Pipe Size from Feeder Pump to Multiple Boilers??

JUGHNE
JUGHNE Member Posts: 11,430
edited May 2021 in THE MAIN WALL
I will have 2 boilers with solenoid controls fed by a single boiler feeder pump.
(ShipCo 60-DMS-MU1; 1/3HP; 6 GPM @ 10 PSI; 34 gallon tank)

I was thinking of using 1/2" black pipe from the pump to each boiler.
(M&M 150 feeder/LWCO controls on each)

I have another site with the same pump feeding 2 slightly larger boilers that sends water thru 3/4" blk pipe too quickly and knocks the steam down. It has a nearly full port 3/4" bypass from pump discharge directly back into the tank. There are 2 throttling ball valves on each boiler plus the drop thru 3/4" electric valves. It still fill too quickly.

I thought 3/4 at the pump reduced to 1/2" to each boiler might knock the flow down better. Boilers are PB-05L with 12.4 gallons of water and PB-04, 10.8 gallons.

If 3/4" is highly recommended then how about 3/4" hard type L copper? (my stock cost less than 3/4" blk pipe does today).........also have old stock of 1/2" black pipe.

Trying to empty shop of old stock.....this is probably my last major piping job.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 26,036
    Unless the runs are very long, 1/2 vs. 3/4 isn't going to make that much difference...

    How about using a globe valve on each run? They can throttle more effectively than a ball valve (I know -- pain in the neck to maintain,, but.)

    Or just get a less enthusiastic pump?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • JUGHNE
    JUGHNE Member Posts: 11,430
    The runs are pretty short, 4-6'.

    In addition to isolation ball valves, I was going to try iron gas cocks, sometimes referred to as "I bibs", IIRC.
    They have the slotted tapered plug, that rotates only 1/4 turn.
    Heavy iron seems like it should not wear down like ball valves.

    This is the smallest pump available, least GPM.
    Unique pump tank is only 9" tall, 30 X 30 square. Needed as inlet is 6 1/2" AFF, existing true "dry" pipe is 9" AFF. 2 pipe system. F&T on EOM....2" return.

    Thanks for your input Jamie.

    I am sure all of us are thankful and remembering the reason for long week end.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 17,878
    I would use the 3/4 copper. If you put in 1/2" and it's too small your stuck. 3/4" with a valve in it to throttle the flow would be better IMHO
    JUGHNE
  • dopey27177
    dopey27177 Member Posts: 916
    Dole makes in line flow control valves 1/2 & 3/4".
    These are inline orificed fittings fixed at a specific flow rate.
    Can be had from 1/2 gpm and up/

    Jake