can you use copper for a steam radiator return?
Comments
-
The die hard steamers will say not to. But it has been done successfully by many. There may be some issues with dissimilar metal over time but the time is going to be many years. Then it is the next guy's problem. That is why you want to get black pipe and fittings (not galvanized) just in case YOU are the next guy. Seems like the Black Pipe will insure that YOU are not the next guy.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Shouldn't be a problem... I hope... having done that a few times...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
@bbillcee
The general rule is copper is ok below the boiler water line. Above the boiler water line it should be black pipe.
But sometimes you do the best you can. Certainly the steam near boiler piping and the steam mains should not be copper1 -
@Jamie Hall says it's ok... then it's ok. He has done this and he is still at the location where he did it... so he IS that NEXT GUY!Jamie Hall said:Shouldn't be a problem... I hope... having done that a few times...
...and hs has over 7 times more posts than me!Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Concerning the dissimilar metals, many suggest a brass valve between the copper and black iron....at each end.
IIWM, I would add a hose bib in the copper at each end. Then you could flush the line and see what might be in there after a few years.0 -
thanks guys, here some pics of the mess!
0 -
Threaded brass pipe?Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0
-
Those elbows should be taken off and replaced with tees. When you drop under a doorway your also supposed to pipe over the door for a vent. But if it heated well before i guess you can skip that.
I wouldn't hesitate to use copper there. You should put something around the pipe under the floor to prevent corossion.2 -
-
-
Ok, this is weird to me. There is a bottom connection feeding from the top, there is a top connection feeding from the bottom. This is the basement, that's a wet return.
That entire rad, or a large portion of it, has to be below the boiler water line, unless the boiler is in a deep pit? Even so, the radiator connections make no sense.
For the original question I'd do copper on that, and the aforementioned tees (for me for cleanouts) all day long. I'd also install it in such a manner that if more of the other run rotted out, I could easily replace it. Either unions, or running the copper above ground a short distance as it's easier to cut later.0 -
I can't find ratings for anything higher than 200 degrees, but it's OK for 80psi at that temperature so I would think it would be fine for any wet return, especially a buried one where the ground will act to cool it.mattmia2 said:What happened to the pex discussion? Seems that pex would be rated at far more than 30 psi at 212 f and would solve a lot of ground and masonry contact problems in a wet return.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
I've never seen a reference to PEX being able to withstand anything over 200 F. One has to remember that the strength doesn't fall gently and gracefully with temperature... things melt or begin to deform very easily.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
OK what is the temperature of a wet return? I think I'd bet it's well under 200 and now I must check
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
Should be well under 200. It might be warm... but not much more than that.ethicalpaul said:OK what is the temperature of a wet return? I think I'd bet it's well under 200 and now I must check
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
JUGHNE said:Can you explain the piping on that radiator in the picture? Does it heat well? Where does the pipe on the left side go to?
0 -
0
-
Heating with steam condensate returning.
That rad would stay full of water up to the height of the boiler water line.
It is part of the wet return system.
All your wet return lines below the boiler water line are always full of water.
It sits in the pipe and part of your radiator until some more is added to the end where the pipe drops down from the heating main.
Add in one end and it flows out the other end.
That is why maybe it might be good to replace all the wet return you have, if practical. Nasty water sits in it all year long.
It is like a trap under the sink.0 -
If your wet return is dry and full of steam you have bigger problemsmattmia2 said:I guess the issue might be if something goes awry and it ends up dry and full of steam.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
Like... much bigger problems!ethicalpaul said:
If your wet return is dry and full of steam you have bigger problemsmattmia2 said:I guess the issue might be if something goes awry and it ends up dry and full of steam.
On the return water question -- that's not hard to figure out. Every 10,000 BTUh that the boiler is putting out will result in about 1.25 gallons of condensate per hour. We usually think in terms of gallons per minute for water flow -- but for condensate we are talking fractions of a cup per minute!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Interesting idea, I’m guessing there is a drip off the main that feeds the condensate into the bottom.
I can’t imagine how much crud must be in that thing.
Has it ever been flushed out?0 -
Since it doesn't appear that there is any way to do that without a fair bit of surgery, i'm going to go with no.KC_Jones said:Interesting idea, I’m guessing there is a drip off the main that feeds the condensate into the bottom.
I can’t imagine how much crud must be in that thing.
Has it ever been flushed out?0 -
the original returns failed in 1980 so that when this stuff was put in and its never been flushedmattmia2 said:
Since it doesn't appear that there is any way to do that without a fair bit of surgery, i'm going to go with no.KC_Jones said:Interesting idea, I’m guessing there is a drip off the main that feeds the condensate into the bottom.
I can’t imagine how much crud must be in that thing.
Has it ever been flushed out?
0 -
My great uncle Had the house built in 35, my father bought it off him in 66 and I bought in 2006 .. the story was that this configuration was taken from “popular mechanics” back in the day… it’s simply using the return hot water to put out some additional heat with the radiator hooked in … does the radiator get hot? Yes not burning but it puts out heat … I’m not a plumber but it seems to work🤷🏻♂️I would assume the rad has to fully fill up with water before it returns to the boiler… I have question That maybe someone here can answer… how much water actually raturns? A gallon? 5 gallons? 10 gallons?bbillcee said:JUGHNE said:Can you explain the piping on that radiator in the picture?
