Add zone of radiators to existant floor radiant
josephny
Member Posts: 274
I'm looking into adding another zone with panel radiators to the under floor radiant I have now.
Wondering how to choose between the various piping configurations shown below:
0
Comments
-
So how would one decide which piping layout to use?
0 -
If I had to do it, I'd do it with a manifold for the panel radiators separate from the radiant manifold. Feed them both off a primary loop, but you will need to use a thermostatic mixing valve at least on the radiant floor manifold, and separate pumps.
Reason being, the panel radiators need significantly different water temperatures from what the floor needs, and they may not be set up to circulate all the time -- while the floor should be.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Jamie,Jamie Hall said:If I had to do it, I'd do it with a manifold for the panel radiators separate from the radiant manifold. Feed them both off a primary loop, but you will need to use a thermostatic mixing valve at least on the radiant floor manifold, and separate pumps.
Reason being, the panel radiators need significantly different water temperatures from what the floor needs, and they may not be set up to circulate all the time -- while the floor should be.
Thank you for sharing your expertise.
My understanding of these things is very limited, but I thought that any zone/loop/manifold would be tapped off the secondary loop? I am using the IBC EZ Pipe Manifold off the boiler, which creates the entire primary loop.
I can figure out how to repipe and tap off the secondary loop, feeding it to another distribution manifold (same way and type as the floor manifold).
But, from what I've read, it's perfectly fine putting 135 or 140* water through the panels.
And, I'd sure prefer to keep it simple -- and I think the simplest way would be to just keep the single zone, single pump, single manifold and add a circuit for each panel.
Thanks.0 -
If you are willing to pay for oversized radiators that will work at the lower water temps, iI would just add to the radiant manifolds. You want to have a way to balance it, I think your existing manifold has that capacity."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
That's the understanding I was missing!Zman said:If you are willing to pay for oversized radiators that will work at the lower water temps, iI would just add to the radiant manifolds. You want to have a way to balance it, I think your existing manifold has that capacity.
Thank you all for your patience and generosity.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements