Steam Replacement
Dan Foley
Member Posts: 1,260
We were called in to try to fix this steam system in Georgetown. It was installed in March and suffered from uneven heat, short cycling and severe water hammer. The sections were also actively leaking at the push nipples.
The boiler was connected to a Webster vapor system with a combination of indirect radiators, convectors and radiators. The pressuretrol was set to 6 PSI.
The biggest issue was the boiler was oversized - by over 2-1/2 times. There was no fixing this one. Rip it out and start over.
0
Comments
-
We went back with a properly sized Peerless 64 Series. Removed the header and Re-piped to manufacturer specs. We replaced the pressuretrol with a Vapor-stat set to 8 oz. and increased the venting.We did the start up today. Quiet with no banging. All radiators hot.4
-
These fittings were at the ends of the steam mains. I had never seen these before. The picture is not clear but they are stamped “Webster Dirt Pocket”.1
-
Beautiful, @Dan Foley !Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
-
Excellent job as always. Amazing the boiler leaked like that when it was almost new. I hope they take the previous contractor to court.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Nice job!
The old (new) boiler couldn't have had much run time since March. Must have water hammered itself to make the nipples leak or they didn't assemble it right0 -
Great looking job.
best of all before receiving the final payment you can say "youve got Heat"
JakeSteam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0 -
Dan Foley, Frank or Gordon , was wondering if you have a view of Peerless, vs Weil Mclain vs Smith commercial cast iron steamer. Gas power burner. WM 88, Smith 19HE or Peerless LC. We have mostly used Weil Mclain but are maybe steering in another direction. Views would be appreciated.
Thanks
Tim0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements