Understanding 007e curve
mjstraw
Member Posts: 41
I think I have an understanding of the application of conventional circ performance curves. But the curve for the 007e has me confused.
At 10 feet of head, it shows 0-8.5gpm flow. How does the circ determine exact flow at 10ft?
At 10 feet of head, it shows 0-8.5gpm flow. How does the circ determine exact flow at 10ft?
Mark
Indiana PA
Indiana PA
0
Comments
-
It doesn't, really. Rather, if it is used as a constant head device, it will automatically vary its speed so that it delivers the requested head -- in this case, 10 feet. Varying the speed varies the flow, which in turn varies the head lost in the system. The maximum flow it can produce at that head is the 8.5 gpm.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
Still confused. If it's going to bump head up to 10ft by ramping up speed, why does the curve show flow values for lower head?Mark
Indiana PA0 -
If I recall correctly, if you are using it as a constant head device you can set it for any head you want -- up to its cutoff head, of course -- or, if used as a constant flow device for any flow up to the maximum it can deliver.
Keep in mind that for any given pump, the combination of head and flow which it will deliver is based on the rpm of the pump. The exact combination of head and flow which the pump will produce in a given system is determined by the head loss characteristics of the system as related to the head gain characteristic of the pump. The former is -- in most cases -- fixed. More flow, more head loss. The latter is also fixed for any particular rpm. More flow, less head added. At some point the characteristic curve of the system will intersect with the characteristic curve of the pump, and that's what the system will operate at.
The 007e is a variable speed pump. It can be controlled to run at any speed from zero up to its maximum speed. With a suitable controller, you can set it to run at any combination of head and flow you want, provided only that it is within the maximum curve. In the case in which you are interested -- varying flow at a lower fixed head -- it's mostly for convenience. From the engineer's standpoint, it might be more helpful, I suppose, to have curves showing the pump rpm or, better, the pump efficiency at various constant heads, or the same information at various constant flows. But the resulting graphs are going to get pretty complicated...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
The circulator doesn't determine the flow, the system does.
We need to know what the system curve is and then plot that with the circ performance curve and where the two curves intersect it the actual flow and head that is occurring.
We go into details on how to get those numbers with this webinar
EnjoyDave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
1 -
Good explanations. I'd add that those little circs can be made with various characteristics. Before variable speed Taco catalogue offered pumps whose flow was finite even at zero head and others with ever increasing flow as resistance decreased. Chosen correctly one could then design intelligent circuits with simplistic on/off control. Now with variable speed one must decide how she wants each circ to behave.0
-
Most of the small ECM circulators have the control circuit built in and you can choose the behavior(although the 007e does not, something like the Grunfos Alpha 2 does)0
-
that's a great question, is the decimal that's throwing you off? I would agree, net flow is dictated by system curve, and there is small precentage of error; it will be close.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
Thanks Dave H_2 (can't get @ to work with your ID)
I watched that webinar and the one on ECM circs. The latter was the more helpful of the two.
@mattmia2 had it right earlier. The 007e runs in constant pressure aka constant head aka zone valve mode. Can't be changed to any other mode. Curious that it's also advertised as a zone circ while the ECM webinar recommended a fixed speed circ for that purpose.
Mark
Indiana PA0 -
Correction - After 7 days of continuous circulation it switches to proportional pressure mode. But there is nothing you can do to force a mode change.
Mark
Indiana PA0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements