Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Over-fired 3-Pass Boiler

Steamhead
Steamhead Member Posts: 17,333
edited January 2018 in Oil Heating
We installed this Solaia eleven years ago. The house has gone through several owners since then, who did not use us for maintenance. The current owner was tired of the high fuel oil bills, so she got in touch and asked about switching to gas. The switch is easy on these boilers since Boyertown Furnace offers a Carlin EZ-Gas already configured for them.

Last week the boiler went down, so I responded and diagnosed a bad nozzle which had not been changed in quite a while. On inspection, I saw that whoever "serviced" the boiler last had used the wrong nozzle. This boiler, with the Beckett AFG, uses a 0.60x70B nozzle at 160 PSI for a firing rate of 0.75 GPH.

Someone had used a 0.75x70B nozzle, still at 160 PSI, which resulted in a firing rate of about 0.95 GPH- a significant over-firing. I put the right one in and fired it up.

The conversion was scheduled for this week, and this is what we found when we opened it up:







Pathetic. I won't mention the name of the oil company, but it's one of the ones now owned by Star Gas Partners.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting

Comments

  • Steamhead
    Steamhead Member Posts: 17,333
    edited January 2018
    Here's the boiler with the EZ-Gas installed, all clean inside and ready for more years of service.



    With proper maintenance, the oil company might still have this account. But they couldn't even bother to read the label on the boiler which tells exactly what nozzle to use.

    Like taking candy from a baby.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    Harvey Ramer
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,261
    edited January 2018
    I did a service call on a New Yorker (steamer) today that required a 4gph nozzle. Instead, it had a 2.25gph installed.
    Flue gasses were under 350 going into an unlined exterior masonry chimney. And it took an eternity for steam to reach the rads.
    We will do a little rad research, some math and get him fixed up.
  • Steamhead
    Steamhead Member Posts: 17,333
    How dirty was it?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,261
    Not too bad, actually. A few kibbles and bits in the boiler flues. The whole inside was covered in a light film of soot though. That was due to a malfunctioning Barometric Damper and the resulting loss of draft to the boiler.
    Dave_154
  • newagedawn
    newagedawn Member Posts: 586
    its sad when companies hire kids for cheap and dont train them, when they could pay a competent tech a good wage and make a family a happier life
    "The bitter taste of a poor install lasts far longer than the JOY of the lowest price"
    Ironman
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Yeah but I bet even over fired, if set up with an analyzer and smoke gun, wouldn't have made that mess.
    What's sad, as Frank alluded to, is these large companies are buying up everyone they can to 'get the gallons'. But aren't servicing them properly, continuing the conversation that oil is 'dirty, etc.'
    So they will continue to lose customers market share to gas and propane.
    Sad

    There was an error rendering this rich post.

    MikeAmann
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,298
    @Steamhead they probably did look at the rating plate and assumed the nozzle they took out was too small so he put a .75 to match the firing rate.

    Too bad. Must have been an old timer like me. Don't all oil burners run their pumps at 100psi?? Nope!!

    LOL
    Ironman
  • lchmb
    lchmb Member Posts: 2,997
    when they expect 4 tuneups in 8 hours what do you expect? And people dont want to pay to get it done right..they just want it done fast...
    MikeAmann