nearly so, and it may not have enough pitch. That can be a real ause of slow or even no heat.
1 -
What size is the pipe supplying these radiators?
What is the EDR of these radiators?
If you don't know the EDR, can you give us the details, i.e. height, width, depth, number of tubes and sections, and possibly a picture or two?Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
That was a useful finding. There's definitely water in the supply (either from an unintentional water trap probably due to house settling or from carryover from the boiler). Venting won't help you.joco said:I came back from vacation which gave me the chance to run the boiler for a couple hours. Both of these radiators did eventually heat up all the way across, but the supply pipe on each gurgles pretty loud. So it makes me think there's water trapped somewhere. I'm going to try raising the radiators and see if that gives me enough pitch. Is there anything else I can try short of opening the floor/walls?
I keep pasting this all over the place, but here was my adventure with that problem: https://forum.heatinghelp.com/discussion/167233/fixing-pitch-issues-in-old-houseNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
I've attached a photo of the 2 radiators as well as the riser from the basement. I think both radiators are fed from the same riser.Hap_Hazzard said:What size is the pipe supplying these radiators?
What is the EDR of these radiators?
If you don't know the EDR, can you give us the details, i.e. height, width, depth, number of tubes and sections, and possibly a picture or two?
As you can see it's a real pain to get at the riser pipe, it's run off the supply to indirect radiators, and the pipe is squeezed behind the ducts. There is some banging that comes from it on startup.
0 -
If both radiators are fed from a bullhead tee, that could be a problem, because it's impossible to pitch the two branches in different directions, so it would be helpful to see exactly how they did it. If you can't get at the pipes from below, you might be able to feed a flexible borescope down from above, but you'd have to take the traps off.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
#pigtail ?
all your gages and trols are above a single steel pigtail,
has that been checked for cleaned and clear back into the boiler ?
maybe you're not seeing the pressure you may have(?)
the 2 traps,
sometimes they freeze shut,
have you opened their caps, and jossled them?
and then they work again
known to beat dead horses0 -
Hap_Hazzard said:If both radiators are fed from a bullhead tee, that could be a problem, because it's impossible to pitch the two branches in different directions, so it would be helpful to see exactly how they did it. If you can't get at the pipes from below, you might be able to feed a flexible borescope down from above, but you'd have to take the traps off.neilc said:#pigtail ? all your gages and trols are above a single steel pigtail, has that been checked for cleaned and clear back into the boiler ? maybe you're not seeing the pressure you may have(?) the 2 traps, sometimes they freeze shut, have you opened their caps, and jossled them? and then they work again0
-
how do these 2 rads get their air to venting ?known to beat dead horses0
-
Are the indirect coils still connected?
If so can you isolate them, they could be stealing steam from the risers.
If that improves things perhaps you could repipe to the indirects if you need them.
I had a job where there were 2 large fan coils on a gym stage, the stage was walled off to be a separate room, the steam still flowed thru the coils. The room got so hot that AC was added to it. I shut the valves off and no longer needed the AC.
Just a for instance on how some simple things are overlooked.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements