Winter is Coming, Heat is Missing
USN_Retired
Member, Email Confirmation Posts: 6
I have a new Laars Mascot II Combi unit. I have since learned this was probably a bad choice, so now I’d like to try and make the best of it.
The unit is installed in an insulated garage using a primary/secondary loop setup with a heat exchanger separating the two. Primary side was flushed and filled with water using the internal pump to circulate liquid and remove air then the unit was powered down for the night.
Power was reapplied the following morning prior to the propane service folks arriving. The 24V 2A circuit breaker immediately tripped.
Obviously the unit cannot be tested or fired without control voltage, and the blower runs continuously. There are no visible signs of anything abnormal. My next step will be to remove the control module and open it to see if anything jumps out.
Does anyone have any idea of what the “usual culprit” might be?
Thanks.
The unit is installed in an insulated garage using a primary/secondary loop setup with a heat exchanger separating the two. Primary side was flushed and filled with water using the internal pump to circulate liquid and remove air then the unit was powered down for the night.
Power was reapplied the following morning prior to the propane service folks arriving. The 24V 2A circuit breaker immediately tripped.
Obviously the unit cannot be tested or fired without control voltage, and the blower runs continuously. There are no visible signs of anything abnormal. My next step will be to remove the control module and open it to see if anything jumps out.
Does anyone have any idea of what the “usual culprit” might be?
Thanks.
0
Comments
-
Is the 24V 2A circuit breaker part of the boiler? Some pictures would help.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Look around for loose wires, maybe a wire nut came off, Or a wire could be pinched under a cover0
-
Did something leak and soak some portion of the controls?0
-
-
Yes, the circuit breaker is part of the boiler and is located behind the center panel with the power switch, display etc.Is the 24V 2A circuit breaker part of the boiler? Some pictures would help.
The circuit breakers are near the center and the 2A one is on the right with the white line indicating it is tripped. The left breaker is the main 10A.
0 -
0
-
No loose or pinched wires, and no missing wire nuts.EBEBRATT-Ed said:Look around for loose wires, maybe a wire nut came off, Or a wire could be pinched under a cover
0 -
There was a small amount of water that dripped from the air eliminator but it was wiped from the tray and didn't contact any circuit components.mattmia2 said:Did something leak and soak some portion of the controls?
0 -
Well folks, I went down the painful road of disconnecting things and reconnecting. No changes so I started chasing wires. Clipped one tie wrap on a bundle that held it to the chassis, and everything works.
I’ve studied that bundle looking for anything. Nothing!!! Maybe some tension on a connector downstream or some other bizarre item? Who knows?
The bundle is nicely tied over its length and seems to lie nicely where it should. I have not replaced the tie wrap but will keep an eye on things.
I’ll get the propane folks out next week to accomplish the fuel conversion.
I’ll keep everyone posted.1 -
i'd look very carefully along that whole harness for a wire that chaffed or cut on the edge of something or got melted somewhere. wen you cut the zip tie something anywhere from end to end of that harness could have moved away from what it was touching. especially look for wires passing through holes with raw metal edges where someone didn't put a grommet back while working on it.1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements