It's possible this oil burner has not been serviced in over a decade...service recommendations?
BroadwichCT
Member Posts: 22
Recently purchased a house with a lot of deferred and/or amateur maintenance. The residential oil-fired Crown burner was manufactured in 2007, and from what I can see on the damaged tag it might be a Kingston model. I learned by reading the manual last night that it's a problem that it was installed into a stone rock chimney with no liner, and the same chimney also vents the gas water heater.
The prior owners could not remember when they had the boiler serviced, and there was no service tag attached. The auto feed counter showed nearly 900 gallons. The mains are insulated (one thing done right!).
When I turned boiler for the first time Nov.1st, steam began leaking from both ends of the sight glass. I turned everything off and fixed the leaking gaskets. It appears to have been happening for quite some time due to the mineral build up around the glass.
After turning on the burner it began cycling every two/three minutes. I found this website and dove in, discovering swing settings. Unfortunately the owners had broken the setting button off the thermostat, but after opening the thermostat and fixing the button I set the swing to 3 degrees and a constant temperature of 68. This greatly improved the short cycling. I collected data on the water usage for the next few days and found it to be extremely high (15 gallons). After more research on this site I assessed each air vent on the radiators and found that each and every one of them was leaking steam or even dripping water and two supply valves were leaking. I fixed the leaking supply valves, purchased all new vents and after these fixes and installation, the new water usage (so far) is about 3 gallons a week.
After installing the new vents however, the short cycling returned. I learned that the boiler is extremely oversized, which is likely a factor in the short cycling I'm experiencing.
I cannot verify the function of the Pressuretrol as some dopehead used thread lock on the pigtail and given the method of installation, I can't apply counter torque to get it free so that I can verify the integrity of the pigtail. I have purchased a low pressure (3 psi) gauge that I am planning to try installing on the day I have our cleaning scheduled, just in case I break off the pigtail. By the way, the Pressuretrol is set at .5/1.5.
I did discover that I had two extremely undersized main line vents, unfortunately installed on an elbow, and neither was functioning. Figuring a functioning vent would be better than none until I could get someone to tap the pipe appropriately, I purchased a Gorton #2 for where I had enough clearance to put that size, and a Gorton #1 for the other vent. Unfortunately the Gorton #2 arrived defective (from everything I read on this site), verified by trying to blow through the vent but no air would pass. I purchased another, which just let steam pour out when installed. Again, I can't verify the pressure the system is running at until I can get the gauge installed.
So, given all this I realize that all the deferred maintenance leaking to extreme water usage has likely shortened the lifespan of the boiler. I accept that.
What I would like is recommendations on how to maximize my boiler cleaning/servicing. Is there anything I can do to maximize their time/make their job easier, given the lack of maintenance?
Second, how urgently do I need to get the chimney lined?
Thank you in advance for your expertise and advice. Typing all this out has made me realize how much I have learned in just four weeks...thanks to all who offer their assistance on this site!
The prior owners could not remember when they had the boiler serviced, and there was no service tag attached. The auto feed counter showed nearly 900 gallons. The mains are insulated (one thing done right!).
When I turned boiler for the first time Nov.1st, steam began leaking from both ends of the sight glass. I turned everything off and fixed the leaking gaskets. It appears to have been happening for quite some time due to the mineral build up around the glass.
After turning on the burner it began cycling every two/three minutes. I found this website and dove in, discovering swing settings. Unfortunately the owners had broken the setting button off the thermostat, but after opening the thermostat and fixing the button I set the swing to 3 degrees and a constant temperature of 68. This greatly improved the short cycling. I collected data on the water usage for the next few days and found it to be extremely high (15 gallons). After more research on this site I assessed each air vent on the radiators and found that each and every one of them was leaking steam or even dripping water and two supply valves were leaking. I fixed the leaking supply valves, purchased all new vents and after these fixes and installation, the new water usage (so far) is about 3 gallons a week.
After installing the new vents however, the short cycling returned. I learned that the boiler is extremely oversized, which is likely a factor in the short cycling I'm experiencing.
I cannot verify the function of the Pressuretrol as some dopehead used thread lock on the pigtail and given the method of installation, I can't apply counter torque to get it free so that I can verify the integrity of the pigtail. I have purchased a low pressure (3 psi) gauge that I am planning to try installing on the day I have our cleaning scheduled, just in case I break off the pigtail. By the way, the Pressuretrol is set at .5/1.5.
I did discover that I had two extremely undersized main line vents, unfortunately installed on an elbow, and neither was functioning. Figuring a functioning vent would be better than none until I could get someone to tap the pipe appropriately, I purchased a Gorton #2 for where I had enough clearance to put that size, and a Gorton #1 for the other vent. Unfortunately the Gorton #2 arrived defective (from everything I read on this site), verified by trying to blow through the vent but no air would pass. I purchased another, which just let steam pour out when installed. Again, I can't verify the pressure the system is running at until I can get the gauge installed.
So, given all this I realize that all the deferred maintenance leaking to extreme water usage has likely shortened the lifespan of the boiler. I accept that.
What I would like is recommendations on how to maximize my boiler cleaning/servicing. Is there anything I can do to maximize their time/make their job easier, given the lack of maintenance?
Second, how urgently do I need to get the chimney lined?
Thank you in advance for your expertise and advice. Typing all this out has made me realize how much I have learned in just four weeks...thanks to all who offer their assistance on this site!
0
Comments
-
Water usage at 3 gallons per week is still quite extreme, keep looking for where you are losing it. Are there any underground returns?
If you have a main vent blowing steam it's defective, contact Gorton about that.
I cannot comment on the oil burner side of things much, other than to say you should absolutely get it cleaned and serviced by a competent tech, that will do a full combustion analysis. If they are really good they may be able to down fire some if you truly are oversized. The manufacturer many times has a firing range on the boiler, if you are on the high end you should at least be able to go to the low end. I don't service them (another homeowner here), so I will leave it to others if there is anything you can do.
If you want more comment about your system we always enjoy pictures.1 -
Try this with the stuck Gorton #2: Turn it upside down and fill it up with water. Then shake it a few times and dump the water out. I'll bet that frees up the plunger. This might work with the other one too.
That first servicing is probably going to take a while. Here are some examples of what it might look like inside:
https://forum.heatinghelp.com/discussion/184249/you-can-tell-how-long-ago-this-was-serviced
https://forum.heatinghelp.com/discussion/164295/over-fired-3-pass-boiler
https://forum.heatinghelp.com/discussion/146509/quot-serviced-every-year-quot-we-were-speechless
https://forum.heatinghelp.com/discussion/132567/one-of-the-worst-maintained-oil-fired-boilers-weve-seen
Looking forward to your pics!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Yes it is against code and potentially very dangerous to fire any fuel burning appliance into an unlined chimney. The products of combustion can damage the chimney, specifically the mortar joints allowing products of combustion (Carbon Monoxide, etc.) to spill into the living space, and weakening the structure of the chimney. And a potential fire hazard.
The best thing you can do is find a great steam person. They can advise you of any deficiencies, and how to maintain the boiler in between service (annual) intervals.
And get the chimney lined.
And don't wait another 10 years.There was an error rendering this rich post.
1 -
KC_Jones said:Water usage at 3 gallons per week is still quite extreme, keep looking for where you are losing it. Are there any underground returns? If you have a main vent blowing steam it's defective, contact Gorton about that. I cannot comment on the oil burner side of things much, other than to say you should absolutely get it cleaned and serviced by a competent tech, that will do a full combustion analysis. If they are really good they may be able to down fire some if you truly are oversized. The manufacturer many times has a firing range on the boiler, if you are on the high end you should at least be able to go to the low end. I don't service them (another homeowner here), so I will leave it to others if there is anything you can do. If you want more comment about your system we always enjoy pictures.
I did contact Gorton about the defect vent and Ken got right back to me. Kudos on that.
The ability to tweak the boiler despite being oversized is definitely something I'll check into. Thank you again. Pictures coming up!0 -
Steamhead said:Try this with the stuck Gorton #2: Turn it upside down and fill it up with water. Then shake it a few times and dump the water out. I'll bet that frees up the plunger. This might work with the other one too. That first servicing is probably going to take a while. Here are some examples of what it might look like inside: https://forum.heatinghelp.com/discussion/184249/you-can-tell-how-long-ago-this-was-serviced https://forum.heatinghelp.com/discussion/164295/over-fired-3-pass-boiler https://forum.heatinghelp.com/discussion/146509/quot-serviced-every-year-quot-we-were-speechless https://forum.heatinghelp.com/discussion/132567/one-of-the-worst-maintained-oil-fired-boilers-weve-seen Looking forward to your pics!0
-
@BroadwichCT
Your off to a good start fixing what you have fixed. I would check "find a contractor" on this site. And also post where you are located, someone may have a recommendation.
Talk with friends family about a good contractor
I am guessing your in CT, and good contractors there are a little thin. You may be able to get @Charlie from wmass you could pm him1 -
STEVEusaPA said:Yes it is against code and potentially very dangerous to fire any fuel burning appliance into an unlined chimney. The products of combustion can damage the chimney, specifically the mortar joints allowing products of combustion (Carbon Monoxide, etc.) to spill into the living space, and weakening the structure of the chimney. And a potential fire hazard. The best thing you can do is find a great steam person. They can advise you of any deficiencies, and how to maintain the boiler in between service (annual) intervals. And get the chimney lined. And don't wait another 10 years.
I called in late August to get appointments for servicing the boiler, right after purchasing the house, and the first I was able to get was mid December. I'm experiencing that with all kinds of contractors.
I'm in SE Connecticut, and just found the New England Steamworks, but still waiting on when he's able to get to my area.0 -
0 -
The steam piping is creative, definitely not right. On point of clarification, see the picture I attached. I did red for one set of connections and blue for the other. Do I have the piping traced properly? If not could you take another picture from the other side to clarify?
0 -
@KC_Jones
Good question. Here are some additional photos from: (a) directly behind the piping in the photo you highlighted (b) as well as a shot looking from the side and upwards. If the light and/or angles are still problematic just let me know.0 -
That clarifies it. At first I thought you didn't have any kind of equalizer. It's piped entirely wrong, but there is "something" there at least. You will definitely get wet steam with that set up. I don't think that is your primary concern though, by your description. If it was me and the longevity of that boiler was in question (900 gallons of make up water), I'd leave the piping as is and just save up for when the boiler is replaced, then have it done properly, knowing you may only get this set up "so good".
I'd concentrate on getting the burner serviced, finding the leaks, and getting the venting squared away, in that order.
For leaks, it might not be water most likely steam. Steam is invisible so it can make it tough. radiator valve packings are one place, old vents are another. Use a mirror, or I like to use a metal wrench (chrome plated) and put it close to suspected leak points, then look for condensation. If you get condensation, you have a leak. Valve packings IMHO, aren't too bad and fairly DIY friendly, as are vent replacements.
1 -
@EBEBRATT-Ed. Thank you for the recommendation. I'll pm him. Thank you also for the encouragement that I'm off to a good start.0
-
@BroadwichCT
If you can get @Charlie from wmass or @New England SteamWorks you will be in the best hands possible. Too bad the installer didn't pipe it right. The fix shouldn't be that bad.
I agree with @KC_Jones
Fix up as many leaks as you can find and work on the venting. I would also calculate the EDR of the radiation connected that way when you get someone their they can determine if the burner can be downfired which may calm the system down a little bit0 -
@EBEBRATT-Ed
@KC_Jones
This sounds like a good plan of action.
You don't know how much I appreciate these recommendations and referrals. I moved out here from another part of the country and unfortunately I don't really know anyone in the area to get referrals.
Is there anything I should do (or not do) immediately prior to the service to make their job easier? Such as, run the boiler for x number of hours, don't run the boiler for x number of hours, anything along those lines?
@KC_Jones I like the recommendation of using something like a mirror to collect condensate. Smart!
0 -
Red Loctite can be "unlocked" with 500F heat. Blue Loctite is supposed to be unlockable with two big wrenches (one for backup), but a little heat might help.BroadwichCT said:I cannot verify the function of the Pressuretrol as some dopehead used thread lock on the pigtail and given the method of installation, I can't apply counter torque to get it free
https://www.loctiteproducts.com/en/know-how/build-things/threadlocker-red-or-blue-which-ones-right-for-you.html#C
0 -
@BroadwichCT
your boiler is the patient waiting for the doctor. could be worse. your running for now, try and get the vents to work if you can that's about it0 -
WMno57 said:
I cannot verify the function of the Pressuretrol as some dopehead used thread lock on the pigtail and given the method of installation, I can't apply counter torque to get it free
Red Loctite can be "unlocked" with 500F heat. Blue Loctite is supposed to be unlockable with two big wrenches (one for backup), but a little heat might help. https://www.loctiteproducts.com/en/know-how/build-things/threadlocker-red-or-blue-which-ones-right-for-you.html#C0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements