How Many Thermostat Wires in One Hole.
Alan (California Radiant) Forbes
Member Posts: 4,214
We have a job in San Francisco with 25 zones. I know: Crazy, but the owner is a techie and likes choices.
I usually drill 3/8" holes for thermostat wires and run one wire per hole, but with so many thermostats, it makes more sense to drill one or more large holes for all of them; 1-3/8" size since that's a common drill bit for us.
I know that sensor wires should run alone, but is there a problem grouping thermostat and manifold actuator wires?
I usually drill 3/8" holes for thermostat wires and run one wire per hole, but with so many thermostats, it makes more sense to drill one or more large holes for all of them; 1-3/8" size since that's a common drill bit for us.
I know that sensor wires should run alone, but is there a problem grouping thermostat and manifold actuator wires?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
Are the manifold actuator wires at line voltage or 24 volts? If line voltage they shouldn't (depending on code, flat out mustn't) be run in the same hole, never mind conduit.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Yes, Jamie: All 24 volts.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Not to drift too far in to the weeds, but I thought for line voltage wiring there were some exceptions to the fill derating requirements to account for all the cables being on the same circuit so collectively they could only be carrying the ampacity of the circuit so they did not need to be derated when combined.0
-
As long as they never want to convert to a system like Tekmar TN4 where the system communicates through the wire you should be OK. On high-end jobs, running shielded cable is a good idea to future-proof the installation."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
True -- but only if they are in fact all on the same circuit and of the same voltage. You can have two or more circuits in a conduit (depending on fill, of course), but only if the are complete circuits -- that is one or two hots and a neutral.mattmia2 said:Not to drift too far in to the weeds, but I thought for line voltage wiring there were some exceptions to the fill derating requirements to account for all the cables being on the same circuit so collectively they could only be carrying the ampacity of the circuit so they did not need to be derated when combined.
But never different voltages.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If your using say 5 transformers, I would at least bundle them that way. 5 sets a piece. And label label label.
On jobs like this, do you typically leave a field wiring schematic behind?0 -
Shielded cable would insure against any weird discoveries like hey this model thermostat makes some hash that normally isn't a problem but when you couple the lines to several together by running them in parallel or to a different model that hash interferes with the other t-stat. This was my concern, not about heat which is what the rules in the NEC for line voltage are concerned with but about discovering some weird interference.Zman said:As long as they never want to convert to a system like Tekmar TN4 where the system communicates through the wire you should be OK. On high-end jobs, running shielded cable is a good idea to future-proof the installation.
1 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements