Hydra
tiki
tiki Member Posts: 1
Hi
I have a HYDRA Evolution that shut down and the only way to start it again is by resetting it with the fuse. Does not seem to be a safety issue cause I let it stand closed until it's cold but to restart it have to go and remove the fuse and that will restart it.
Tried when it's working putting a small fan in frond of it but it didn't help.
Does changing the motherboard fix the issue or something else is in the play.
Thank you
tiki
  • Ironman
    Ironman Member Posts: 7,927
    Interrupting the power probably resets the board from a safety lockout. You need to find which safety is tripping and why.
    Bob Boan
    A bit more information might help. You are referring, I presume, to one of the Hydra Evolution electric boilers as manufactured by Dettson? This link: https://www.dettson.com/wp-content/uploads/2015/04/X40156-H_HYDRA_EN.pdf may take you to the owner's manual, assuming you can identify the model. They are rather short of trouble shooting, but I do note one comment: the ambient temperature in the vicinity of the boiler must be less than 27C.
    I note that Dettson does have service technicians in the Montreal and Rive Sud areas. Have you contacted them?
  • sydneyblum
    sydneyblum Member Posts: 3
    I was able to purchase a Dettson circuit board and an electrician replaced my defective one with this new one. So far the boiler is functioning correctly.