Replacing steam valves

Help! I am new here. We just installed a boiler as the home previously had one but the previous owners removed it so we added it back. Well it’s now up and running but some of the radiators make a lot of noise. The installers recommended switching out the vents. Well the radiators are recessed in the wall. I attempted to remove one of the vents but it broke off. Any idea how I get this piece out of here?? That bolt will not budge and I cant seem to find a socket wrench that will grip it to turn. Do I really have to tear down the wall?? Pics included of the wall and the piece that broke. 

Comments

  • delcrossv
    delcrossv Member Posts: 1,165
    The experts may have a better ideas but I'd start with PB Blaster on the threads, then get one person on a pipe wrench on the coupling below the vent and a socket wrench on the vent itself.
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • Jamie Hall
    Jamie Hall Member Posts: 24,479
    Well that's pesky of it.

    I'll get to that in a moment, but first... can you describe the noises? There are many different noises a steam system can make (it really shouldn't make any) -- and as many or more causes for them. But vents, unless the noise is a whistle, are rarely the exact culprit. So if you can describe what is going on, maybe we can figure out what to do to make it shut up.

    Now. I'm not quite sure what that widget was before it broke. I have to admit that it doesn't quite look like bits and pieces of a vent, but it might be. To get it off, though... my first thought would be to find a deep socket which you can destroy and which is a smidge smaller than that hex (e.g. -- if that hex is about 3/4 inch, try a 18 mm) and pound it on there. Use ample PB Blaster or equivalent. Then if you can get in there with an impact wrench, try that. Otherwise you can hope you can get at least a two tooth swing on a ratchet wrench and see if you can get it. Otherwise, your point of attack is going to be that reducer. Your clearances are to tight for a nutcracker, so you will need to cut a couple of slits in that reducer if you can get in there. It looks to me as though there may just barely be clearance to get a Dremel and its cutting wheel in there. Once you get some slits, you may be able to spring it open enough with a cold chisel to get it out of there.

    good luck...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • mattmia2
    mattmia2 Member Posts: 10,686
    edited October 2021
    Looks like a half or 3/4 inch Male steam air vent. Try a deep well socket and an extension and ratchet. Try to hold the coupling with a pipe wrench if you can.

    It was something like this:
    https://www.supplyhouse.com/Hoffman-401413-4A-1-2-x-3-4-Straight-Steam-Main-Air-Valve-8037000-p

    I think those are trane convectors but others would know better.
  • clammy
    clammy Member Posts: 3,150
    Carbonics pipe break is the product to use, spray it on rap on the pipe and wait a few minutes to do it’s magic and then dis assembly . I ve used every product out there over the years and this stuff is clearly the stuff . I ve removed piped that where we’ll over 50 years old using this stuff not that it will do everything but it’s clearly the best I ve used ever as compared to other products it does smell but it does work . Peace and good luck clammy

    R.A. Calmbacher L.L.C. HVAC
    NJ Master HVAC Lic.
    Mahwah, NJ
    Specializing in steam and hydronic heating

  • Handymandy327
    Handymandy327 Member Posts: 7
    mattmia2 said:
    Looks like a half or 3/4 inch Male steam air vent. Try a deep well socket and an extension and ratchet. Try to hold the coupling with a pipe wrench if you can. It was something like this: https://www.supplyhouse.com/Hoffman-401413-4A-1-2-x-3-4-Straight-Steam-Main-Air-Valve-8037000-p I think those are trane convectors but others would know better.
    That’s the steam air vent im replacing them with. But the bottom piece is the same. I tried a deep well socket with an extension and wrench. I used a 11/4 but it still won’t grip the bolt to turn it. It’s such a tight fit I don’t think I can get a pipe wrench in there 
  • Handymandy327
    Handymandy327 Member Posts: 7
    edited October 2021
    Well that's pesky of it. I'll get to that in a moment, but first... can you describe the noises? There are many different noises a steam system can make (it really shouldn't make any) -- and as many or more causes for them. But vents, unless the noise is a whistle, are rarely the exact culprit. So if you can describe what is going on, maybe we can figure out what to do to make it shut up. Now. I'm not quite sure what that widget was before it broke. I have to admit that it doesn't quite look like bits and pieces of a vent, but it might be. To get it off, though... my first thought would be to find a deep socket which you can destroy and which is a smidge smaller than that hex (e.g. -- if that hex is about 3/4 inch, try a 18 mm) and pound it on there. Use ample PB Blaster or equivalent. Then if you can get in there with an impact wrench, try that. Otherwise you can hope you can get at least a two tooth swing on a ratchet wrench and see if you can get it. Otherwise, your point of attack is going to be that reducer. Your clearances are to tight for a nutcracker, so you will need to cut a couple of slits in that reducer if you can get in there. It looks to me as though there may just barely be clearance to get a Dremel and its cutting wheel in there. Once you get some slits, you may be able to spring it open enough with a cold chisel to get it out of there. good luck...
    The noise is like a whistle or it blowing the steam. The installer said it was the vents. I was able to replace one of them and it did stop on that one so I assume that is the problem. 

    I tried a deep socket wrench. I used 1 1/4 but it still didn’t get on the bolt. Maybe if I pound it though it will get stuck. I don’t think I can fit an impact wrench in there. 

    I will try the dremel. Hopefully I can rent that instead of buying one 😅
  • Jamie Hall
    Jamie Hall Member Posts: 24,479
    If the sound is a whistle sort of, and it's coming from the vents... check you system pressure and make sure the cutoff is below 2 psi.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    mattmia2ethicalpaul
  • Handymandy327
    Handymandy327 Member Posts: 7
    delcrossv said:
    The experts may have a better ideas but I'd start with PB Blaster on the threads, then get one person on a pipe wrench on the coupling below the vent and a socket wrench on the vent itself.
    Will definitely try the pb blaster. I’m not sure if we can reach the socket wrench below the vent tho. It’s just a hallow cut out on the floor
  • Handymandy327
    Handymandy327 Member Posts: 7
    clammy said:
    Carbonics pipe break is the product to use, spray it on rap on the pipe and wait a few minutes to do it’s magic and then dis assembly . I ve used every product out there over the years and this stuff is clearly the stuff . I ve removed piped that where we’ll over 50 years old using this stuff not that it will do everything but it’s clearly the best I ve used ever as compared to other products it does smell but it does work . Peace and good luck clammy
    Where can I find that? I tried googling carbonic pipe break but nothing useful came up. Thanks!
  • Dan_NJ
    Dan_NJ Member Posts: 254
  • JUGHNE
    JUGHNE Member Posts: 11,248
    Maybe a good quality basin wrench. Look for one in a plumbing store.
    It needs to have good teeth.

    Try all the spray several times.
    You can put a pipe wrench on the handle to get leverage.
    It is called abusing the tool but that is what they are for, to be used.
  • Handymandy327
    Handymandy327 Member Posts: 7
    Just wanted to update that we ended up having to cut a whole in the wall. So will not be changing out the other ones anytime soon 😅 I can deal with the whistling for now
  • mattmia2
    mattmia2 Member Posts: 10,686
    I still don't see why if you measure that and get a deep well socket that size you can't remove it with a ratchet and extension(s) long enough to get out of the air outlet opening. shower valve sockets are also an option but would be harder to turn because you would have to do it down inside the enclosure.
    delcrossv
  • Handymandy327
    Handymandy327 Member Posts: 7
    mattmia2 said:
    I still don't see why if you measure that and get a deep well socket that size you can't remove it with a ratchet and extension(s) long enough to get out of the air outlet opening. shower valve sockets are also an option but would be harder to turn because you would have to do it down inside the enclosure.
    We tried multiple sockets. Even the installation company came out to try. We couldn’t find a socket that would fit and/or get a grip to turn it. Can try again in the summer when we don’t have to have the heat running 
  • mattmia2
    mattmia2 Member Posts: 10,686
    I would measure it with a micrometer or a caliper then try to match it up to a standard english or metric socket size and order that socket from someone like zoro or mcmaster-carr.
  • KC_Jones
    KC_Jones Member Posts: 5,789
    Maybe it's just the angle of the picture, but that almost looks like an 8 point, not a 6 point. That would contribute to limiting socket choice. If that's the case would need an 8 point socket, which could explain having trouble getting one to fit.

    Again, maybe it's just a weird angle in the picture.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    mattmia2
  • mattmia2
    mattmia2 Member Posts: 10,686
    KC_Jones said:

    Maybe it's just the angle of the picture, but that almost looks like an 8 point, not a 6 point. That would contribute to limiting socket choice. If that's the case would need an 8 point socket, which could explain having trouble getting one to fit.

    Again, maybe it's just a weird angle in the picture.

    I didn't catch that, but I think it is.
  • delcrossv
    delcrossv Member Posts: 1,165
    Sure looks like it. Good catch. I know Proto makes 8 point sockets, probably can get a cheap set off Amazon.
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • ethicalpaul
    ethicalpaul Member Posts: 6,356

    Just wanted to update that we ended up having to cut a whole in the wall. So will not be changing out the other ones anytime soon 😅 I can deal with the whistling for now

    Don't miss Jamie's helpful post where he mentioned that your steam pressure may be too high if you hear whistling...you shouldn't have to deal with whistling, even if the vents do leak a bit (the pressure should never be high enough to cause a whistle).

    But long term you really don't want leaking vents, so do keep an eye on them and mark any leakers for replacement when convenient

    NJ Steam Homeowner.
    Free NJ and remote steam advice: https://heatinghelp.com/find-a-contractor/detail/new-jersey-steam-help/
    See my sight glass boiler videos: https://bit.ly/3sZW1el

    mattmia2
  • JUGHNE
    JUGHNE Member Posts: 11,248
    Compare the flats on it to the flats on the reducing bushing below.
    KC_Jones
  • KC_Jones
    KC_Jones Member Posts: 5,789
    JUGHNE said:

    Compare the flats on it to the flats on the reducing bushing below.

    That definitely confirms 8 point for me, I will remember to look down next time.

    An old boss would have called that a "forest for the trees kind of thing".
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control