Modcon flue gas smells of gas
rhl
rhl Member Posts: 109
Hi,
I've noticed a condition were on startup we smell gas from the boiler flue pipe just for a moment before we start seeing the white flue gas.
Modcon aqua balance combi boiler.
I replaced the flue gas sensor (which was corroded) and the ignitor -- went ahead and vacuumed out heat exchanger and cleaned per manual.
Refractory is partially worn -- will replace when new part arrives.
Boiler was installed in 2018.
Is this normal? Anything else to check?
    Are you smelling gas -- or combustion products? Both have an odour, but are quite different.
    mattmia2 Member Posts: 17,476
    did you do a combustion analysis on this? Might not be unusual for a small amount of unburned gas to be emitted as it is lighting
    Zman
    HVACNUT Member Posts: 7,526
    Are you smelling this outside at the exhaust or inside at the boiler?
    You might get a good whiff if you're near the exhaust outside on ignition only. Inside, that needs to be checked. Do you have a combustion analyzer and manometer?
    EBEBRATT-Ed Member Posts: 20,482
    Do a combustion analysis. If it lights ok and the combustion test is ok I wouldn't worry about it
  • rhl
    Outside the boiler -- I don't have one personally -- will ask plumber. thank you everyone.
    edited November 2021
    You don't necessarily need a plumber. A service technician familiar with mod cons and the correct tools is who's needed. Come back and let us know. The tech should leave a printout or email you the combustion report.
    You don't necessarily even want a plumber. Not all of them have any idea how to adjust a mod/con...