Does it heat well?
Where does the pipe on the left side go to?
It's an interesting condenser. No need for traps?0 -
It is something that an article in "Popular Mechanics" was the idea for this.
Once upon a time people would do things like this.
Say, change the pulley speed for heating to AC etc.
Thermocouple change outs were just something any guy could do.
I had some Handy Man books from that era, it was surprising what projects the homeowner would take on.
And the next generation would learn to do the same type of things.
Today they are challenged to change the furnace filter.
Some literally do not know if they have 2 heating units or where they are.5 -
lol very true!JUGHNE said:It is something that an article in "Popular Mechanics" was the idea for this.
Once upon a time people would do things like this.
Say, change the pulley speed for heating to AC etc.
Thermocouple change outs were just something any guy could do.
I had some Handy Man books from that era, it was surprising what projects the homeowner would take on.
And the next generation would learn to do the same type of things.
Today they are challenged to change the furnace filter.
Some literally do not know if they have 2 heating units or where they are.
0 -
-
0
-
-
I haven't, but the rated maximum working temperature is 140°F. That's even less than PEX.BobC said:Has anyone tried boiling some PVC pipe in a saucepan to see how it reacts to 212 temperatures?
Copper lasts forever as potable water piping. If fresh water in all its varying compositions doesn't hurt it, it should be fine for condensate, which is basically distilled water with a lot of dissolved iron.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
My great uncle Had the house built in 35, my father bought it off him in 66 and I bought in 2006 .. the story was that this configuration was taken from “popular mechanics” back in the day… it’s simply using the return hot water to put out some additional heat with the radiator hooked in … does the radiator get hot? Yes not burning but it puts out heat … I’m not a plumber but it seems to work🤷🏻♂️I would assume the rad has to fully fill up with water before it returns to the boiler… I have question That maybe someone here can answer… how much water actually raturns? A gallon? 5 gallons? 10 gallons?bbillcee said:JUGHNE said:Can you explain the piping on that radiator in the picture?
Does it heat well?
Where does the pipe on the left side go to?
Do you need the heat there? Or I should ask Do you need to waste the fuel keeping that rad hot?
Is that the condensate coming down to the left? Is yes can you run it closer to the ceiling until your past the door?0 -
Copper lasts forever as potable water piping. If fresh water in all its varying compositions doesn't hurt it, it should be fine for condensate, which is basically distilled water with a lot of dissolved iron.
If "forever" is 5-50 years, sureNJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el1 -
About half of mine is about 70 and still in good shape and it has spent its life in ann arbor water that turns brass screws and washers to powder.ethicalpaul said:Copper lasts forever as potable water piping. If fresh water in all its varying compositions doesn't hurt it, it should be fine for condensate, which is basically distilled water with a lot of dissolved iron.
If "forever" is 5-50 years, sure1 -
Pecmsg, you are thinking that cond rad is wasting fuel?
True, but I can see benefits to a little heat in the basement.
Especially if the piping is insulated.
Less waste heat than what sits in the boiler when not firing.
It is probably a sludge collector though.
Keeping sludge out of the wet return and boiler.
I can see it causing slow condensate return eventually.
Would have been handy to have a drain port on the other lower tapping.
And I though it would be full only up to the water line....wrong....it has to fill completely up to spill out of the top connection.0 -
Congrats! I had the same experience in Michigan when I lived there, but google "copper pinholes"mattmia2 said:About half of mine is about 70 and still in good shape and it has spent its life in ann arbor water that turns brass screws and washers to powder.
NJ Steam Homeowner.
Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
See my sight glass boiler videos: https://bit.ly/3sZW1el0 -
If the heats NOT needed in the basement, then yes, it is wasting fuel, just like uninsulated pipes. If they want the heat thats fine.JUGHNE said:Pecmsg, you are thinking that cond rad is wasting fuel?
True, but I can see benefits to a little heat in the basement.
Especially if the piping is insulated.
Less waste heat than what sits in the boiler when not firing.
It is probably a sludge collector though.
Keeping sludge out of the wet return and boiler.
I can see it causing slow condensate return eventually.
Would have been handy to have a drain port on the other lower tapping.
And I though it would be full only up to the water line....wrong....it has to fill completely up to spill out of the top connection.1 -
It would interesting to looks at the rad through a FLIR camera to see how far up the sludge has accumulated.I have to admit the multiple elbows and reduction in size of the return makes me uncomfortable. At some point it’s going to completely fill up and present a puzzle/headache to someone.IMHO, I’d follow @pecmsg advice and route the pipe as it comes down the wall with a 90 to go over the top of the door and then over to the boiler.The radiator is not capturing free heat, the boiler will have to replace that energy during the next cycle. I admit the residual heat would likely be given up to the boiler room regardless doesn't impacting operating cost. Just shifting where the residue energy in the condensate gets dissipated.If you want to heat that room you can do a hot water heat off the boiler below the waterline as I’ve seen people discuss on the forum. Seems like it was refer to as a “Bronx” or “Brooklyn” system.0
-
That pipe may be a separate return??0
-
Good point. I see the larger (1-1/4”?) line come down and into the lower radiator inlet and come out the upper port on opposite side and down into what looks like a tee to a smaller 3/4” line that returns to boiler on one side and wraps around corner other side.Is that a second smaller condensate return?0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements