Expansion tank psi after shipping

Options
jgaudet
jgaudet Member Posts: 87
I bought a #90 -14 gallon diaphragm expansion tank I think from PEX universe maybe and it had to be shipped to me and said it was pre pressurized to 12 psi but when I checked it it's 28 psi would that be cause it shipped by plane maybe?  Also my fill valve is pre set to 15 psi when I take the air down in my tank should I go to the recommended 12 or go to 15? Thanks.

Comments

  • HVACNUT
    HVACNUT Member Posts: 5,841
    Options
    Use an accurate water pressure gauge, make sure cold water pressure is at 15 psi (hydro coil in an attic?) and make the extrol 15 psi.
  • jgaudet
    jgaudet Member Posts: 87
    Options
    Do I need a water pressure gauge if I'm checking the air PSI?  And I don't have a hydro coil. It's for hot water boiler for heating my house
  • Jamie Hall
    Jamie Hall Member Posts: 23,324
    Options
    You need an accurate air pressure gauge to set the expansion tank. It must be disconnected from the system -- or at least valved in such a way as to be open to the air. Then set it to your desired system pressure, less about 2 psi. Then reconnect it to the system

    Now -- you need an accurate water pressure gauge to make sure that your system is charged to the correct pressure. Not all automatic feed valves are all that accurate... nor are the gauges on boilers or whatever.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • jgaudet
    jgaudet Member Posts: 87
    edited October 2021
    Options
    Ahh ok got ya. My tank ain't hooked up yet I just got it Im doing my system over and I checked the psi and it's showing 28 psi so I will have to let air out till it gets down to 12 psi then hook hook it all up.. also when I fill my system back up and bleed the zones should I isolate the expansion tank while.i bleed the zones or no? And I put a picture here is my expansion tank good to be piped like this or does it have to be directly under the spirovent? Thanks 
  • Zman
    Zman Member Posts: 7,569
    Options
    Assuming that the circ is pumping to the left of the diagram, that location should work well. I prefer to not locate the tank directly below the separator. Sediment tends to end up in that location that will end up in the tank and reduce its life expectancy. If you install a valve like this (or build your own) you can check the pressure of the tank without removing it from the system. https://www.supplyhouse.com/Webstone-H-44672-1-2-Pro-Pal-Full-Port-Brass-Ball-Valve-w-Hi-Flow-Hose-Drain-FIP-x-FIP-600-WOG?gclid=CjwKCAjwk6-LBhBZEiwAOUUDp9YG4yV0LLWxSceQ6sJK8DXsUFAtWxU8fVVwIaqgsGH7zFRUa14ZexoCyUYQAvD_BwE
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • jgaudet
    jgaudet Member Posts: 87
    Options
    Yes you are correct it is pumping to the left to the zones. I just wasn't sure if the piping going to the expansion tank could turn like that in the picture! And I actually got the exact same service valve i was going to put it on top of the tank like my picture but I think I will install it right under the spirovent jr. And then just pipe down to the tank with the 1/2 pipe!  Also do you isolate the tank when bleeding the zones? 
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,544
    Options
    You can isolate the tank if you want to when filling, it really doesn't matter
  • jgaudet
    jgaudet Member Posts: 87
    Options
    @EBEBRATT-Ed ok thanks I probably won't isolate it I just wanted to make sure, I'm almost done doing my system over and will have to bleed it after I get it filled back up, here's a pic of what my old return manifold looked like and now my new one. Just have to finish up the supply side now. Here's what's done so far.